John,
You are a TC member yourself.
If, as it seems, the interp of NFPA is that we do indeed include the
published equivalent length for a mech tee with a sprinkler installed
directly in it, that we just deem it ridiculous, because Steve said so?

By the way, I know Steve did not say so.
This is all about rules and interpretations, is it not?

Brad
On Oct 29, 2016 2:13 PM, "John Denhardt" <[email protected]>
wrote:

> I could not agree more with Steve.  It is fine to look at the details but
> do not go beyond ridiculous.
>
> John
>
> John August Denhardt, P.E.
> Strickland Fire Protection
>
> On Oct 29, 2016, at 1:03 PM, Steve Leyton <[email protected]>
> wrote:
>
> There's a saying in our business that we design systems with computers,
> use lasers to measure pipe for fabrication, then mark with a paint  pen and
> cut it with a chop saw. In other words there are some weak links in the
> chain of events that we take for granted every day.
>
> The hydraulic design method that we use, the number of sprinklers and
> sizes of design areas that we include in our models, all provide for
> conservative safety factors. So to the point of whether or not a rubber
> gasket reduces the inside diameter compared to a weld-o-let or a threaded
> fitting, my reaction to that is so what, who cares?
>
> All these formulas and algorithms and commentary amount to a whole lot of
> over-analysis and here's why: if you were to actually account for that
>  hundredth or thousandth an inch, the impact would be an almost
> indiscernibly higher starting pressure at the end sprinkler. Thereafter,
> you would have an almost indiscernible lower net K-factor at each
> successive sprinkler thus reducing overflow,making the system demand lower
> by a fraction of a fraction of a PSI here and a GPM there.
>
> So if you want to spend an extra 3 or 4 hours per calc boilng down these
> metrics, be my guest but as far as this discussion thread is concerned I'm
> pretty sure the horse is dead and beyond resuscitation.
>
>
> Steve
>
>
> -------- Original message --------
> From: "rongreenman ." <[email protected]>
> Date: 10/29/16 9:44 AM (GMT-08:00)
> To: [email protected]
> Subject: Re: Hydraulic losses when using a Mechanical Tee on Sprinkler
> Outlet
>
> In y experience with mech tees I always used the type with the lip so the
> hole size was substantially bigger for it than a elder outlet and the
> rubber was well away from the hole. That aside dramatic is a pretty heady
> word Brad (pun intended). The fitting the head is screwed into, including
> welded outlets and mech tees, do not need to be calculated per NFPA. Ig the
> listing requires it then that would trump the standard but to my knowledge
> no head requires that fitting be included. Given all the slop in the model
> we use, and that it is a model I'm always amazed that a bunch of
> engineering types act like it is an actual and mathematically accurate
> representation of what goes in each piece  of the system in all cases.
>
> On Sat, Oct 29, 2016 at 9:23 AM, Brad Casterline <[email protected]>
> wrote:
>
>> This is actually pretty dramatic Ron. In Russell's case, if the K25 head
>> is in a 1" welded pipe-o-let the pressure required at the branch line is
>> the same as at the head, where as if it is in a 1" mechanical tee the
>> pressure required at the branch line is the same as if the head was on a 1"
>> x 11'-0" sprig or drop!
>>
>> Of course if the K for a K25 was established when it was in a 1" mech
>> tee, it could rightly be excluded.
>>
>> Both welded outlets and mech tees have similar hole sizes, but I think
>> the gaskets on mech tees reduce the AREA of the hole, which plays the
>> biggest part of the ultimate Coefficient of Discharge, aka, K-Factor.
>>
>> Just my two no nonsense :)
>>
>> Brad
>> On Oct 29, 2016 11:02 AM, "rongreenman ." <[email protected]> wrote:
>>
>>> Are we once again worrying about the difference between 0.003 psi and
>>> 0.004 psi?
>>>
>>>  If I recall the number we're trying to compare demand against supply is
>>> based on a formulae with a constant (average), an average C-factor of
>>> deterioration based on variable conditions over many years, a nominal
>>> diameter, and a velocity pressure determined by holding a pitot in a stream
>>> of water that's trying to rip the pitot out of your had while you take an
>>> average reading from a bouncing gauge that has a +/– built in. Then we do
>>> the math, round to the nearest 50 gpm, and apply it to a graph so small
>>> that the width of the line has an effect.
