I think what is being said is that you can protect the piping and that a valve 
in the line doesn’t affect the protection of the pipe.  Is that correct?

Other questions had arisen about using the heat tape to actually protect valves 
which is a different issue.


Craig L. Prahl
Fire Protection Group Lead/SME
CH2M
200 Verdae Blvd.
Greenville, SC  29607
Direct - 864.920.7540
Fax - 864.920.7129
CH2MHILL Extension  77540
[email protected]


From: Sprinklerforum [mailto:[email protected]] On 
Behalf Of Greg McGahan
Sent: Wednesday, December 07, 2016 9:41 AM
To: [email protected]
Subject: Re: pipe heat trace [EXTERNAL]

Craig,

It is against the listing to take bonnets out of hanger rings too, but there is 
hardly a condominium in in Florida that still has bonnets in the rings.

But I did my due diligence and got the answer from the manufacturer, The 
listing is not effected by the presence of valves. So for me, I am pleased with 
that. It is also not effected by by the presence of flanges. Their software 
that calculates the size and length of the their products ask for all pertinent 
information regarding valves, hangers and flanges.

Just my opinion as a guy trying to walk all the lines and still make a living.

Greg




Greg McGahan
Living Water Fire Protection, LLC<http://www.livingwaterfp.com>
1160 McKenzie Road
Cantonment, FL 32533
850-937-1850
fax 850-937-1852

On Wed, Dec 7, 2016 at 8:27 AM, 
<[email protected]<mailto:[email protected]>> wrote:
But that answer doesn’t state whether or not their listing includes heat 
tracing of valves.


Craig L. Prahl
Fire Protection Group Lead/SME
CH2M
200 Verdae Blvd.
Greenville, SC  29607
Direct - 864.920.7540<tel:(864)%20920-7540>
Fax - 864.920.7129<tel:(864)%20920-7129>
CH2MHILL Extension  77540
[email protected]<mailto:[email protected]>

From: Sprinklerforum 
[mailto:[email protected]<mailto:[email protected]>]
 On Behalf Of Greg McGahan
Sent: Wednesday, December 07, 2016 9:24 AM
To: 
[email protected]<mailto:[email protected]>
Subject: Re: pipe heat trace [EXTERNAL]

I have checked with one manufacturer concerning their listing if valves were in 
the line and their answer was that valving did not effect their listing.

So I am comfortable with using their product. From a practical standpoint I am 
100% confident that the valve will not freeze if heat traced and insulated.

Greg


Greg McGahan
Living Water Fire Protection, LLC<http://www.livingwaterfp.com>
1160 McKenzie Road
Cantonment, FL 32533
850-937-1850<tel:(850)%20937-1850>
fax 850-937-1852<tel:(850)%20937-1852>

On Mon, Dec 5, 2016 at 9:41 PM, AKS-Gmail-IMAP 
<[email protected]<mailto:[email protected]>> wrote:
It is worthwhile to note that joint and pipe failures related to pipe freezing 
are not failures located at the site where freezing takes place. Contrary to 
conventional wisdom the failures are not from ice stressing piping material. 
Instead it is the overpressure in the still liquid portions of the piping 
caused by a decrease in space, i.e. an advancing ice plug, that causes the 
breaks. The water at the break can subsequently flash freeze due to pressure 
loss giving the impression it was, “ice that done it."  A dramatic usefull 
example of this concept is the common method of using dry ice to freeze a line 
off when a shutoff valve has failed. Just make sure there is a way to relieve 
the overpressure. With this in mind there might be some instances where 
pressure relief mechanisms located in strategic locations would be a good idea.

Allan Seidel
St. Louis, MO


On Dec 5, 2016, at 2:37 PM, [email protected]<mailto:[email protected]> 
wrote:

You can only trace valves if the product says it is listed for protecting 
valves in NFPA 13 systems or something similar.

You can’t automatically assume you can do anything.  What does the listing 
state, that’s where you start.


Craig L. Prahl
Fire Protection Group Lead/SME
CH2M
200 Verdae Blvd.
Greenville, SC  29607
Direct - 864.920.7540<tel:(864)%20920-7540>
Fax - 864.920.7129<tel:(864)%20920-7129>
CH2MHILL Extension  77540
[email protected]<mailto:[email protected]>

From: Sprinklerforum [mailto:[email protected]] On 
Behalf Of Dewayne Martinez
Sent: Thursday, December 01, 2016 3:53 PM
To: 
[email protected]<mailto:[email protected]>
Subject: RE: pipe heat trace [EXTERNAL]

So I can heat trace the sectional valves since they are not specifically 
excluded per NFPA 13 and 14?

From: Sprinklerforum 
[mailto:[email protected]<mailto:[email protected]>]
 On Behalf Of Roland Huggins
Sent: Thursday, December 01, 2016 10:23 AM
To: 
[email protected]<mailto:[email protected]>
Subject: Re: pipe heat trace

NFPA 14 has similar requirements for the dry pipe valve but this is a sectional 
control valves (another term from 13 since 14 does not differentiate by name 
but it helps focus the discussion).


Roland Huggins, PE - VP Engineering
American Fire Sprinkler Assn.       ---      Fire Sprinklers Saves Lives
Dallas, TX
http://www.firesprinkler.org<http://www.firesprinkler.org/>



On Nov 30, 2016, at 12:11 PM, [email protected]<mailto:[email protected]> 
wrote:

Heat trace systems for fire protection are to be Listed for their intended 
purpose.  You need to look at the listing to see what the system’s installation 
limitations are.  Some systems may only be used for pipe up to a certain size 
for example.

No you cannot use heat tape on system valves.

The systems are also to be electrically supervised, typically accomplished 
through the fire alarm system.

See 2013, NFPA 13, 8.16.4.1.4 – 8.16.4.1.4.2 for more info.

NFPA 13, 2013: 7.2.5.2.3 Heat tape shall not be used in lieu of heated valve 
enclosures to protect the dry pipe valve and supply pipe against freezing.
This is under Dry Pipe Valves, there is also similar verbiage under preaction 
and deluge valves in 7.3.1.8.2.3 since dry, preaction or deluge would be the 
most likely systems used where the system could be subject to freezing.  it 
would be assumed that a wet pipe system valve would automatically be located in 
a heated area.




Craig L. Prahl
Fire Protection Group Lead/SME
CH2M
200 Verdae Blvd.
Greenville, SC  29607
Direct - 864.920.7540<tel:(864)%20920-7540>
Fax - 864.920.7129<tel:(864)%20920-7129>
CH2MHILL Extension  77540
[email protected]<mailto:[email protected]>

From: Sprinklerforum [mailto:[email protected]] On 
Behalf Of Dewayne Martinez
Sent: Wednesday, November 30, 2016 11:17 AM
To: 
[email protected]<mailto:[email protected]>
Subject: pipe heat trace [EXTERNAL]

I need to heat trace some standpipe feed mains in a parking garage when running 
from the riser room to the stairwells.  Is it acceptable to also heat trace the 
standpipe control valves?  They would prefer to keep them out of the stairwells.
Thanks,
Dewayne
_______________________________________________
Sprinklerforum mailing list
[email protected]<mailto:[email protected]>
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org

_______________________________________________
Sprinklerforum mailing list
[email protected]<mailto:[email protected]>
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org


_______________________________________________
Sprinklerforum mailing list
[email protected]<mailto:[email protected]>
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org


_______________________________________________
Sprinklerforum mailing list
[email protected]<mailto:[email protected]>
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org

_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org

Reply via email to