Table 13.2.1 Height is 12', the shelf depth is 36". Height of celling is
25'.
Tim Easter, ?
W.W. Gay Fire & Integrated Systems, Inc.
522 Stockton Street
Jacksonville, FL 32204
Phone: (904) 387-7973 Cell: (904) 476-4325 Fax: (904) 394-7261
This electronic message contains information from W. W. Gay Fire
Protection, Inc., which may be confidential or privileged. The information
is for use of the individual or the entity named above. If you are not the
intended recipient, please be aware that any disclosure, copying,
distribution or use of the contents of this message is prohibited. If you
have received this electronic transmission in error, please notify us
immediately at 1-904-387-7973.
From: [email protected] [mailto:[email protected]]
Sent: Monday, November 28, 2016 10:47 AM
To: [email protected]
Subject: RE: HELP - Class III
We need a lot more info.
What is the .20 design criteria based on? (What table, chapter, etc of NFPA
13) What height storage, height of ceiling, what type of arrangement of
Class III.
Is this shelf storage and not racks?
Craig L. Prahl
Fire Protection Group Lead/SME
CH2M
200 Verdae Blvd.
Greenville, SC 29607
Direct - 864.920.7540
Fax - 864.920.7129
CH2MHILL Extension 77540
[email protected]
From: Sprinklerforum [mailto:[email protected]]
On Behalf Of Tim Easter
Sent: Monday, November 28, 2016 10:24 AM
To: [email protected]
Subject: HELP - Class III [EXTERNAL]
I have a storage warehouse with Class III commodities. I was told to 150%
increase the density from .2 to .3 gpm/sf because of 36" shelf depth. I
cannot find this requirement within NFPA 13. Can anyone help?
Tim Easter, PE
<http://www.wwgfp.com/Brochere.jpg> Description: Description: Description:
http://www.wwgfp.com/MailLogo.gif
522 Stockton Street
Jacksonville, FL 32204
Office: (904) 387-7973 Cell: (904) 476-4325 Fax: (904) 394-7261
This electronic message contains information from W. W. Gay Fire
Protection, Inc., which may be confidential or privileged. The information
is for use of the individual or the entity named above. If you are not the
intended recipient, please be aware that any disclosure, copying,
distribution or use of the contents of this message is prohibited. If you
have received this electronic transmission in error, please notify us
immediately at 1-904-387-7973.
_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org