Ah-HA!   Thanks Jim ... I blipped over that at least twice whilst skimming for 
the info.   "Floor Control ..." not in the index, "Control Valves" doesn't 
include reference to floor controls.   I'm very interested to see where this 
information lands in the 2019 'cause we know it's on the move again for sure.

SL

From: Sprinklerforum [mailto:[email protected]] On 
Behalf Of Jim Davidson
Sent: Monday, September 26, 2016 2:48 PM
To: [email protected]
Subject: RE: Question for any member of Installation Sub-TC

Steve,

It is in Section 8.2.4 of the 2016 edition of NFPA 13.

Have a fire safe day!

Regards

Jim

Davidson Associates

Fire Protection Engineering                                                     
                                                                                
       P. O. Box 4002
Code Consultants                                                                
                                                                                
Greenville, DE  19807
                                                                                
                                                                                
                       (302) 994-9500
                                                                                
                                                                                
                Fax (302) 994-3414

CONFIDENTIALITY
This report and any attachments are confidential and also may be privileged.
If you are not the named recipient, or have otherwise received this report in 
error, please destroy the report, notify the sender immediately, and do not 
disclose its contents to any other person, use them for any purpose, or store 
or copy them in any medium.
Thank you for your cooperation.

From: Sprinklerforum [mailto:[email protected]] On 
Behalf Of Steve Leyton
Sent: Monday, September 26, 2016 5:31 PM
To: 
[email protected]<mailto:[email protected]>
Subject: Question for any member of Installation Sub-TC

Was 8.16.1.5 Floor Control Valve Assemblies (13, 2013 edition) completely 
rescinded in 2016 edition?

[Steve Signature (3)]

_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org

Reply via email to