Actually the A.7.2 explicitly states that for areas outside dwelling unit that 
must apply full 13 design factors, a hose stream is not required.


Roland Huggins, PE - Senior VP Engineering
American Fire Sprinkler Assn.    
Dallas, TX
http://www.firesprinkler.org <http://www.firesprinkler.org/>

Fire Sprinklers Saves Lives




> On Aug 8, 2017, at 10:18 AM, Jay White <jwh...@dynamicfirepro.com> wrote:
> 
> Does NFPA 13R require a hose stream demand? Section A.7.2 of NFPA 13R only 
> reference a hose stream demand requirement of NFPA 13. The only additional 
> demand required in a calculation is the domestic demand if there is a common 
> domestic/fire main as referenced in section 9.6 of NFPA 13R.
>  