thanks
From: Sprinklerforum [mailto:[email protected]] On Behalf Of Jeff Normand Sent: November-03-17 9:07 AM To: [email protected] Subject: Re: PROSCENIUM CURTAIN CALCULATION 6 foot spacing on sprinklers maximum would be 8 sprinklers. 6 foot x 3 gpm/ft is 18 gpm per sprinkler for a total of 108 gpm. On Fri, Nov 3, 2017 at 7:31 AM, Trillium Fire Sprinkler Design Inc. <[email protected]> wrote: I have a question regarding the design. They are asking for a deluge systm. I have a total opening of 48'. I have spaced my sprinklers accordingly. The code says minimum 3 gpm per lineal foot of water curtain. With no sprinkler discharging less than 15 gpm. 48 feet x3 gpm =144 gpm 144 gpm /9 sprinklers= 16 gpm per sprinkler Did I do this correctly? Thanks for any input Troy _______________________________________________ Sprinklerforum mailing list [email protected] http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org