>>>
>>> And as Brad said the fitting is calculated into the K factor of the
>>> sprinkler. And as someone else noted the flexible drop is a drop, not a
>>> fitting. It has a fitting the sprinkler screws into. It also has a friction
>>> loss value that has to be an average as it doesn't take the curves into
>>> account. And do we calculate the gain from the elevation change?
>>>
>>> On Fri, Oct 28, 2016 at 8:33 AM, Brad Casterline <
>>> [email protected]> wrote:
>>>
>>>> Here is my original reply, for what it's worth...
>>>>
>>>>
>>>>
>>>>
>>>>
>>>> Russell,
>>>>
>>>>
>>>>
>>>> My understanding is we do not have to figure the loss for the fitting
>>>> the
>>>>
>>>> sprinkler is in because when the K Factor was being established it was
>>>> in a
>>>>
>>>> fitting.
>>>>
>>>> NFPA 13 (2016) 23.4.4.8.1 (9) confirms that.
>>>>
>>>> But it's a good question because we're supposed to use a manufacturer's
>>>>
>>>> published loss if they have one.
>>>>
>>>> So would it make sense to, if the published loss is greater, subtract
>>>> the
>>>>
>>>> loss shown in 13, and include that difference?
>>>>
>>>>
>>>>
>>>> Brad
>>>>
>>>>
>>>>
>>>>
>>>> ------------------------------
>>>>
>>>> *From:* Sprinklerforum [mailto:sprinklerforum-bounces
>>>> @lists.firesprinkler.org] *On Behalf Of *Brad Casterline
>>>> *Sent:* Friday, October 28, 2016 10:19 AM
>>>> *To:* [email protected]
>>>> *Subject:* RE: Hydraulic losses when using a Mechanical Tee on
>>>> Sprinkler Outlet
>>>>
>>>>
>>>>
>>>> Here is the e-mail I sent to our in-office guy whom submits questions
>>>> to NFPA:
>>>>
>>>>
>>>>
>>>>
>>>>
>>>> *****
>>>>
>>>> "From NFPA 13- 2016
>>>>
>>>>
>>>>
>>>>
>>>>
>>>> *23.4.3.1.1 *Table 23.4.3.1.1 shall be used to determine the
>>>>
>>>> equivalent length of pipe for fittings and devices unless manufacturer’s
>>>>
>>>> test data indicate that other factors are appropriate.
>>>>
>>>>
>>>>
>>>> *23.4.4.8.1*
>>>>
>>>> (9) Friction loss shall be excluded for the fitting directly
>>>>
>>>> connected to a sprinkler.
>>>>
>>>>
>>>>
>>>>
>>>>
>>>> A 1" tee in the table is 5' equivalent length.
>>>>
>>>> A mechanical tee with 1" outlet is 11' equivalent length.
>>>>
>>>>
>>>>
>>>> If the sprinkler is directly attached to the mechanical tee do we still
>>>> exclude it?"
>>>>
>>>> *****
>>>>
>>>>
>>>>
>>>>
>>>>
>>>> When we got the recent response Gregory pasted, I asked the guy for the
>>>> exact wording of the submitted question, but since submitting a question
>>>> on-line 'disappears' once submitted, it was not available. He said he
>>>> reworded mine a little, but thinks the last line (which is what this is all
>>>> about) was clear.
