Calculator not working or brain - should be 144 gpm = 8 x 18

On Fri, Nov 3, 2017 at 9:56 AM, Trillium Fire Sprinkler Design Inc. <
[email protected]> wrote:

> thanks
>
>
>
> *From:* Sprinklerforum [mailto:[email protected].
> org] *On Behalf Of *Jeff Normand
> *Sent:* November-03-17 9:07 AM
> *To:* [email protected]
> *Subject:* Re: PROSCENIUM CURTAIN CALCULATION
>
>
>
> 6 foot spacing on sprinklers maximum would be 8 sprinklers.
>
>
>
> 6 foot x 3 gpm/ft is 18 gpm per sprinkler for a total of 108 gpm.
>
>
>
> On Fri, Nov 3, 2017 at 7:31 AM, Trillium Fire Sprinkler Design Inc. <
> [email protected]> wrote:
>
> I have a question regarding the design.
>
>
>
> They are asking for a deluge systm.
>
>
>
> I have a total opening of 48'. I have spaced my sprinklers accordingly.
>
>
>
> The code says minimum 3 gpm per lineal foot of water curtain. With no
> sprinkler discharging less than 15 gpm.
>
>
>
> 48 feet x3 gpm =144 gpm
>
>
>
> 144 gpm /9 sprinklers= 16 gpm per sprinkler
>
>
>
> Did I do this correctly?
>
>
>
> Thanks for any input
>
>
>
> Troy
>
>
>
>
>
>
>
>
>
>
>
>
>