There is a landing at each of 11 levels, the stairs are in the center of the 
tower, with some additional floor space at each landing. The whole thing is of 
combustible construction so we have sprinklers at each level. It is more an 11 
storey tower than a continuous shaft.  Also, it is not heated, so we have a dry 
system to feed all the sprinklers.

 

David Bitton, ing./Eng.

Quest Loss Control Services Inc.

Les services de prévention des sinistres Quest

5100, rue de la Savane, bureau 200

Montréal, Québec 

H4P 1T8

(514) 341-4545

 <http://www.questlosscontrol.com/> www.questlosscontrol.com

 

From: Sprinklerforum [mailto:[email protected]] On 
Behalf Of Prahl, Craig/GVL
Sent: February 8, 2018 12:21 PM
To: [email protected]
Subject: RE: Church Steeple

 

When you say levels, we picture separated floor levels.  Is that what you have?

 

But then again it sounds more like a continuous shaft.

 

Are there landings at these levels?  How often do they occur?  How big are they?

 

Does the stair run up through the center? 

 


Craig L. Prahl 
Fire Protection Group Lead/SME
Direct - 864.920.7540

Fax - 864.920.7129
Direct Extension  77540
CH2M is now Jacobs.
200 Verdae Blvd.
Greenville, SC  29607
[email protected] <mailto:[email protected]> 
 <http://www.jacobs.com/> http://www.jacobs.com

 

From: Sprinklerforum [mailto:[email protected]] On 
Behalf Of David Bitton
Sent: Thursday, February 08, 2018 12:05 PM
To: [email protected] 
<mailto:[email protected]> 
Subject: RE: Church Steeple [EXTERNAL]

 

That’s not my situation, as the pitch is strictly at the top level.  Imagine an 
11 storey tower, roughly 25 x 25 ft, with an 80 ft high peaked roof above it.  
There is only one sprinkler at the top level, and about 4 sprinklers at each 
level beneath it. The tower has an open staircase within it so all of the 
levels are communicating.  My question is do I include sprinklers on multiple 
levels or just one level at a time?

 

David Bitton, ing./Eng.

Quest Loss Control Services Inc.

Les services de prévention des sinistres Quest

5100, rue de la Savane, bureau 200

Montréal, Québec 

H4P 1T8

(514) 341-4545

 <http://www.questlosscontrol.com/> www.questlosscontrol.com

 

From: Sprinklerforum [mailto:[email protected]] On 
Behalf Of Roland Huggins
Sent: February 8, 2018 10:17 AM
To: [email protected] 
<mailto:[email protected]> 
Subject: Re: Church Steeple

 

ALONG the pitch of the ceiling(s) that is inside the HORIZONTAL floor area IS 
one level. That’s why we have the section in 8.6.4.1.3 on steeply pitched 
ceiling

 

Roland

 

Roland Huggins, PE - Senior VP Engineering

American Fire Sprinkler Assn.    

Dallas, TX

http://www.firesprinkler.org <http://www.firesprinkler.org/> 

 

Fire Sprinklers Saves Lives

 

 

 

On Feb 7, 2018, at 3:58 PM, Fpdcdesign <[email protected] 
<mailto:[email protected]> > wrote:

 

It's a tough call without seeming the drawing and/or visiting the building. 
Without NFPA 13 (or other technical source) guidance, it comes down to 
engineering judgement. 


Todd G Williams, PE

Fire Protection Design/Consulting

Stonington, CT

 <tel:860-535-2080> 860-535-2080 (ofc)

 <tel:860-553-3553> 860-553-3553 (fax)

 <tel:860-608-4559> 860-608-4559 (cell)





On Feb 7, 2018 at 6:27 PM, < <mailto:[email protected]> David 
Bitton> wrote:

Hello,

 

I have a very tall but narrow church steeple to protect.  At the peak, there is 
a single sprinkler head, with the lower levels having between 2 and 4 
sprinklers at each level.  I am having a problem determining the heads to 
include in my design area.  The levels are not closed off from each other, so I 
think that restricting the calculations to one level would not be conservative 
enough.  I have not found any guidance in NFPA 13.

 

I would appreciate your thoughts about this issue.

 

David Bitton, ing./Eng.

Quest Loss Control Services Inc.

Les services de prévention des sinistres Quest

5100, rue de la Savane, bureau 200

Montréal, Québec 

H4P 1T8

(514) 341-4545

 <http://www.questlosscontrol.com/> www.questlosscontrol.com

 

_______________________________________________ Sprinklerforum mailing list  
<mailto:[email protected]> 
[email protected]  
<http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org> 
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org

_______________________________________________
Sprinklerforum mailing list
 <mailto:[email protected]> 
[email protected]
 <http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org> 
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org

 

_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org

Reply via email to