I have always done it based on my actual sprinkler spacing. The sprinklers are 
6’ apart (unless you put in baffles). 6x3 = 18 gpm each. 

Travis Mack, SET
MFP Design, LLC
"Follow" us on Facebook: 
https://www.facebook.com/pages/MFP-Design-LLC/92218417692
Send large files to MFP Design via:
https://www.hightail.com/u/MFPDesign

Sent from my iPhone

> On Nov 3, 2017, at 5:31 AM, Trillium Fire Sprinkler Design Inc. 
> <[email protected]> wrote:
> 
> I have a question regarding the design.
>  
> They are asking for a deluge systm.
>  
> I have a total opening of 48'. I have spaced my sprinklers accordingly.
>  
> The code says minimum 3 gpm per lineal foot of water curtain. With no 
> sprinkler discharging less than 15 gpm.
>  
> 48 feet x3 gpm =144 gpm
>  
> 144 gpm /9 sprinklers= 16 gpm per sprinkler
>  
> Did I do this correctly?
>  
> Thanks for any input
>  
> Troy
>  
>  
> 
> 
> 
> 
>  
> 
>  
> 