The plant machines need to have 200,000 primers and 200 lbs of powder available a day for manufacture. The verbiage below comes from the code review and has been agreed to by the owner.
Small Arms Primers Quantities not exceeding 750,000 shall be permitted to be stored in a building where not more than 100,000 are stored in any one pile and where piles are at least 15 ft apart. Small arms primers not stored in accordance with 14.5.6(1) through 14.5.6(2) shall be stored in a magazine meeting the requirements of Chapter 9. Smokeless Propellants Quantities exceeding 100 Lbs, but not exceeding 800 Lbs, shall be stored in non-portable storage cabinets having walls of at least 1” thickness. But again, in your all’s opinion, is this an Ex Haz Grp I or II, or something else? Just trying to figure out if I’m looking at the project the right way. Thanks, John Paulsen – SET Crown Fire System Design 6282 Seeds Rd. Grove City, OH 43123 P – 614-782-2438 F – 614-782-2374 C – 614-348-8206 From: Sprinklerforum [mailto:sprinklerforum-boun...@lists.firesprinkler.org] On Behalf Of Charles Bamford Sent: Friday, January 20, 2017 4:15 PM To: sprinklerforum@lists.firesprinkler.org Subject: Re: Ammunition Manufacturer Paging Scott Mitchell.......... On Friday, January 20, 2017 11:27 AM, "Hinson, Ryan" <rhin...@burnsmcd.com <mailto:rhin...@burnsmcd.com> > wrote: How much DOT Class Division 1.1 (primer) and 1.3 (gunpowder)explosives will be located inside the building at any one time…and where? What blast resistance requirements are required between said explosives and the rest of the building? Where are explosives stored? Have venting considerations in coordination with suppression activation and the impact of humidity on the explosives themselves been considered? Any explosion control measures necessary or NFPA 68 and 69 considerations/requirements per NFPA 495? Where, if any, is there ‘transient storage state’ of primer boxes? This change in use needs to be reviewed/analyzed from a building Code standpoint by a knowledgeable licensed fire protection engineer. I’m very surprised there does not already appear to be one involved. Ryan L. Hinson, PE*, SET** \ Burns & McDonnell Senior Fire Protection Engineer O 952-656-3662 \ M 320-250-5404 \ F 952-229-2923 rhin...@burnsmcd.com <mailto:rhin...@burnsmcd.com> \ <http://www.burnsmcd.com/> burnsmcd.com 8201 Norman Center Drive, Suite 300 \ Bloomington, MN 55437 *Registered in: MN, PA, & TX **NICET IV - Water-Based Systems Layout From: Sprinklerforum [mailto:sprinklerforum-boun...@lists.firesprinkler.org] On Behalf Of John Paulsen Sent: Friday, January 20, 2017 1:01 PM To: sprinklerforum@lists.firesprinkler.org <mailto:sprinklerforum@lists.firesprinkler.org> Subject: Ammunition Manufacturer Good Afternoon All: I am working with the owner of an existing 28,000 Sq Ft manufacturing facility of non-combustible construction. The owner wants to convert the facility to the manufacture of small arms ammunition. He has been through the initial code review with the State, but there seem to be some “inconsistencies” with those findings. The State has determined the Use Group to be H (High Hazard) even though small arms ammunition mfg is listed in the exceptions. Under those exceptions, the Use Group would revert to the Group which best fits it’s use. In MY opinion that would be Use Group F-1. So I have laid this thing out to EH Grp II (.4 / 2500) Does anybody out there have any past experience with something along these lines that can tell me if I’m off base or not? Thanks, John Paulsen – SET Crown Fire System Design 6282 Seeds Rd. Grove City, OH 43123 P – 614-782-2438 F – 614-782-2374 C – 614-348-8206 _______________________________________________ Sprinklerforum mailing list Sprinklerforum@lists.firesprinkler.org <mailto:Sprinklerforum@lists.firesprinkler.org> http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org
_______________________________________________ Sprinklerforum mailing list Sprinklerforum@lists.firesprinkler.org http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org