Good analysis Bruce.
I was just thinking a manual deluge would be the way to go. That would be
identical the very earliest systems in England  (pipes with holes and a
control valve someone opened if need be).
Obviously the area is attended while loading/unloading.

And since I'm at home relaxing now as opposed to being in my cubicle
worrying about being busted for 'being on the internet' I want to correct
something from my first post: .000283 ft^2, not ft^3.
And if anyone is leery of deriving a K Factor using feet, seconds, and
gravity, please try it with nominal 1/2" sprinklers. The well-known C of D
for them is .75.

Brad
On Sep 19, 2016 3:39 PM, "Bruce Verhei" <bver...@comcast.net> wrote:

> Why not a large orifice sidewall at each side of each trailer?
>
> Going back to objectives, and what is not objective. Writing it out helps,
> at least me.
>
> 1. Goal is not to protect trailer or trailers contents;
>
> Assumed after this:
>
> 2. Goal is not to keep fire originating in building from spreading to
> trailer/contents.
>
> 3. Goal is to confine fire originating in trailer or at opening from
> spreading to building.
>
> 4. Design to reduce smoke damage is not a consideration.
>
> 5. Activation reliability/cost. Normally we think of reliability and cost
> as being in conflict. In this case I don't think they are. It is my
> observation that sprinkler heads are much more reliable than detection
> system coupled to deluge valve.
>
> 6. Effectiveness. Some judgement and experience are call for. But I'd
> expect the sidewall would likely be as or more effective at cooling the
> plume moving into the building as the drill holes.
>
> 7. On-going cost. Sidewall would be cheaper.
>
> 8. Feasibility. We'd need to see more detail to see this.
>
> 9. Alarm, and response. Deluge detection, and sidewall would both result
> in response. Assuming waterflow detection and off-site monitoring.
>
> Is this an old European national standard that pre-dates the EU? Similar
> here to that DOD long term housing goods storage in plywood bins,
> administered by someone who doesn't understand and doesn't care?
>
> You might find this has been around for decades, long before higher flow
> sidewalls were available. (Again, like that outside canopy/loading dock
> detail showing a dry pendant on a 45. Why? Because it was quite awhile
> before dry sidewalls were commonly available.)
>
> Maybe asking the question will result in a change in practice. To me it
> sounds like a spec coated in dust.
>
> Best
>
> Bruce Verhei
>
> On Sep 19, 2016, at 08:59, <mphe...@aerofire.com> <mphe...@aerofire.com>
> wrote:
>
> Because, Ron, it would need to be a fuse that is UL Listed for use with
> the Keg. (actuating device) But it would be fun to watch the test.
>
> Mark at Aero
>
> 602 820-7894
>
>
>
> *From:* Sprinklerforum [mailto:sprinklerforum-bounces@lists.firesprinkler.
> org <sprinklerforum-boun...@lists.firesprinkler.org>] *On Behalf Of 
> *rongreenman
> .
> *Sent:* Monday, September 19, 2016 8:50 AM
> *To:* sprinklerforum@lists.firesprinkler.org
> *Subject:* Re: spray bar versus deluge heads for opening protection
>
>
>
> Why not just put a barrel of water on top of keg of black powder with a
> fuse going into the trailer?
>
>
>
>
>
> On Mon, Sep 19, 2016 at 8:47 AM, Brad Casterline <bcasterl...@fsc-inc.com>
> wrote:
>
> That's upstream Gus. I'm just trying to help Craig get out of the (if Mr.
> Greenman will pardon my French) Remote Area with the calc software he has.
>
> :)
>
> Brad
>
> -----Original Message-----
> From: Sprinklerforum [mailto:sprinklerforum-bounces@lists.firesprinkler.
> org]
>
> On Behalf Of Gus Olson
> Sent: Monday, September 19, 2016 10:37 AM
> To: sprinklerforum@lists.firesprinkler.org
> Subject: RE: spray bar versus deluge heads for opening protection
>
> Brad,
> Don't forget to add a strainer
>
> Gus Olson
>
> -----Original Message-----
> From: Sprinklerforum [mailto:sprinklerforum-bounces@lists.firesprinkler.
> org]
> On Behalf Of Brad Casterline
> Sent: Monday, September 19, 2016 11:30 AM
> To: sprinklerforum@lists.firesprinkler.org
> Subject: RE: spray bar versus deluge heads for opening protection
>
> P = 40 PSI
> K = 1.55
> Q = 9.8 GPM
>
> 36 GPM / 9.8 = 3.67 holes per nozzle
>
> call it 4 :)
>
> Brad
>
> -----Original Message-----
