So it seems that once again because we aren't part of the initial design
process, experts on the interealtion of building/life safety systems at a
detail level far above the that of most architects and engineers are not
consulted until a plan is finalized. Sad.
On Mon, May 8, 2017 at 11:33 AM Steve Leyton <[email protected]>
wrote:

> One of our local AHJ’s observed that there are UL listed assemblies for
> floor ceiling assemblies and that the addition of insulation in fact voids
> the listing of some that aren’t insulated (remember, this is sunny CA).
> So for plans submitted to that particular agency, we not only have to pick
> between the 3,000 sq. ft. (or 8-sprinkler) design area or using
> insulation.  In the case of the latter, they want a detail of the
> floor-ceiling and/or roof-ceiling assembly showing the insulation AND the
> UL listing number for the assembly.   On the sprinkler plans.
>
>
>
> At first, we were frustrated because they hadn’t codified this and we were
> just getting back plan review comments.  But I see why they’re doing it and
> I agree with this practice.
>
>
>
> Steve L.
>
>
>
> *From:* Sprinklerforum [mailto:
> [email protected]] *On Behalf Of *John
> Drucker
> *Sent:* Monday, May 08, 2017 9:29 AM
>
>
> *To:* [email protected]
> *Subject:* Re: special inspections
>
>
>
> Ahhh I was waiting for that question. Because it's in the sprinkler
> standard, noted on the sprinkler plans by the sprinkler designer, and often
> the architect nor engineer know the sprinkler designer took that option, or
> it conflicts with the architects design.
>
>
>
> As a result we deny such applications unless the insulation fill is also
> shown on the architectural plans. In New Jersey it is also an adopted
> regulation that any plans, shop drawings etc prepared by other than the
> principal designer have to be reviewed and approved by the principal
> designer with an accompanying letter at the time of submission to that
> affect. Often enough we get back from the principal designer that the
> method submitted by others is not approved.
>
> On May 8, 2017 12:14 PM, "rongreenman ." <[email protected]> wrote:
>
> Seems to me that if the architect or GC wants to fill the space with
> insulation instead of sprinkle ring it's between him and the insulator to
> get it right. If the AHJ wants to get involved then OK, but with them. If
> you don't put in sprinklers because insulation has been approved what
> business is it of the sprinkler guy?
>
> On Mon, May 8, 2017 at 10:54 AM John Drucker - Home <
> [email protected]> wrote:
>
> Members,
>
> When an interstitial space is filled entirely with non-combustible
> insulation we coordinate with the contractor and perform the inspection
> ourselves.
>
> John
>
> John Drucker, CET
> Assistant Construction Official
> Fire Protection Subcode Official
> Electrical Subcode Official
> Building Inspector
> Borough of Red Bank
> Red Bank, New Jersey
> Email: [email protected]
> Cell/Text: 732-904-6823
>
>
>
>
> _______________________________________________
> Sprinklerforum mailing list
> [email protected]
>
> http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org
>
> --
>
> Sent from Gmail Mobile
> _______________________________________________
> Sprinklerforum mailing list
> [email protected]
>
> http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org
>
-- 
Sent from Gmail Mobile
_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org

Reply via email to