No offense Travis, but I would rather let Roland be the judge of that,.,.,K?
On Oct 29, 2016 2:10 PM, "Travis Mack" <[email protected]> wrote:

> As Steve said the horse is dead.
>
> I hope everyone has a great weekend.
>
> Travis Mack, SET
> MFP Design, LLC
> "Follow" us on Facebook: https://www.facebook.com/pages/MFP-Design-
> LLC/92218417692
> Send large files to MFP Design via:
> https://www.hightail.com/u/MFPDesign
>
> Sent from my iPhone
>
> On Oct 29, 2016, at 11:06 AM, Brad Casterline <[email protected]>
> wrote:
>
> Damien -
> I think so, using Hazen-Williams. It disturbs me though that a fitting or
> valve, installed and anchored, can shrink or grow depending on the flow.
> With Darcy-Weisbach, using a "K-Value" for fittings and valves that
> doesn't happen.
> This is because friction head is directly proportional to the square of
> the velocity, and D-W is all about the velocity, whereas H-W gets similar
> results with much less effort over an acceptable range of fire protection
> velocities.
>
> Ron -
> I kicked myself right after I posted that for not saying something like,
> "the only reason I can think of why a 1" threaded tee or 1" pipe-o-let is
> EQL=5ft whilst a 1" mechanical tee is EQL=11ft is it must have something to
> do with gaskets.
> (I miss the aroma of warm oil, taking smoke breaks in the fab shop-- been
> 15 years-- even then that's the closest I got to the reality of mech tees).
>
> Steve -
> I was just trying to help Russell. I think he would have had more replies
> if I had just stayed out of it.
> He contacted me off Forum, I said I would see if I could get a formal
> interp, I got one, and here we are.
> The problem is, I'm not sure the question was expressed adequately, I
> apologized for letting him down, he is back...
> You are a TC member-- is it a dead horse or not?
> I could care less how it turns out-- I do what my P.E. tells me to do.
>
> Brad
> On Oct 29, 2016 12:03 PM, "Steve Leyton" <[email protected]>
> wrote:
>
>> There's a saying in our business that we design systems with computers,
>> use lasers to measure pipe for fabrication, then mark with a paint  pen and
>> cut it with a chop saw. In other words there are some weak links in the
>> chain of events that we take for granted every day.
>>
>> The hydraulic design method that we use, the number of sprinklers and
>> sizes of design areas that we include in our models, all provide for
>> conservative safety factors. So to the point of whether or not a rubber
>> gasket reduces the inside diameter compared to a weld-o-let or a threaded
>> fitting, my reaction to that is so what, who cares?
>>
>> All these formulas and algorithms and commentary amount to a whole lot of
>> over-analysis and here's why: if you were to actually account for that
>>  hundredth or thousandth an inch, the impact would be an almost
>> indiscernibly higher starting pressure at the end sprinkler. Thereafter,
>> you would have an almost indiscernible lower net K-factor at each
>> successive sprinkler thus reducing overflow,making the system demand lower
>> by a fraction of a fraction of a PSI here and a GPM there.
>>
>> So if you want to spend an extra 3 or 4 hours per calc boilng down these
>> metrics, be my guest but as far as this discussion thread is concerned I'm
>> pretty sure the horse is dead and beyond resuscitation.
>>
>>
>> Steve
>>
>>
>> -------- Original message --------
>> From: "rongreenman ." <[email protected]>
>> Date: 10/29/16 9:44 AM (GMT-08:00)
>> To: [email protected]
>> Subject: Re: Hydraulic losses when using a Mechanical Tee on Sprinkler
>> Outlet
>>
>> In y experience with mech tees I always used the type with the lip so the
>> hole size was substantially bigger for it than a elder outlet and the
>> rubber was well away from the hole. That aside dramatic is a pretty heady
>> word Brad (pun intended). The fitting the head is screwed into, including
>> welded outlets and mech tees, do not need to be calculated per NFPA. Ig the
>> listing requires it then that would trump the standard but to my knowledge
>> no head requires that fitting be included. Given all the slop in the model
>> we use, and that it is a model I'm always amazed that a bunch of
>> engineering types act like it is an actual and mathematically accurate
>> representation of what goes in each piece  of the system in all cases.
>>
>> On Sat, Oct 29, 2016 at 9:23 AM, Brad Casterline <[email protected]>
>> wrote:
>>
>>> This is actually pretty dramatic Ron. In Russell's case, if the K25 head
>>> is in a 1" welded pipe-o-let the pressure required at the branch line is
>>> the same as at the head, where as if it is in a 1" mechanical tee the
>>> pressure required at the branch line is the same as if the head was on a 1"
>>> x 11'-0" sprig or drop!
>>>
>>> Of course if the K for a K25 was established when it was in a 1" mech
>>> tee, it could rightly be excluded.