> From: Sprinklerforum [mailto:sprinklerforum-bounces@lists.firesprinkler.
> org]
> On Behalf Of craig.pr...@ch2m.com
> Sent: Monday, September 19, 2016 9:57 AM
> To: sprinklerforum@lists.firesprinkler.org
> Subject: RE: spray bar versus deluge heads for opening protection
>
> Dude, you need serious help.   HAHA
>
> Now how many average sprinkler designers could have figured that out?
>
> But it has to equal the discharge of spray nozzles which are required to
> provide a minimum of 36 gpm at 40 psi around the perimeter.
>
>
>
> Craig L. Prahl
> Fire Protection Group Lead/SME
> CH2M
> 200 Verdae Blvd.
> Greenville, SC  29607
> Direct - 864.920.7540
> Fax - 864.920.7129
> CH2MHILL Extension  77540
> craig.pr...@ch2m.com
>
>
>
> -----Original Message-----
> From: Sprinklerforum [mailto:sprinklerforum-bounces@lists.firesprinkler.
> org]
> On Behalf Of Brad Casterline
> Sent: Monday, September 19, 2016 10:37 AM
> To: sprinklerforum@lists.firesprinkler.org
> Subject: RE: spray bar versus deluge heads for opening protection
> [EXTERNAL]
>
> (.25/24)^2 * PI = .000314 ft^2
> assume coefficient of discharge of .9
> .000314 *.9 = .000283
>
> 'imply' 7 PSI
> 7 / .433 = 16.167 (h)
> v = (2gh)^.5 = 32.266 ft/sec
>
> 32.266 ft/sec * .000283 ft^3 = .00913 ft^3/sec, * 7.48 * 60 = 4.1 GPM
>
> Q = 4.1
> P = 7.0
> K = 1.55
>
> Brad
>
> -----Original Message-----
> From: Sprinklerforum [mailto:sprinklerforum-bounces@lists.firesprinkler.
> org]
> On Behalf Of craig.pr...@ch2m.com
> Sent: Monday, September 19, 2016 9:11 AM
> To: sprinklerforum@lists.firesprinkler.org
> Subject: spray bar versus deluge heads for opening protection
>
> Today's teaser.
>
> An owner gives you this criteria for protecting a truck dock door opening.
> A semi-trailer is parked at the opening up against the dock seal, the
> trailer contains wooded pallets.
>
> The rollup door and the trailer doors remain open at all times for in and
> out access.
>
> Their recommended method of protecting the opening is to use 1.5" pipe with
> 1/4" holes drilled every 6".  Provide this around the opening which is 12"
> wide by 9' high.  This is approved by their international corporate safety
> department.
>
> This will be a deluge system for two dock doors.
>
> How are you going to calculate this?
>
>
> Craig L. Prahl
> Fire Protection Group Lead/SME
> CH2M
> 200 Verdae Blvd.
> Greenville, SC  29607
> Direct - 864.920.7540
> Fax - 864.920.7129
> CH2MHILL Extension  77540
> craig.pr...@ch2m.com
>
> _______________________________________________
> Sprinklerforum mailing list
> Sprinklerforum@lists.firesprinkler.org
> http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.
> org
>
> _______________________________________________
> Sprinklerforum mailing list
> Sprinklerforum@lists.firesprinkler.org
> http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.
> org
> _______________________________________________
> Sprinklerforum mailing list
> Sprinklerforum@lists.firesprinkler.org
> http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.
> org
>
> _______________________________________________
> Sprinklerforum mailing list
> Sprinklerforum@lists.firesprinkler.org
> http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.
> org
>
> _______________________________________________
> Sprinklerforum mailing list
> Sprinklerforum@lists.firesprinkler.org
> http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.
> org
>
> _______________________________________________
> Sprinklerforum mailing list
> Sprinklerforum@lists.firesprinkler.org
> http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.
> org
>
>
>
>
>
> --
>
> Ron Greenman
>
>
> 4110 Olson Dr., NW
> Gig Harbor, WA 98335
>
> rongreen...@gmail.com
>
> 253.576.9700
>
>
>
> The Universe is monstrously indifferent to the presence of man. -Werner
> Herzog, screenwriter, film director, author, actor and opera
> director (1942-)
>
> _______________________________________________
> Sprinklerforum mailing list
> Sprinklerforum@lists.firesprinkler.org
> http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.
> org
>
>
> _______________________________________________
> Sprinklerforum mailing list
> Sprinklerforum@lists.firesprinkler.org
> http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.
> org
>
>