Yes.  Yes.  Yes.

Reed A. Roisum, SET | Karges-Faulconbridge, Inc. | Senior Fire Protection 
Designer | Fargo, ND | direct: 701.552.9903 | mobile: 701.388.1352 | 
KFIengineers.com<http://www.kfiengineers.com>
From: Sprinklerforum [mailto:[email protected]] On 
Behalf Of Matthew J Willis
Sent: Friday, October 6, 2017 11:51 AM
To: [email protected]
Subject: RE: Pipe Schedule System

Don't forget the wording. System.

You bringing another U/g supply, and System Riser? One Building, one system yes?

R/
Matt



Matthew J. Willis
Project Manager
Rapid Fire Protection Inc.<http://rapidfireinc.com/>
1530 Samco Road
Rapid City, SD 57702
Office-605.348.2342
Direct Line-605.593.5063
Cell-605.391.2733
Fax:-605.348.0108

[cid:[email protected]]



From: Sprinklerforum [mailto:[email protected]] On 
Behalf Of Scott Futrell
Sent: Friday, October 6, 2017 10:47 AM
To: 
[email protected]<mailto:[email protected]>
Subject: RE: Pipe Schedule System

It's simple to me Reed.

I would not want the liability if the fire occurred in the pipe schedule system 
and that system failed to control the fire, as intended.  Knowing that it 
doesn't work is where your liability begins, in my opinion.

Scott

Office: (763) 425-1001 x 2
Cell: (612) 759-5556

From: Sprinklerforum [mailto:[email protected]] On 
Behalf Of Reed A. Roisum, SET
Sent: Friday, October 06, 2017 11:41 AM
To: 
[email protected]<mailto:[email protected]>
Subject: Pipe Schedule System

I have an existing pipe schedule system in a partially sprinklered 
building...installed in 1969.  I am doing a life safety analysis that includes 
budget estimating to provide new fire alarm and sprinklers.  The existing pipe 
schedule portion of the system is considerably higher in elevation and remote.  
It doesn't work hydraulically with the city supply.  Even when I replace the 
system with larger pipe I can't get the calc to work.

In order to install a new system or keep the existing system in place and have 
it hydraulically "work" we will need to install a fire pump.  My problem is, 
the owner may decide to just upgrade the fire alarm system and not sprinkler 
the building if we need a fire pump as the sprinkler retrofit is voluntary.

My question for the Forum is, can an existing pipe schedule system be left in 
place even if we retrofit the rest of the building and hydraulically prove the 
rest of the building?

NFPA 13, 2013 edition...
23.5 Pipe Schedules  Pipe schedules shall not be used, except in existing 
systems and in new systems or extensions to existing systems described in 
Chapter 11.  Water supplies shall conform to 11.2.2.

If I can meet the water supply requirements of Table 11.2.2.1 for Ordinary 
Hazard, which is a minimum pressure of 20 psi flowing 850 gpm then is the pipe 
schedule permitted?

It appears as though I am out of luck because of 11.2.2.6.1 Residual 
Pressure... The residual pressure requirement of Table 11.2.2.1 shall be met at 
the elevation of the highest sprinkler.

The main reason I can't get the calc to work is because of elevation.

I would assume the AHJ would be willing to work with us if the choices are... 
1. No upgrade to the sprinkler system, or 2. A fully sprinklered building with 
2000 sq ft that is pipe schedule and doesn't work hydraulically.

Any insight or ideas will be appreciated.

Reed



Reed A. Roisum, SET | Karges-Faulconbridge, Inc. | Senior Fire Protection 
Designer | Fargo, ND | direct: 701.552.9903 | mobile: 701.388.1352 | 
KFIengineers.com<http://www.kfiengineers.com>

______________________________________________________________________
This email has been scanned by the Symantec Email Security.cloud service.
For more information please visit http://www.symanteccloud.com
______________________________________________________________________

______________________________________________________________________
This email has been scanned by the Symantec Email Security.cloud service.
For more information please visit http://www.symanteccloud.com
______________________________________________________________________

______________________________________________________________________
This email has been scanned by the Symantec Email Security.cloud service.
For more information please visit http://www.symanteccloud.com
______________________________________________________________________
_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org

Reply via email to