not many items have a percentage increase (and both that come to mind are for Racks less than 25 ft). Normally, as already stated, that factor is simply part of determining the storage arrangement which then takes you to the appropriate section (or line in the Table).
Roland Roland Huggins, PE - VP Engineering American Fire Sprinkler Assn. --- Fire Sprinklers Saves Lives Dallas, TX http://www.firesprinkler.org <http://www.firesprinkler.org/> > On Nov 28, 2016, at 7:24 AM, Tim Easter <[email protected]> wrote: > > I have a storage warehouse with Class III commodities. I was told to 150% > increase the density from .2 to .3 gpm/sf because of 36” shelf depth. I > cannot find this requirement within NFPA 13. Can anyone help? > > > > Tim Easter, PE > <http://www.wwgfp.com/Brochere.jpg> > 522 Stockton Street > Jacksonville, FL 32204 > Office: (904) 387-7973 Cell: (904) 476-4325 Fax: (904) 394-7261 > > > > > > This electronic message contains information from W. W. Gay Fire > Protection, Inc., which may be confidential or privileged. The information is > for use of the individual or the entity named above. If you are not the > intended recipient, please be aware that any disclosure, copying, > distribution or use of the contents of this message is prohibited. If you > have received this electronic transmission in error, please notify us > immediately at 1-904-387-7973. > > _______________________________________________ > Sprinklerforum mailing list > [email protected] > <mailto:[email protected]> > http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org > <http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org>
_______________________________________________ Sprinklerforum mailing list [email protected] http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org