Hello Tom,

I just did a search in the PDF for "Floor Control Valve Assemblies" I came up 
in 8.4.2 as the only location on the whole phrase.

Then a search on "Floor Control Valve" came up with : 
8.16.1.1.2.2 Floor control valves in high-rise buildings and
valves controlling flow to sprinklers in circulating closed loop
systems shall comply with 8.16.1.1.2.1(1) or 8.16.1.1.2.1(2).

Tuesday, September 27, 2016, 7:53:21 AM, you wrote:



> On Sep 26, 2016, at 4:36 PM, Steve Leyton <[email protected]> wrote:

> That’s my question – has it been rescinded?   Didn’t see it anywhere else in 
> the standard but figured it was worth a question …
>  
> SL
>  
> From: Sprinklerforum [mailto:[email protected]] 
> On Behalf Of Joe Burtell
> Sent: Monday, September 26, 2016 2:31 PM
> To: [email protected]
> Subject: Re: Question for any member of Installation Sub-TC
>  
> 2016
>  
> 8.16.1.5* In-Rack Sprinkler System Control Valves.
> A.8.16.1.5 In-rack sprinklers and ceiling sprinklers selected for protection 
> should be con-
> trolled by at least two separate indicating valves and drains. In higher rack 
> arrangements, 
> consideration should be given to providing more than one in-rack control 
> valve in order to 
> limit the extent of any single impairment.
>  
> I would say, yes or it moved?


> Best regards,

> Joe Burtell, SET, CFPS

>  

> <image001.jpg>

> PH: 406-652-7697

> Fax: 406-652-7743 | Cell: 406-861-4507

> Email: [email protected]

> Web Site: http://www.burtellfire.com

> NOTICE:  The information contained in this e-mail transmission is intended 
> only for use of the individual or entity named above.  This e-mail 
> transmission, and any documents, files, previous e-mail transmissions or 
> other information attached to it, may contain confidential information that 
> is legally privileged.  If you are not the intended recipient of this e-mail 
> transmission, or the employee or agent responsible for delivering it to the 
> intended recipient, you are hereby notified that any disclosure, 
> dissemination, distribution, copying or other use of this transmission or any 
> of the information contained in or attached to this e-mail is strictly 
> prohibited.  If you have received this e-mail transmission in error, please 
> immediately notify us by return e-mail transmission and destroy the original 
> e-mail transmission as well as its attachments without reading or saving it 
> in any manner.  Thank you.

>  
> On Mon, Sep 26, 2016 at 3:17 PM, Steve Leyton <[email protected]> 
> wrote:
> Was 8.16.1.5 Floor Control Valve Assemblies (13, 2013 edition) completely 
> rescinded in 2016 edition?
>  
> <image002.png>
>  

> _______________________________________________
> Sprinklerforum mailing list
> [email protected]
> http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org

>  _______________________________________________
> Sprinklerforum mailing list
> [email protected]
> http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org

>  



-- 
Best regards,
 Charles                            mailto:[email protected]

_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org

Reply via email to