As Steve said the horse is dead. 

I hope everyone has a great weekend. 

Travis Mack, SET
MFP Design, LLC
"Follow" us on Facebook: 
https://www.facebook.com/pages/MFP-Design-LLC/92218417692
Send large files to MFP Design via:
https://www.hightail.com/u/MFPDesign

Sent from my iPhone

> On Oct 29, 2016, at 11:06 AM, Brad Casterline <[email protected]> wrote:
> 
> Damien -
> I think so, using Hazen-Williams. It disturbs me though that a fitting or 
> valve, installed and anchored, can shrink or grow depending on the flow. 
> With Darcy-Weisbach, using a "K-Value" for fittings and valves that doesn't 
> happen.
> This is because friction head is directly proportional to the square of the 
> velocity, and D-W is all about the velocity, whereas H-W gets similar results 
> with much less effort over an acceptable range of fire protection velocities.
> 
> Ron -
> I kicked myself right after I posted that for not saying something like, "the 
> only reason I can think of why a 1" threaded tee or 1" pipe-o-let is EQL=5ft 
> whilst a 1" mechanical tee is EQL=11ft is it must have something to do with 
> gaskets.
> (I miss the aroma of warm oil, taking smoke breaks in the fab shop-- been 15 
> years-- even then that's the closest I got to the reality of mech tees).
> 
> Steve -
> I was just trying to help Russell. I think he would have had more replies if 
> I had just stayed out of it.
> He contacted me off Forum, I said I would see if I could get a formal interp, 
> I got one, and here we are.
> The problem is, I'm not sure the question was expressed adequately, I 
> apologized for letting him down, he is back...
> You are a TC member-- is it a dead horse or not?
> I could care less how it turns out-- I do what my P.E. tells me to do.
> 
> Brad
>> On Oct 29, 2016 12:03 PM, "Steve Leyton" <[email protected]> wrote:
>> There's a saying in our business that we design systems with computers, use 
>> lasers to measure pipe for fabrication, then mark with a paint  pen and cut 
>> it with a chop saw. In other words there are some weak links in the chain of 
>> events that we take for granted every day. 
>> 
>> The hydraulic design method that we use, the number of sprinklers and sizes 
>> of design areas that we include in our models, all provide for conservative 
>> safety factors. So to the point of whether or not a rubber gasket reduces 
>> the inside diameter compared to a weld-o-let or a threaded fitting, my 
>> reaction to that is so what, who cares?   
>> 
>> All these formulas and algorithms and commentary amount to a whole lot of 
>> over-analysis and here's why: if you were to actually account for that  
>> hundredth or thousandth an inch, the impact would be an almost indiscernibly 
>> higher starting pressure at the end sprinkler. Thereafter, you would have an 
>> almost indiscernible lower net K-factor at each successive sprinkler thus 
>> reducing overflow,making the system demand lower by a fraction of a fraction 
>> of a PSI here and a GPM there.
>> 
>> So if you want to spend an extra 3 or 4 hours per calc boilng down these 
>> metrics, be my guest but as far as this discussion thread is concerned I'm 
>> pretty sure the horse is dead and beyond resuscitation.
>> 
>> 
>> Steve
>> 
>> 
>> -------- Original message --------
>> From: "rongreenman ." <[email protected]>
>> Date: 10/29/16 9:44 AM (GMT-08:00)
>> To: [email protected]
>> Subject: Re: Hydraulic losses when using a Mechanical Tee on Sprinkler Outlet
>> 
>> In y experience with mech tees I always used the type with the lip so the 
>> hole size was substantially bigger for it than a elder outlet and the rubber 
>> was well away from the hole. That aside dramatic is a pretty heady word Brad 
>> (pun intended). The fitting the head is screwed into, including welded 
>> outlets and mech tees, do not need to be calculated per NFPA. Ig the listing 
>> requires it then that would trump the standard but to my knowledge no head 
>> requires that fitting be included. Given all the slop in the model we use, 
>> and that it is a model I'm always amazed that a bunch of engineering types 
>> act like it is an actual and mathematically accurate representation of what 
>> goes in each piece  of the system in all cases.
>> 
>>> On Sat, Oct 29, 2016 at 9:23 AM, Brad Casterline <[email protected]> 
>>> wrote:
>>> This is actually pretty dramatic Ron. In Russell's case, if the K25 head is 
>>> in a 1" welded pipe-o-let the pressure required at the branch line is the 
>>> same as at the head, where as if it is in a 1" mechanical tee the pressure 
>>> required at the branch line is the same as if the head was on a 1" x 11'-0" 
>>> sprig or drop!
>>> 
>>> Of course if the K for a K25 was established when it was in a 1" mech tee, 
>>> it could rightly be excluded.