>>>>
>>>>
>>>>
>>>> Personally, I like my original reply to Russell, but I'm just a Tech,
>>>> so there's that :)
>>>>
>>>>
>>>>
>>>> Brad
>>>>
>>>>
>>>>
>>>>
>>>> ------------------------------
>>>>
>>>> *From:* Sprinklerforum [mailto:sprinklerforum-bounces
>>>> @lists.firesprinkler.org] *On Behalf Of *Russell & Carol Gregory
>>>> *Sent:* Thursday, October 27, 2016 10:01 PM
>>>> *To:* [email protected]
>>>> *Subject:* RE: Hydraulic losses when using a Mechanical Tee on
>>>> Sprinkler Outlet
>>>>
>>>>
>>>>
>>>> Ken, and others,
>>>>
>>>> We have been excluding the loss for a welded outlet or a mech tee when
>>>> a sprinkler is directly attached. If the outlet is to feed a pipe
>>>> (regardless of length) then the standard loss for a branch on tee would be
>>>> used, however if the Manufacturers Data Sheet states that the loss in a
>>>> clamp tee is greater than the loss in Table 23.4.3.1.1 (NFPA 13 2016) for a
>>>> side outlet of tee, THEN the ADDITIONAL LOSS shall be included. I think
>>>> they should say the Higher EQL Loss should be used so you don’t use less
>>>> than the Table Loss.
>>>>
>>>>
>>>>
>>>> Here is a recent NFPA Response to a similar question;
>>>>
>>>>
>>>>
>>>> Table 23.4.3.1.1 is required to be used to determine the equivalent
>>>> length
>>>>
>>>> of pipe for fittings and devices unless manufacturers' test data
>>>> indicate
>>>>
>>>> that other factors are appropriate. In your situation since the
>>>> manufacturer
>>>>
>>>> specifies an equivalent length of 11 feet, you are required to use 11
>>>> feet
>>>>
>>>> for the equivalent length.
>>>>
>>>>
>>>>
>>>> In regards to Section 23.4.4.8(9) of the 2016 edition of NFPA 13, if an
>>>>
>>>> extension is used with a tee, that tee must be included in the hydraulic
>>>>
>>>> calculations. The allowance to use an extension is restricted to
>>>> sprinklers
>>>>
>>>> with a relative low discharge volume. They will most likely be used for
>>>>
>>>> minor adjustments to interface with the ceiling.
>>>>
>>>>
>>>>
>>>> This answers some of the other Forum responses to my questions but does
>>>> not answer my problem.
>>>>
>>>>
>>>>
>>>> What I would like to see is a practical flow test done with a K36 (us
>>>> k25) head and see if there is a significant difference between welded
>>>> outlet, threaded tee and clamp tee. Does anyone know if this has been
>>>> done???
>>>>
>>>>
>>>>
>>>> Our AHJ has asked for the full loss to be included and this will nearly
>>>> double the pressure required at a K-36 sprinkler from 345kPa(50psi) to
>>>> around 600kPa(90psi), if clamp tees are used. There is quite a variation
>>>> between Brands for the stated EQL.
>>>>
>>>> Makes life difficult if site staff change from welded to mechanical
>>>> fittings and then buy a variety of brands!!!!!
>>>>
>>>>
>>>>
>>>> Thanks for the responses.
>>>>
>>>> Russell Gregory
>>>>
>>>>
>>>>
>>>>
>>>>
>>>> *From:* Sprinklerforum [mailto:sprinklerforum-bounces
>>>> @lists.firesprinkler.org] *On Behalf Of *Parsley Consulting
>>>> *Sent:* Friday, 28 October 2016 3:56 AM
>>>> *To:* [email protected]
>>>> *Subject:* Re: Hydraulic losses when using a Mechanical Tee on
>>>> Sprinkler Outlet
>>>>
>>>>
>>>>
>>>> Russell,
>>>>     Mark and Todd are both correct.
>>>>     If the sprinkler is directly attached to the fitting, in this case
>>>> the welded outlet or mechanical tee, the friction loss through that fitting
>>>> is excluded from the hydraulic calculations, per NFPA 13, 23.4.4.7.1(9).  I
>>>> don't know that I've ever had a set of calculations sent back with a
>>>> comment that I didn't include the friction loss equivalent for the welded
>>>> outlet or mechanical tee which was directly attached to the sprinkler.
>>>>     Todd's comment is valid as well, however it's worth noting, I
>>>> believe, that when you're designing a system with flexible drops you must
>>>> account for the equivalent length of the device, using the manufacturer's
>>>> data.  My own experience has been that those values are substantial.
