Heat trace systems for fire protection are to be Listed for their intended 
purpose.  You need to look at the listing to see what the system’s installation 
limitations are.  Some systems may only be used for pipe up to a certain size 
for example.

No you cannot use heat tape on system valves.

The systems are also to be electrically supervised, typically accomplished 
through the fire alarm system.

See 2013, NFPA 13, 8.16.4.1.4 – 8.16.4.1.4.2 for more info.

NFPA 13, 2013: 7.2.5.2.3 Heat tape shall not be used in lieu of heated valve 
enclosures to protect the dry pipe valve and supply pipe against freezing.
This is under Dry Pipe Valves, there is also similar verbiage under preaction 
and deluge valves in 7.3.1.8.2.3 since dry, preaction or deluge would be the 
most likely systems used where the system could be subject to freezing.  it 
would be assumed that a wet pipe system valve would automatically be located in 
a heated area.




Craig L. Prahl
Fire Protection Group Lead/SME
CH2M
200 Verdae Blvd.
Greenville, SC  29607
Direct - 864.920.7540
Fax - 864.920.7129
CH2MHILL Extension  77540
[email protected]


From: Sprinklerforum [mailto:[email protected]] On 
Behalf Of Dewayne Martinez
Sent: Wednesday, November 30, 2016 11:17 AM
To: [email protected]
Subject: pipe heat trace [EXTERNAL]

I need to heat trace some standpipe feed mains in a parking garage when running 
from the riser room to the stairwells.  Is it acceptable to also heat trace the 
standpipe control valves?  They would prefer to keep them out of the stairwells.
Thanks,
Dewayne