I have a question regarding the design.
They are asking for a deluge systm. I have a total opening of 48'. I have spaced my sprinklers accordingly. The code says minimum 3 gpm per lineal foot of water curtain. With no sprinkler discharging less than 15 gpm. 48 feet x3 gpm =144 gpm 144 gpm /9 sprinklers= 16 gpm per sprinkler Did I do this correctly? Thanks for any input Troy