See figure A*.6.5.1.2 from NFPA 13, 2016

[cid:[email protected]]





Jeff Hewitt, PE, SET, PM.SFPE
Corporate Engineer

      [cid:[email protected]]
American Fire Protection, LLC
5525 Eastcliff Industrial Loop | Birmingham, AL  35210
205-591-9111 ext. 1452 | 205-317-0918 (cell)
205-591-9990 (Fax)

          
[http://www.sfpe.org/resource/resmgr/Member_Logos/ProfessionalMember_logo.jpg]

Licensed in AL, AR, FL, GA, IL, KY, MS, MO, NC, SC, TN, TX
Fire sprinklers save lives.  Can you live without them?

Please note that any positions expressed above are my professional opinion 
only, as a member of the NFPA 13 Technical Committee, and do not represent an 
official interpretation of the NFPA 13 standard.

From: Sprinklerforum [mailto:[email protected]] On 
Behalf Of Gregory Lindholm
Sent: Wednesday, February 22, 2017 8:32 AM
To: [email protected]
Subject: 38" wide soffit along wall


I thought I knew the answer to this one, but now having second thoughts



21'-6" to roof deck, Light Hazard, 38" wide soffit along a wall @ 8'-2" above 
the floor.



Do we need sprinklers under the soffit?



1st thought was no, because it is less than 48" wide, but then looking @ NFPA 
#13 - 2016, 8.6.5.1 and 8.6.5.2, it looks like we "will need" heads under the 
soffit.



It is not like something 38" wide sitting out in the middle of a room where a 
pattern could develop around the obstruction from different areas. The edge of 
this soffit goes to the roof deck, so no pattern can develop around it.



Thoughts?


Greg Lindholm