I have checked with one manufacturer concerning their listing if valves
were in the line and their answer was that valving did not effect their
listing.

So I am comfortable with using their product. From a practical standpoint I
am 100% confident that the valve will not freeze if heat traced and
insulated.

Greg


Greg McGahan
Living Water Fire Protection, LLC <http://www.livingwaterfp.com>
1160 McKenzie Road
Cantonment, FL 32533
850-937-1850
fax 850-937-1852

On Mon, Dec 5, 2016 at 9:41 PM, AKS-Gmail-IMAP <[email protected]> wrote:

> It is worthwhile to note that joint and pipe failures related to pipe
> freezing are not failures located at the site where freezing takes place.
> Contrary to conventional wisdom the failures are not from ice stressing
> piping material. Instead it is the overpressure in the still liquid
> portions of the piping caused by a decrease in space, i.e. an advancing ice
> plug, that causes the breaks. The water at the break can subsequently flash
> freeze due to pressure loss giving the impression it was, “ice that done
> it."  A dramatic usefull example of this concept is the common method of
> using dry ice to freeze a line off when a shutoff valve has failed. Just
> make sure there is a way to relieve the overpressure. With this in mind
> there might be some instances where pressure relief mechanisms located in
> strategic locations would be a good idea.
>
> Allan Seidel
> St. Louis, MO
>
>
> On Dec 5, 2016, at 2:37 PM, [email protected] wrote:
>
> You can only trace valves if the product says it is listed for protecting
> valves in NFPA 13 systems or something similar.
>
> You can’t automatically assume you can do anything.  What does the
> listing state, that’s where you start.
>
>
> *Craig L. Prahl*
>  Fire Protection Group Lead/SME
> *CH2M*
> 200 Verdae Blvd.
> Greenville, SC  29607
> Direct - 864.920.7540 <(864)%20920-7540>
> Fax - 864.920.7129 <(864)%20920-7129>
> CH2MHILL Extension  77540
> [email protected]
>
>
> *From:* Sprinklerforum [mailto:[email protected].
> org <[email protected]>] *On Behalf Of *Dewayne
> Martinez
> *Sent:* Thursday, December 01, 2016 3:53 PM
> *To:* [email protected]
> *Subject:* RE: pipe heat trace [EXTERNAL]
>
> So I can heat trace the sectional valves since they are not specifically
> excluded per NFPA 13 and 14?
>
> *From:* Sprinklerforum [mailto:[email protected].
> org] *On Behalf Of *Roland Huggins
> *Sent:* Thursday, December 01, 2016 10:23 AM
> *To:* [email protected]
> *Subject:* Re: pipe heat trace
>
> NFPA 14 has similar requirements for the dry pipe valve but this is a
> sectional control valves (another term from 13 since 14 does not
> differentiate by name but it helps focus the discussion).
>
>
> Roland Huggins, PE - VP Engineering
> American Fire Sprinkler Assn.       ---      Fire Sprinklers Saves Lives
> Dallas, TX
> http://www.firesprinkler.org
>
>
>
>
> On Nov 30, 2016, at 12:11 PM, [email protected] wrote:
>
> Heat trace systems for fire protection are to be Listed for their
> intended purpose.  You need to look at the listing to see what the
> system’s installation limitations are.  Some systems may only be used for
> pipe up to a certain size for example.
>
> No you cannot use heat tape on system valves.
>
> The systems are also to be electrically supervised, typically accomplished
> through the fire alarm system.
>
> See 2013, NFPA 13, 8.16.4.1.4 – 8.16.4.1.4.2 for more info.
>
> NFPA 13, 2013: 7.2.5.2.3 Heat tape shall not be used in lieu of heated
> valve enclosures to protect the dry pipe valve and supply pipe against
> freezing.
> This is under Dry Pipe Valves, there is also similar verbiage under
> preaction and deluge valves in 7.3.1.8.2.3 since dry, preaction or deluge
> would be the most likely systems used where the system could be subject to
> freezing.  it would be assumed that a wet pipe system valve would
> automatically be located in a heated area.
>
>
>
>
> *Craig L. Prahl*
> Fire Protection Group Lead/SME
> *CH2M*
> 200 Verdae Blvd.
> Greenville, SC  29607
> Direct - 864.920.7540 <(864)%20920-7540>
> Fax - 864.920.7129 <(864)%20920-7129>
>
> CH2MHILL Extension  77540
> [email protected]
>
>
> *From:* Sprinklerforum [mailto:[email protected].
> org <[email protected]>] *On Behalf Of *Dewayne
> Martinez
> *Sent:* Wednesday, November 30, 2016 11:17 AM
> *To:* [email protected]
> *Subject:* pipe heat trace [EXTERNAL]
>
> I need to heat trace some standpipe feed mains in a parking garage when
> running from the riser room to the stairwells.  Is it acceptable to also
> heat trace the standpipe control valves?  They would prefer to keep them
> out of the stairwells.
> Thanks,
> Dewayne
> _______________________________________________
> Sprinklerforum mailing list
> [email protected]
> http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.
> org
>
>
> _______________________________________________
> Sprinklerforum mailing list
> [email protected]
> http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.
> org
>
>
>
> _______________________________________________
> Sprinklerforum mailing list
> [email protected]
> http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.
> org
>
>
_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org

Reply via email to