>>>
>>> Both welded outlets and mech tees have similar hole sizes, but I think
>>> the gaskets on mech tees reduce the AREA of the hole, which plays the
>>> biggest part of the ultimate Coefficient of Discharge, aka, K-Factor.
>>>
>>> Just my two no nonsense :)
>>>
>>> Brad
>>> On Oct 29, 2016 11:02 AM, "rongreenman ." <[email protected]> wrote:
>>>
>>>> Are we once again worrying about the difference between 0.003 psi and
>>>> 0.004 psi?
>>>>
>>>>  If I recall the number we're trying to compare demand against supply
>>>> is based on a formulae with a constant (average), an average C-factor of
>>>> deterioration based on variable conditions over many years, a nominal
>>>> diameter, and a velocity pressure determined by holding a pitot in a stream
>>>> of water that's trying to rip the pitot out of your had while you take an
>>>> average reading from a bouncing gauge that has a +/– built in. Then we do
>>>> the math, round to the nearest 50 gpm, and apply it to a graph so small
>>>> that the width of the line has an effect.
>>>>
>>>> And as Brad said the fitting is calculated into the K factor of the
>>>> sprinkler. And as someone else noted the flexible drop is a drop, not a
>>>> fitting. It has a fitting the sprinkler screws into. It also has a friction
>>>> loss value that has to be an average as it doesn't take the curves into
>>>> account. And do we calculate the gain from the elevation change?
>>>>
>>>> On Fri, Oct 28, 2016 at 8:33 AM, Brad Casterline <
>>>> [email protected]> wrote:
>>>>
>>>>> Here is my original reply, for what it's worth...
>>>>>
>>>>>
>>>>>
>>>>>
>>>>>
>>>>> Russell,
>>>>>
>>>>>
>>>>>
>>>>> My understanding is we do not have to figure the loss for the fitting
>>>>> the
>>>>>
>>>>> sprinkler is in because when the K Factor was being established it was
>>>>> in a
>>>>>
>>>>> fitting.
>>>>>
>>>>> NFPA 13 (2016) 23.4.4.8.1 (9) confirms that.
>>>>>
>>>>> But it's a good question because we're supposed to use a manufacturer's
>>>>>
>>>>> published loss if they have one.
>>>>>
>>>>> So would it make sense to, if the published loss is greater, subtract
>>>>> the
>>>>>
>>>>> loss shown in 13, and include that difference?
>>>>>
>>>>>
>>>>>
>>>>> Brad
>>>>>
>>>>>
>>>>>
>>>>>
>>>>> ------------------------------
>>>>>
>>>>> *From:* Sprinklerforum [mailto:sprinklerforum-bounces
>>>>> @lists.firesprinkler.org] *On Behalf Of *Brad Casterline
>>>>> *Sent:* Friday, October 28, 2016 10:19 AM
>>>>> *To:* [email protected]
>>>>> *Subject:* RE: Hydraulic losses when using a Mechanical Tee on
>>>>> Sprinkler Outlet
>>>>>
>>>>>
>>>>>
>>>>> Here is the e-mail I sent to our in-office guy whom submits questions
>>>>> to NFPA:
>>>>>
>>>>>
>>>>>
>>>>>
>>>>>
>>>>> *****
>>>>>
>>>>> "From NFPA 13- 2016
>>>>>
>>>>>
>>>>>
>>>>>
>>>>>
>>>>> *23.4.3.1.1 *Table 23.4.3.1.1 shall be used to determine the
>>>>>
>>>>> equivalent length of pipe for fittings and devices unless
>>>>> manufacturer’s
>>>>>
>>>>> test data indicate that other factors are appropriate.
>>>>>
>>>>>
>>>>>
>>>>> *23.4.4.8.1*
>>>>>
>>>>> (9) Friction loss shall be excluded for the fitting directly
>>>>>
>>>>> connected to a sprinkler.
>>>>>
>>>>>
>>>>>
>>>>>
>>>>>
>>>>> A 1" tee in the table is 5' equivalent length.
>>>>>
>>>>> A mechanical tee with 1" outlet is 11' equivalent length.
>>>>>
>>>>>
>>>>>
>>>>> If the sprinkler is directly attached to the mechanical tee do we
>>>>> still exclude it?"
>>>>>
>>>>> *****
>>>>>
>>>>>
>>>>>
>>>>>
>>>>>
>>>>> When we got the recent response Gregory pasted, I asked the guy for
>>>>> the exact wording of the submitted question, but since submitting a
>>>>> question on-line 'disappears' once submitted, it was not available. He 
>>>>> said
>>>>> he reworded mine a little, but thinks the last line (which is what this is
>>>>> all about) was clear.
