I have a question regarding the design.

 

They are asking for a deluge systm.

 

I have a total opening of 48'. I have spaced my sprinklers accordingly.

 

The code says minimum 3 gpm per lineal foot of water curtain. With no sprinkler 
discharging less than 15 gpm.

 

48 feet x3 gpm =144 gpm

 

144 gpm /9 sprinklers= 16 gpm per sprinkler

 

Did I do this correctly?

 

Thanks for any input

 

Troy

 

 







 

 