>>>> sincerely,
>>>>
>>>>
>>>> *Ken Wagoner, SET *
>>>>
>>>>
>>>> *Parsley Consulting 350 West 9th Avenue, Suite 206 Escondido,
>>>> California 92025 *
>>>> *Phone 760-745-6181 <760-745-6181> **Visit our website
>>>> <http://www.parsleyconsulting.com/> *
>>>>
>>>> On 10/27/2016 1:30 AM, Russell & Carol Gregory wrote:
>>>>
>>>> I posted a message on this subject early this month but only received
>>>> one reply(thanks Brad). This was surprising as I thought it was a serious
>>>> problem if the full EQL for tee had to be added to calculations. Especially
>>>> if the change was made on-site after design had been completed with welded
>>>> outlets.
>>>>
>>>> So my query is as follows;
>>>>
>>>>
>>>>
>>>> When calculating a Range Pipe with welded threaded outlets for
>>>> sprinklers it is not necessary to include a loss for the water leaving the
>>>> range pipe and entering the sprinkler. The total pressure is assumed to
>>>> apply to the sprinkler orfice.
>>>>
>>>> This means that a 80nb pipe with a 25nb outlet and a k36 sprinkler does
>>>> not have an additional loss added for the outlet fitting.
>>>>
>>>>
>>>>
>>>> If I change my design and fabricate the 80nb range pipe with 80 x 25
>>>> Mechanical Tees for the Sprinkler outlet do I have to apply an additional
>>>> loss factor for that fitting? The published EQL for Mech tees varies
>>>> greatly between brands,( 0.8m up to 2.4m). This means a head pressure of
>>>> 345kPa would need around 600kPa in the range if this additional loss is
>>>> added.
>>>>
>>>>
>>>>
>>>> Questions;
>>>>
>>>> 1.       Is it common practice in USA to use 80 x 25 clamp/mechanical
>>>> tees  for attaching large bore Storage Sprinklers directly to 80nb range
>>>> pipes?
>>>>
>>>> 2.       Is it common practice to add in an additional loss for the
>>>> clamp tee, in the hydraulic calculation, where the sprinkler is directly
>>>> fitted to the tee outlet?
>>>>
>>>>
>>>>
>>>> I would appreciate the Forum members advise as to what is the standard
>>>> practice in the USA.
>>>>
>>>>
>>>>
>>>> Russell Gregory
>>>>
>>>> Christchurch
>>>>
>>>> New Zealand
>>>>
>>>>
>>>>
>>>> e-mail [email protected]
>>>>
>>>>
>>>>
>>>>
>>>>
>>>> _______________________________________________
>>>>
>>>> Sprinklerforum mailing list
>>>>
>>>> [email protected]
>>>>
>>>> http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org
>>>>
>>>>
>>>>
>>>> _______________________________________________
>>>> Sprinklerforum mailing list
>>>> [email protected]
>>>> http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-f
>>>> iresprinkler.org
>>>>
>>>>
>>>
>>>
>>> --
>>> Ron Greenman
>>>
>>> 4110 Olson Dr., NW
>>> Gig Harbor, WA 98335
>>>
>>> [email protected]
>>>
>>> 253.576.9700
>>>
>>> The Universe is monstrously indifferent to the presence of man. -Werner
>>> Herzog, screenwriter, film director, author, actor and opera
>>> director (1942-)
>>>
>>> _______________________________________________
>>> Sprinklerforum mailing list
>>> [email protected]
>>> http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-f
>>> iresprinkler.org
>>>
>>>
>> _______________________________________________
>> Sprinklerforum mailing list
>> [email protected]
>> http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-
>> firesprinkler.org
>>
>>
>
>
> --
> Ron Greenman
>
> 4110 Olson Dr., NW
> Gig Harbor, WA 98335
>
> [email protected]
>
> 253.576.9700
>
> The Universe is monstrously indifferent to the presence of man. -Werner
> Herzog, screenwriter, film director, author, actor and opera
> director (1942-)
>
> _______________________________________________
> Sprinklerforum mailing list
> [email protected]
> http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.
> org
>
>
> _______________________________________________
> Sprinklerforum mailing list
> [email protected]
> http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.
> org
>
>
_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org

Reply via email to