Calculator not working or brain - should be 144 gpm = 8 x 18 On Fri, Nov 3, 2017 at 9:56 AM, Trillium Fire Sprinkler Design Inc. < [email protected]> wrote:
> thanks > > > > *From:* Sprinklerforum [mailto:[email protected]. > org] *On Behalf Of *Jeff Normand > *Sent:* November-03-17 9:07 AM > *To:* [email protected] > *Subject:* Re: PROSCENIUM CURTAIN CALCULATION > > > > 6 foot spacing on sprinklers maximum would be 8 sprinklers. > > > > 6 foot x 3 gpm/ft is 18 gpm per sprinkler for a total of 108 gpm. > > > > On Fri, Nov 3, 2017 at 7:31 AM, Trillium Fire Sprinkler Design Inc. < > [email protected]> wrote: > > I have a question regarding the design. > > > > They are asking for a deluge systm. > > > > I have a total opening of 48'. I have spaced my sprinklers accordingly. > > > > The code says minimum 3 gpm per lineal foot of water curtain. With no > sprinkler discharging less than 15 gpm. > > > > 48 feet x3 gpm =144 gpm > > > > 144 gpm /9 sprinklers= 16 gpm per sprinkler > > > > Did I do this correctly? > > > > Thanks for any input > > > > Troy > > > > > > > > > > > > > > _______________________________________________ > Sprinklerforum mailing list > [email protected] > http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler. > org > > > > _______________________________________________ > Sprinklerforum mailing list > [email protected] > http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler. > org > >
_______________________________________________ Sprinklerforum mailing list [email protected] http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org