>>>>>
>>>>>
>>>>>
>>>>> Personally, I like my original reply to Russell, but I'm just a Tech,
>>>>> so there's that :)
>>>>>
>>>>>
>>>>>
>>>>> Brad
>>>>>
>>>>>
>>>>>
>>>>>
>>>>> ------------------------------
>>>>>
>>>>> *From:* Sprinklerforum [mailto:sprinklerforum-bounces
>>>>> @lists.firesprinkler.org] *On Behalf Of *Russell & Carol Gregory
>>>>> *Sent:* Thursday, October 27, 2016 10:01 PM
>>>>> *To:* [email protected]
>>>>> *Subject:* RE: Hydraulic losses when using a Mechanical Tee on
>>>>> Sprinkler Outlet
>>>>>
>>>>>
>>>>>
>>>>> Ken, and others,
>>>>>
>>>>> We have been excluding the loss for a welded outlet or a mech tee when
>>>>> a sprinkler is directly attached. If the outlet is to feed a pipe
>>>>> (regardless of length) then the standard loss for a branch on tee would be
>>>>> used, however if the Manufacturers Data Sheet states that the loss in a
>>>>> clamp tee is greater than the loss in Table 23.4.3.1.1 (NFPA 13 2016) for 
>>>>> a
>>>>> side outlet of tee, THEN the ADDITIONAL LOSS shall be included. I think
>>>>> they should say the Higher EQL Loss should be used so you don’t use less
>>>>> than the Table Loss.
>>>>>
>>>>>
>>>>>
>>>>> Here is a recent NFPA Response to a similar question;
>>>>>
>>>>>
>>>>>
>>>>> Table 23.4.3.1.1 is required to be used to determine the equivalent
>>>>> length
>>>>>
>>>>> of pipe for fittings and devices unless manufacturers' test data
>>>>> indicate
>>>>>
>>>>> that other factors are appropriate. In your situation since the
>>>>> manufacturer
>>>>>
>>>>> specifies an equivalent length of 11 feet, you are required to use 11
>>>>> feet
>>>>>
>>>>> for the equivalent length.
>>>>>
>>>>>
>>>>>
>>>>> In regards to Section 23.4.4.8(9) of the 2016 edition of NFPA 13, if an
>>>>>
>>>>> extension is used with a tee, that tee must be included in the
>>>>> hydraulic
>>>>>
>>>>> calculations. The allowance to use an extension is restricted to
>>>>> sprinklers
>>>>>
>>>>> with a relative low discharge volume. They will most likely be used for
>>>>>
>>>>> minor adjustments to interface with the ceiling.
>>>>>
>>>>>
>>>>>
>>>>> This answers some of the other Forum responses to my questions but
>>>>> does not answer my problem.
>>>>>
>>>>>
>>>>>
>>>>> What I would like to see is a practical flow test done with a K36 (us
>>>>> k25) head and see if there is a significant difference between welded
>>>>> outlet, threaded tee and clamp tee. Does anyone know if this has been
>>>>> done???
>>>>>
>>>>>
>>>>>
>>>>> Our AHJ has asked for the full loss to be included and this will
>>>>> nearly double the pressure required at a K-36 sprinkler from 345kPa(50psi)
>>>>> to around 600kPa(90psi), if clamp tees are used. There is quite a 
>>>>> variation
>>>>> between Brands for the stated EQL.
>>>>>
>>>>> Makes life difficult if site staff change from welded to mechanical
>>>>> fittings and then buy a variety of brands!!!!!
>>>>>
>>>>>
>>>>>
>>>>> Thanks for the responses.
>>>>>
>>>>> Russell Gregory
>>>>>
>>>>>
>>>>>
>>>>>
>>>>>
>>>>> *From:* Sprinklerforum [mailto:sprinklerforum-bounces
>>>>> @lists.firesprinkler.org] *On Behalf Of *Parsley Consulting
>>>>> *Sent:* Friday, 28 October 2016 3:56 AM
>>>>> *To:* [email protected]
>>>>> *Subject:* Re: Hydraulic losses when using a Mechanical Tee on
>>>>> Sprinkler Outlet
>>>>>
>>>>>
>>>>>
>>>>> Russell,
>>>>>     Mark and Todd are both correct.
>>>>>     If the sprinkler is directly attached to the fitting, in this case
>>>>> the welded outlet or mechanical tee, the friction loss through that 
>>>>> fitting
>>>>> is excluded from the hydraulic calculations, per NFPA 13, 23.4.4.7.1(9).  
>>>>> I
>>>>> don't know that I've ever had a set of calculations sent back with a
>>>>> comment that I didn't include the friction loss equivalent for the welded
>>>>> outlet or mechanical tee which was directly attached to the sprinkler.
>>>>>     Todd's comment is valid as well, however it's worth noting, I
>>>>> believe, that when you're designing a system with flexible drops you must
>>>>> account for the equivalent length of the device, using the manufacturer's
>>>>> data.  My own experience has been that those values are substantial.