>>> 
>>> Both welded outlets and mech tees have similar hole sizes, but I think the 
>>> gaskets on mech tees reduce the AREA of the hole, which plays the biggest 
>>> part of the ultimate Coefficient of Discharge, aka, K-Factor.
>>> 
>>> Just my two no nonsense :)
>>> 
>>> Brad
>>> 
>>>> On Oct 29, 2016 11:02 AM, "rongreenman ." <[email protected]> wrote:
>>>> Are we once again worrying about the difference between 0.003 psi and 
>>>> 0.004 psi?
>>>> 
>>>>  If I recall the number we're trying to compare demand against supply is 
>>>> based on a formulae with a constant (average), an average C-factor of 
>>>> deterioration based on variable conditions over many years, a nominal 
>>>> diameter, and a velocity pressure determined by holding a pitot in a 
>>>> stream of water that's trying to rip the pitot out of your had while you 
>>>> take an average reading from a bouncing gauge that has a +/– built in. 
>>>> Then we do the math, round to the nearest 50 gpm, and apply it to a graph 
>>>> so small that the width of the line has an effect. 
>>>> 
>>>> And as Brad said the fitting is calculated into the K factor of the 
>>>> sprinkler. And as someone else noted the flexible drop is a drop, not a 
>>>> fitting. It has a fitting the sprinkler screws into. It also has a 
>>>> friction loss value that has to be an average as it doesn't take the 
>>>> curves into account. And do we calculate the gain from the elevation 
>>>> change?
>>>> 
>>>>> On Fri, Oct 28, 2016 at 8:33 AM, Brad Casterline 
>>>>> <[email protected]> wrote:
>>>>> Here is my original reply, for what it's worth...
>>>>> 
>>>>>  
>>>>> 
>>>>>  
>>>>> 
>>>>> Russell,
>>>>> 
>>>>>  
>>>>> 
>>>>> My understanding is we do not have to figure the loss for the fitting the
>>>>> 
>>>>> sprinkler is in because when the K Factor was being established it was in 
>>>>> a
>>>>> 
>>>>> fitting.
>>>>> 
>>>>> NFPA 13 (2016) 23.4.4.8.1 (9) confirms that.
>>>>> 
>>>>> But it's a good question because we're supposed to use a manufacturer's
>>>>> 
>>>>> published loss if they have one.
>>>>> 
>>>>> So would it make sense to, if the published loss is greater, subtract the
>>>>> 
>>>>> loss shown in 13, and include that difference?
>>>>> 
>>>>>  
>>>>> 
>>>>> Brad
>>>>> 
>>>>>  
>>>>> 
>>>>>  
>>>>> 
>>>>> From: Sprinklerforum 
>>>>> [mailto:[email protected]] On Behalf Of Brad 
>>>>> Casterline
>>>>> Sent: Friday, October 28, 2016 10:19 AM
>>>>> To: [email protected]
>>>>> Subject: RE: Hydraulic losses when using a Mechanical Tee on Sprinkler 
>>>>> Outlet
>>>>> 
>>>>>  
>>>>> 
>>>>> Here is the e-mail I sent to our in-office guy whom submits questions to 
>>>>> NFPA:
>>>>> 
>>>>>  
>>>>> 
>>>>>  
>>>>> 
>>>>> *****
>>>>> 
>>>>> "From NFPA 13- 2016
>>>>> 
>>>>>  
>>>>> 
>>>>>  
>>>>> 
>>>>> 23.4.3.1.1 Table 23.4.3.1.1 shall be used to determine the
>>>>> 
>>>>> equivalent length of pipe for fittings and devices unless manufacturer’s
>>>>> 
>>>>> test data indicate that other factors are appropriate.
>>>>> 
>>>>>  
>>>>> 
>>>>> 23.4.4.8.1
>>>>> 
>>>>> (9) Friction loss shall be excluded for the fitting directly
>>>>> 
>>>>> connected to a sprinkler.
>>>>> 
>>>>>  
>>>>> 
>>>>>  
>>>>> 
>>>>> A 1" tee in the table is 5' equivalent length.
>>>>> 
>>>>> A mechanical tee with 1" outlet is 11' equivalent length.
>>>>> 
>>>>>  
>>>>> 
>>>>> If the sprinkler is directly attached to the mechanical tee do we still 
>>>>> exclude it?"
>>>>> 
>>>>> *****
>>>>> 
>>>>>  
>>>>> 
>>>>>  
>>>>> 
>>>>> When we got the recent response Gregory pasted, I asked the guy for the 
>>>>> exact wording of the submitted question, but since submitting a question 
>>>>> on-line 'disappears' once submitted, it was not available. He said he 
>>>>> reworded mine a little, but thinks the last line (which is what this is 
>>>>> all about) was clear.
