Tim,
Thanks for the clarifications. I'll add a couple of notes for you,
from just a quick look at what you've noted.
* If the depth is greater than 30", this is _*not*_ shelf storage, per
the definitions in NFPA 13
o Since the depth exceeds that allowed for "shelf storage", I
would regard this as "single row rack" storage, per 3.9.3.7.7,
as the depth does not exceed 6'-0"
* As the storage is maxed out at 12' high, you are following the
guidance from 16.2.1.2.1, for class III on racks to be protected per
Chapter 13 for miscellaneous storage.
* Table 13.2.1 does indeed tell you that "single row rack storage" of
Class III to _<_ 12'-0", can be protected with a design curve
matching OH2, with a combined hose demand of 250 gpm, for a duration
of 90 minutes. All well and good.
* However. I'm basing what I'm about to say on my own estimate that
the shelves are solid. Make sure that you carefully review the
information in 13.1.3.1 regarding solid rack shelves. If the area
you're protecting _*does not*_ conform with the definition of
miscellaneous storage in 3.9.1.18, then you're going to have to look
at providing in-rack sprinklers, per 16.1.6. The one that appears
most applicable to the conditions you describe is 16.1.6.2.
o Miscellaneous storage criteria
+ Does not exceed 12'-0" in height
+ Is not the primary use of the building (incidental to other use)
+ Not more than 10% of the building area, or
+ Not more than 4,000 ft² of the sprinklered area, which ever
is greater
+ Does not exceed 1,000 ft² in one area
+ Is separated from other storage areas by _>_ 25'-0"
That's my take.
sincerely,
*Ken Wagoner, SET
*Parsley Consulting***
*350 West 9th Avenue, Suite 206
*Escondido, California 92025
*****Phone 760-745-6181*
Visit our website <http://www.parsleyconsulting.com/> ***
On 11/28/2016 8:11 AM, Tim Easter wrote:
Table 13.2.1 Height is 12’, the shelf depth is 36”. Height of celling
is 25’.
**
**
*Tim Easter*,*?*
*W.W. Gay Fire & Integrated Systems, Inc.***
*522 Stockton Street***
*Jacksonville, FL 32204***
*Phone: (904) 387-7973 Cell: (904) 476-4325 Fax: (904) 394-7261***
*This electronic message contains information from W. W. Gay Fire
Protection, Inc., which may be confidential or privileged. The
information is for use of the individual or the entity named above. If
you are not the intended recipient, please be aware that any
disclosure, copying, distribution or use of the contents of this
message is prohibited. If you have received this electronic
transmission in error, please notify us immediately at 1-904-387-7973.***
*From:*[email protected] [mailto:[email protected]]
*Sent:* Monday, November 28, 2016 10:47 AM
*To:* [email protected]
*Subject:* RE: HELP - Class III
We need a lot more info.
What is the .20 design criteria based on? (What table, chapter, etc
of NFPA 13) What height storage, height of ceiling, what type of
arrangement of Class III.
Is this shelf storage and not racks?
*Craig L. Prahl**
*Fire Protection Group Lead/SME
*CH2M*
200 Verdae Blvd.
Greenville, SC 29607
Direct - 864.920.7540
Fax - 864.920.7129
CH2MHILL Extension 77540
[email protected] <mailto:[email protected]>
*From:* Sprinklerforum
[mailto:[email protected]] *On Behalf Of
*Tim Easter
*Sent:* Monday, November 28, 2016 10:24 AM
*To:* [email protected]
*Subject:* HELP - Class III [EXTERNAL]
I have a storage warehouse with Class III commodities. I was told to
150% increase the density from .2 to .3 gpm/sf because of 36” shelf
depth. I cannot find this requirement within NFPA 13. Can anyone help?
**
**
*Tim Easter*,*PE*
Description: Description: Description:
http://www.wwgfp.com/MailLogo.gif <http://www.wwgfp.com/Brochere.jpg>
*522 Stockton Street*
*Jacksonville, FL 32204*
*Office: (904) 387-7973 Cell: (904) 476-4325 Fax: (904) 394-7261*
* This electronic message contains information from W. W. Gay Fire
Protection, Inc., which may be confidential or privileged. The
information is for use of the individual or the entity named above. If
you are not the intended recipient, please be aware that any
disclosure, copying, distribution or use of the contents of this
message is prohibited. If you have received this electronic
transmission in error, please notify us immediately at 1-904-387-7973.***
_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org
_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org