I think that is from 2013 Jeff.

 

And Ben, here is a P.Eng and experienced designer agreeing with you, a few
years ago:

---------------------------------

RE: Obstructions against wall EC's Fig. 8.8.5.2.2(c)

 

2014-04-11 Thread Larry Keeping 

 

 For the next (2016) edition I filed a Public Input asking for the 18
minimum be dropped and for the S dimension to be changed to 1/2 S. As per
the First Draft Report, that was accepted, but of course it is susceptible
to change during the Second round of deliberations. Larry Keeping, P.Eng 

 

 

RE: Obstructions against wall EC's Fig. 8.8.5.2.2(c)

 

2014-04-11 Thread RFletcher 

 

 Glad you have submitted the comment. It will make more sense with those
changes. Ron F -Original Message- From:
[email protected]
[mailto:[email protected]] On Behalf Of Larry
Keeping Sent: Friday, April 11, 2014 9:26 AM

 

Brad

 

  _____  

From: Sprinklerforum [mailto:[email protected]]
On Behalf Of Ben Young
Sent: Wednesday, February 22, 2017 11:23 AM
To: [email protected]
Subject: Re: 38" wide soffit along wall

 

Jeff, one (an AHJ, not me) could argue that this figure doesn't apply since
there's already figure 8.6.5.1.2(c)

I personally feel that the difference between the soffit that goes all the
way up (as in 8.6.5.1.2c) vs the one shown in A.8.6.5.1.2 is ridiculous, but
at the end of the day, the latter is only in the appendix, not the main body
of the code.





Benjamin Young

 

On Wed, Feb 22, 2017 at 9:54 AM, Jeff Hewitt
<[email protected]> wrote:

See figure A*.6.5.1.2 from NFPA 13, 2016

 



 

 

 

 

 

Jeff Hewitt, PE, SET, PM.SFPE

Corporate Engineer

 

      

American Fire Protection, LLC

5525 Eastcliff Industrial Loop | Birmingham, AL  35210

205-591-9111 <tel:(205)%20591-9111>  ext. 1452 | 205-317-0918
<tel:(205)%20317-0918>  (cell)

205-591-9990 <tel:(205)%20591-9990>  (Fax)

 

 
http://www.sfpe.org/resource/resmgr/Member_Logos/ProfessionalMember_logo.jpg

 

Licensed in AL, AR, FL, GA, IL, KY, MS, MO, NC, SC, TN, TX

Fire sprinklers save lives.  Can you live without them?

 

Please note that any positions expressed above are my professional opinion
only, as a member of the NFPA 13 Technical Committee, and do not represent
an official interpretation of the NFPA 13 standard.

 

From: Sprinklerforum [mailto:sprinklerforum-
<mailto:[email protected]>
[email protected]] On Behalf Of Gregory Lindholm
Sent: Wednesday, February 22, 2017 8:32 AM
To: sprinklerforum@lists. <mailto:[email protected]>
firesprinkler.org
Subject: 38" wide soffit along wall

 

I thought I knew the answer to this one, but now having second thoughts

 

21'-6" to roof deck, Light Hazard, 38" wide soffit along a wall @ 8'-2"
above the floor.

 

Do we need sprinklers under the soffit?

 

1st thought was no, because it is less than 48" wide, but then looking @
NFPA #13 - 2016, 8.6.5.1 and 8.6.5.2, it looks like we "will need" heads
under the soffit. 

 

It is not like something 38" wide sitting out in the middle of a room where
a pattern could develop around the obstruction from different areas. The
edge of this soffit goes to the roof deck, so no pattern can develop around
it.

 

Thoughts?

 

Greg Lindholm


_______________________________________________
Sprinklerforum mailing list
Sprinklerforum@lists. <mailto:[email protected]>
firesprinkler.org
http://lists.firesprinkler.
<http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.or
g> org/listinfo.cgi/sprinklerforum-firesprinkler.org

 

_______________________________________________