Same section number.   Plus there's no storage below.  And common sense.

From: Sprinklerforum [mailto:[email protected]] On 
Behalf Of Mike Hairfield
Sent: Wednesday, January 24, 2018 12:56 PM
To: [email protected]
Subject: Re: Conveyors


I do not have the 2016 ed.



We use 2010 here in VA

can you copy it and send it to  me please?

________________________________
From: Sprinklerforum 
<[email protected]<mailto:[email protected]>>
 on behalf of Steve Leyton 
<[email protected]<mailto:[email protected]>>
Sent: Wednesday, January 24, 2018 3:54 PM
To: 
[email protected]<mailto:[email protected]>
Subject: RE: Conveyors


8.12.5.2 of the 2016 ed.



From: Sprinklerforum [mailto:[email protected]] On 
Behalf Of Mike Hairfield
Sent: Wednesday, January 24, 2018 12:53 PM
To: 
[email protected]<mailto:[email protected]>
Subject: Re: Conveyors



24" wide



AHJ is looking for something in NFPA or FM Global that states that

they do not require protection



________________________________

From: Sprinklerforum 
<[email protected]<mailto:[email protected]>>
 on behalf of Steve Leyton 
<[email protected]<mailto:[email protected]>>
Sent: Wednesday, January 24, 2018 3:50 PM
To: 
[email protected]<mailto:[email protected]>
Subject: RE: Conveyors



Oops - they're not 30" wide, they're 30" AFF.  So how wide are they?  I've 
worked on some giant FC projects but the conveyors weren't 48" in any case.



SL



From: Sprinklerforum [mailto:[email protected]] On 
Behalf Of Steve Leyton
Sent: Wednesday, January 24, 2018 12:49 PM
To: 
[email protected]<mailto:[email protected]>
Subject: RE: Conveyors



Considering that the fire load that we want to protect is being conveyed with 
full exposure to sprinklers above, and it's not practical in distribution and 
fulfillment center operations to store combustibles under such belt systems, I 
can't imagine why you'd need sprinklers below a 30" conveyor even if it wasn't 
open.



My 2ยข and nothing more,

Steve L.



From: Sprinklerforum [mailto:[email protected]] On 
Behalf Of Mike Hairfield
Sent: Wednesday, January 24, 2018 12:40 PM
To: Sprinkler Forum
Subject: Conveyors



Here is my question:



ESFR Systems that have some roller conveyors at 30" AFF that the the opening 
between rollers

is over 50% do they require sprinkler protection under them?



It use to be that they were not required to be protected!



Thanks,



Mike Hairfield