Travis. Then you would be good to go in our department, we would be inspecting it and you wouldn't be writing these emails.
John Drucker Assistant Construction Official Fire & Electrical Subcode Official Building Inspector Borough of Red Bank, NJ Cell/Text 732-904-6823 On May 8, 2017 12:30 PM, "Travis Mack, SET" <[email protected]> wrote: In this project, it was shown on the architectural plans. Quite clearly called out. Travis Mack, SET MFP Design, LLC 2508 E Lodgepole Drive Gilbert, AZ 85298 480-505-9271 fax: 866-430-6107 email:[email protected]<mailto:email:[email protected]> http://www.mfpdesign.com https://www.facebook.com/pages/MFP-Design-LLC/92218417692 Send large files to us via: https://www.hightail.com/u/MFPDesign LinkedIn: https://www.linkedin.com/in/travismack On 5/8/2017 9:28 AM, John Drucker wrote: Ahhh I was waiting for that question. Because it's in the sprinkler standard, noted on the sprinkler plans by the sprinkler designer, and often the architect nor engineer know the sprinkler designer took that option, or it conflicts with the architects design. As a result we deny such applications unless the insulation fill is also shown on the architectural plans. In New Jersey it is also an adopted regulation that any plans, shop drawings etc prepared by other than the principal designer have to be reviewed and approved by the principal designer with an accompanying letter at the time of submission to that affect. Often enough we get back from the principal designer that the method submitted by others is not approved. On May 8, 2017 12:14 PM, "rongreenman ." <[email protected]><mailto:[email protected]> wrote: Seems to me that if the architect or GC wants to fill the space with insulation instead of sprinkle ring it's between him and the insulator to get it right. If the AHJ wants to get involved then OK, but with them. If you don't put in sprinklers because insulation has been approved what business is it of the sprinkler guy? On Mon, May 8, 2017 at 10:54 AM John Drucker - Home <[email protected]<mailto:[email protected]>> wrote: Members, When an interstitial space is filled entirely with non-combustible insulation we coordinate with the contractor and perform the inspection ourselves. John John Drucker, CET Assistant Construction Official Fire Protection Subcode Official Electrical Subcode Official Building Inspector Borough of Red Bank Red Bank, New Jersey Email: [email protected]<mailto:[email protected]> Cell/Text: 732-904-6823 _______________________________________________ Sprinklerforum mailing list [email protected]<mailto:[email protected]> http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org -- Sent from Gmail Mobile _______________________________________________ Sprinklerforum mailing list [email protected]<mailto:[email protected]> http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org ________________________________ [AVG logo] <http://www.avg.com/internet-security> This email has been checked for viruses by AVG antivirus software. www.avg.com<http://www.avg.com/internet-security>
_______________________________________________ Sprinklerforum mailing list [email protected] http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org
