We need a lot more info.

What is the .20 design criteria based on?  (What table, chapter, etc of NFPA 
13) What height storage, height of ceiling, what type of arrangement of Class 
III.

Is this shelf storage and not racks?


Craig L. Prahl
Fire Protection Group Lead/SME
CH2M
200 Verdae Blvd.
Greenville, SC  29607
Direct - 864.920.7540
Fax - 864.920.7129
CH2MHILL Extension  77540
[email protected]


From: Sprinklerforum [mailto:[email protected]] On 
Behalf Of Tim Easter
Sent: Monday, November 28, 2016 10:24 AM
To: [email protected]
Subject: HELP - Class III [EXTERNAL]

I have a storage warehouse with Class III commodities. I was told to 150% 
increase the density from .2 to .3 gpm/sf because of 36" shelf depth. I cannot 
find this requirement within NFPA 13. Can anyone help?



Tim Easter, PE
[Description: Description: Description: 
http://www.wwgfp.com/MailLogo.gif]<http://www.wwgfp.com/Brochere.jpg>
522 Stockton Street
Jacksonville, FL 32204
Office: (904) 387-7973  Cell: (904) 476-4325  Fax: (904) 394-7261





     This electronic message contains information from W. W. Gay Fire 
Protection, Inc., which may be confidential or privileged. The information is 
for use of the individual or the entity named above. If you are not the 
intended recipient, please be aware that any disclosure, copying, distribution 
or use of the contents of this message is prohibited. If you have received this 
electronic transmission in error, please notify us immediately at 
1-904-387-7973.

_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org

Reply via email to