Actually the A.7.2 explicitly states that for areas outside dwelling unit that must apply full 13 design factors, a hose stream is not required.
Roland Huggins, PE - Senior VP Engineering American Fire Sprinkler Assn. Dallas, TX http://www.firesprinkler.org <http://www.firesprinkler.org/> Fire Sprinklers Saves Lives > On Aug 8, 2017, at 10:18 AM, Jay White <[email protected]> wrote: > > Does NFPA 13R require a hose stream demand? Section A.7.2 of NFPA 13R only > reference a hose stream demand requirement of NFPA 13. The only additional > demand required in a calculation is the domestic demand if there is a common > domestic/fire main as referenced in section 9.6 of NFPA 13R. > > Jay White > Sales/Design Manager > Dynamic Fire Protection > 9771 Highway 25 South > Starkville, MS 39759 > PH: 662-312-2426 > FAX: 662-324-1545 > > > > _______________________________________________ > Sprinklerforum mailing list > [email protected] > <mailto:[email protected]> > http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org > <http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org>