>>>>> 
>>>>>  
>>>>> 
>>>>> Personally, I like my original reply to Russell, but I'm just a Tech, so 
>>>>> there's that :)
>>>>> 
>>>>>  
>>>>> 
>>>>> Brad
>>>>> 
>>>>>  
>>>>> 
>>>>>  
>>>>> 
>>>>> From: Sprinklerforum 
>>>>> [mailto:[email protected]] On Behalf Of 
>>>>> Russell & Carol Gregory
>>>>> Sent: Thursday, October 27, 2016 10:01 PM
>>>>> To: [email protected]
>>>>> Subject: RE: Hydraulic losses when using a Mechanical Tee on Sprinkler 
>>>>> Outlet
>>>>> 
>>>>>  
>>>>> 
>>>>> Ken, and others,
>>>>> 
>>>>> We have been excluding the loss for a welded outlet or a mech tee when a 
>>>>> sprinkler is directly attached. If the outlet is to feed a pipe 
>>>>> (regardless of length) then the standard loss for a branch on tee would 
>>>>> be used, however if the Manufacturers Data Sheet states that the loss in 
>>>>> a clamp tee is greater than the loss in Table 23.4.3.1.1 (NFPA 13 2016) 
>>>>> for a side outlet of tee, THEN the ADDITIONAL LOSS shall be included. I 
>>>>> think they should say the Higher EQL Loss should be used so you don’t use 
>>>>> less than the Table Loss.
>>>>> 
>>>>>  
>>>>> 
>>>>> Here is a recent NFPA Response to a similar question;
>>>>> 
>>>>>  
>>>>> 
>>>>> Table 23.4.3.1.1 is required to be used to determine the equivalent length
>>>>> 
>>>>> of pipe for fittings and devices unless manufacturers' test data indicate
>>>>> 
>>>>> that other factors are appropriate. In your situation since the 
>>>>> manufacturer
>>>>> 
>>>>> specifies an equivalent length of 11 feet, you are required to use 11 feet
>>>>> 
>>>>> for the equivalent length.
>>>>> 
>>>>>  
>>>>> 
>>>>> In regards to Section 23.4.4.8(9) of the 2016 edition of NFPA 13, if an
>>>>> 
>>>>> extension is used with a tee, that tee must be included in the hydraulic
>>>>> 
>>>>> calculations. The allowance to use an extension is restricted to 
>>>>> sprinklers
>>>>> 
>>>>> with a relative low discharge volume. They will most likely be used for
>>>>> 
>>>>> minor adjustments to interface with the ceiling.
>>>>> 
>>>>>  
>>>>> 
>>>>> This answers some of the other Forum responses to my questions but does 
>>>>> not answer my problem.
>>>>> 
>>>>>  
>>>>> 
>>>>> What I would like to see is a practical flow test done with a K36 (us 
>>>>> k25) head and see if there is a significant difference between welded 
>>>>> outlet, threaded tee and clamp tee. Does anyone know if this has been 
>>>>> done???
>>>>> 
>>>>>  
>>>>> 
>>>>> Our AHJ has asked for the full loss to be included and this will nearly 
>>>>> double the pressure required at a K-36 sprinkler from 345kPa(50psi) to 
>>>>> around 600kPa(90psi), if clamp tees are used. There is quite a variation 
>>>>> between Brands for the stated EQL.
>>>>> 
>>>>> Makes life difficult if site staff change from welded to mechanical 
>>>>> fittings and then buy a variety of brands!!!!!
>>>>> 
>>>>>  
>>>>> 
>>>>> Thanks for the responses.
>>>>> 
>>>>> Russell Gregory
>>>>> 
>>>>>  
>>>>> 
>>>>>  
>>>>> 
>>>>> From: Sprinklerforum 
>>>>> [mailto:[email protected]] On Behalf Of 
>>>>> Parsley Consulting
>>>>> Sent: Friday, 28 October 2016 3:56 AM
>>>>> To: [email protected]
>>>>> Subject: Re: Hydraulic losses when using a Mechanical Tee on Sprinkler 
>>>>> Outlet
>>>>> 
>>>>>  
>>>>> 
>>>>> Russell,
>>>>>     Mark and Todd are both correct.  
>>>>>     If the sprinkler is directly attached to the fitting, in this case 
>>>>> the welded outlet or mechanical tee, the friction loss through that 
>>>>> fitting is excluded from the hydraulic calculations, per NFPA 13, 
>>>>> 23.4.4.7.1(9).  I don't know that I've ever had a set of calculations 
>>>>> sent back with a comment that I didn't include the friction loss 
>>>>> equivalent for the welded outlet or mechanical tee which was directly 
>>>>> attached to the sprinkler.  