>>>>> sincerely,
>>>>>
>>>>>
>>>>> *Ken Wagoner, SET *
>>>>>
>>>>>
>>>>> *Parsley Consulting 350 West 9th Avenue, Suite 206 Escondido,
>>>>> California 92025 *
>>>>> *Phone 760-745-6181 <760-745-6181> **Visit our website
>>>>> <http://www.parsleyconsulting.com/> *
>>>>>
>>>>> On 10/27/2016 1:30 AM, Russell & Carol Gregory wrote:
>>>>>
>>>>> I posted a message on this subject early this month but only received
>>>>> one reply(thanks Brad). This was surprising as I thought it was a serious
>>>>> problem if the full EQL for tee had to be added to calculations. 
>>>>> Especially
>>>>> if the change was made on-site after design had been completed with welded
>>>>> outlets.
>>>>>
>>>>> So my query is as follows;
>>>>>
>>>>>
>>>>>
>>>>> When calculating a Range Pipe with welded threaded outlets for
>>>>> sprinklers it is not necessary to include a loss for the water leaving the
>>>>> range pipe and entering the sprinkler. The total pressure is assumed to
>>>>> apply to the sprinkler orfice.
>>>>>
>>>>> This means that a 80nb pipe with a 25nb outlet and a k36 sprinkler
>>>>> does not have an additional loss added for the outlet fitting.
>>>>>
>>>>>
>>>>>
>>>>> If I change my design and fabricate the 80nb range pipe with 80 x 25
>>>>> Mechanical Tees for the Sprinkler outlet do I have to apply an additional
>>>>> loss factor for that fitting? The published EQL for Mech tees varies
>>>>> greatly between brands,( 0.8m up to 2.4m). This means a head pressure of
>>>>> 345kPa would need around 600kPa in the range if this additional loss is
>>>>> added.
>>>>>
>>>>>
>>>>>
>>>>> Questions;
>>>>>
>>>>> 1.       Is it common practice in USA to use 80 x 25 clamp/mechanical
>>>>> tees  for attaching large bore Storage Sprinklers directly to 80nb range
>>>>> pipes?
>>>>>
>>>>> 2.       Is it common practice to add in an additional loss for the
>>>>> clamp tee, in the hydraulic calculation, where the sprinkler is directly
>>>>> fitted to the tee outlet?
>>>>>
>>>>>
>>>>>
>>>>> I would appreciate the Forum members advise as to what is the standard
>>>>> practice in the USA.
>>>>>
>>>>>
>>>>>
>>>>> Russell Gregory
>>>>>
>>>>> Christchurch
>>>>>
>>>>> New Zealand
>>>>>
>>>>>
>>>>>
>>>>> e-mail [email protected]
>>>>>
>>>>>
>>>>>
>>>>>
>>>>>
>>>>> _______________________________________________
>>>>>
>>>>> Sprinklerforum mailing list
>>>>>
>>>>> [email protected]
>>>>>
>>>>> http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org
>>>>>
>>>>>
>>>>>
>>>>> _______________________________________________
>>>>> Sprinklerforum mailing list
>>>>> [email protected]
>>>>> http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-f
>>>>> iresprinkler.org
>>>>>
>>>>>
>>>>
>>>>
>>>> --
>>>> Ron Greenman
>>>>
>>>> 4110 Olson Dr., NW
>>>> Gig Harbor, WA 98335
>>>>
>>>> [email protected]
>>>>
>>>> 253.576.9700
>>>>
>>>> The Universe is monstrously indifferent to the presence of man. -Werner
>>>> Herzog, screenwriter, film director, author, actor and opera
>>>> director (1942-)
>>>>
>>>> _______________________________________________
>>>> Sprinklerforum mailing list
>>>> [email protected]
>>>> http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-f
>>>> iresprinkler.org
>>>>
>>>>
>>> _______________________________________________
>>> Sprinklerforum mailing list
>>> [email protected]
>>> http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-f
>>> iresprinkler.org
>>>
>>>
>>
>>
>> --
>> Ron Greenman
>>
>> 4110 Olson Dr., NW
>> Gig Harbor, WA 98335
>>
>> [email protected]
>>
>> 253.576.9700
>>
>> The Universe is monstrously indifferent to the presence of man. -Werner
>> Herzog, screenwriter, film director, author, actor and opera
>> director (1942-)
>>
>> _______________________________________________
>> Sprinklerforum mailing list
>> [email protected]
>> http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-
>> firesprinkler.org
>>
>> _______________________________________________
> Sprinklerforum mailing list
> [email protected]
> http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.
> org
>
>
> _______________________________________________
> Sprinklerforum mailing list
> [email protected]
> http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.
> org
>
>
_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org

Reply via email to