We need a lot more info. What is the .20 design criteria based on? (What table, chapter, etc of NFPA 13) What height storage, height of ceiling, what type of arrangement of Class III.
Is this shelf storage and not racks? Craig L. Prahl Fire Protection Group Lead/SME CH2M 200 Verdae Blvd. Greenville, SC 29607 Direct - 864.920.7540 Fax - 864.920.7129 CH2MHILL Extension 77540 [email protected] From: Sprinklerforum [mailto:[email protected]] On Behalf Of Tim Easter Sent: Monday, November 28, 2016 10:24 AM To: [email protected] Subject: HELP - Class III [EXTERNAL] I have a storage warehouse with Class III commodities. I was told to 150% increase the density from .2 to .3 gpm/sf because of 36" shelf depth. I cannot find this requirement within NFPA 13. Can anyone help? Tim Easter, PE [Description: Description: Description: http://www.wwgfp.com/MailLogo.gif]<http://www.wwgfp.com/Brochere.jpg> 522 Stockton Street Jacksonville, FL 32204 Office: (904) 387-7973 Cell: (904) 476-4325 Fax: (904) 394-7261 This electronic message contains information from W. W. Gay Fire Protection, Inc., which may be confidential or privileged. The information is for use of the individual or the entity named above. If you are not the intended recipient, please be aware that any disclosure, copying, distribution or use of the contents of this message is prohibited. If you have received this electronic transmission in error, please notify us immediately at 1-904-387-7973.
_______________________________________________ Sprinklerforum mailing list [email protected] http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org