>>>>>     Todd's comment is valid as well, however it's worth noting, I 
>>>>> believe, that when you're designing a system with flexible drops you must 
>>>>> account for the equivalent length of the device, using the manufacturer's 
>>>>> data.  My own experience has been that those values are substantial.
>>>>> sincerely,
>>>>> 
>>>>> Ken Wagoner, SET
>>>>> Parsley Consulting
>>>>> 350 West 9th Avenue, Suite 206
>>>>> Escondido, California 92025
>>>>> Phone 760-745-6181
>>>>> Visit our website
>>>>> 
>>>>> On 10/27/2016 1:30 AM, Russell & Carol Gregory wrote:
>>>>> 
>>>>> I posted a message on this subject early this month but only received one 
>>>>> reply(thanks Brad). This was surprising as I thought it was a serious 
>>>>> problem if the full EQL for tee had to be added to calculations. 
>>>>> Especially if the change was made on-site after design had been completed 
>>>>> with welded outlets.
>>>>> 
>>>>> So my query is as follows;
>>>>> 
>>>>>  
>>>>> 
>>>>> When calculating a Range Pipe with welded threaded outlets for sprinklers 
>>>>> it is not necessary to include a loss for the water leaving the range 
>>>>> pipe and entering the sprinkler. The total pressure is assumed to apply 
>>>>> to the sprinkler orfice.
>>>>> 
>>>>> This means that a 80nb pipe with a 25nb outlet and a k36 sprinkler does 
>>>>> not have an additional loss added for the outlet fitting.
>>>>> 
>>>>>  
>>>>> 
>>>>> If I change my design and fabricate the 80nb range pipe with 80 x 25 
>>>>> Mechanical Tees for the Sprinkler outlet do I have to apply an additional 
>>>>> loss factor for that fitting? The published EQL for Mech tees varies 
>>>>> greatly between brands,( 0.8m up to 2.4m). This means a head pressure of 
>>>>> 345kPa would need around 600kPa in the range if this additional loss is 
>>>>> added.
>>>>> 
>>>>>  
>>>>> 
>>>>> Questions;
>>>>> 
>>>>> 1.       Is it common practice in USA to use 80 x 25 clamp/mechanical 
>>>>> tees  for attaching large bore Storage Sprinklers directly to 80nb range 
>>>>> pipes?
>>>>> 
>>>>> 2.       Is it common practice to add in an additional loss for the clamp 
>>>>> tee, in the hydraulic calculation, where the sprinkler is directly fitted 
>>>>> to the tee outlet?  
>>>>> 
>>>>>  
>>>>> 
>>>>> I would appreciate the Forum members advise as to what is the standard 
>>>>> practice in the USA.
>>>>> 
>>>>>  
>>>>> 
>>>>> Russell Gregory
>>>>> 
>>>>> Christchurch
>>>>> 
>>>>> New Zealand
>>>>> 
>>>>>  
>>>>> 
>>>>> e-mail [email protected]
>>>>> 
>>>>>  
>>>>> 
>>>>>  
>>>>> 
>>>>> _______________________________________________
>>>>> Sprinklerforum mailing list
>>>>> [email protected]
>>>>> http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org
>>>>>  
>>>>> 
>>>>> 
>>>>> _______________________________________________
>>>>> Sprinklerforum mailing list
>>>>> [email protected]
>>>>> http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org
>>>>> 
>>>> 
>>>> 
>>>> 
>>>> -- 
>>>> Ron Greenman
>>>> 
>>>> 4110 Olson Dr., NW
>>>> Gig Harbor, WA 98335
>>>> 
>>>> [email protected]
>>>> 
>>>> 253.576.9700
>>>> 
>>>> The Universe is monstrously indifferent to the presence of man. -Werner 
>>>> Herzog, screenwriter, film director, author, actor and opera director 
>>>> (1942-)
>>>> 
>>>> _______________________________________________
>>>> Sprinklerforum mailing list
>>>> [email protected]
>>>> http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org
>>>> 
>>> 
>>> _______________________________________________
>>> Sprinklerforum mailing list
>>> [email protected]
>>> http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org
>>> 
>> 
>> 
>> 
>> -- 
>> Ron Greenman
>> 
>> 4110 Olson Dr., NW
>> Gig Harbor, WA 98335
>> 
>> [email protected]
>> 
>> 253.576.9700
>> 
>> The Universe is monstrously indifferent to the presence of man. -Werner 
>> Herzog, screenwriter, film director, author, actor and opera director (1942-)
>> 
>> _______________________________________________
>> Sprinklerforum mailing list
>> [email protected]
>> http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org
>> 
> _______________________________________________
> Sprinklerforum mailing list
> [email protected]
> http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org
_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org

Reply via email to