Also see Chapter 16 of 25.

-----Original Message-----
From: Sprinklerforum [mailto:sprinklerforum-boun...@lists.firesprinkler.org] On 
Behalf Of Ron Greenman
Sent: Monday, February 26, 2018 12:56 PM
To: sprinklerforum@lists.firesprinkler.org
Subject: Re: Residential sprinkler question

Below is the language in 13D/2016 regarding maintenance. It is substantially, 
if not exactly the same as 2013. I left out section 12.3.5 as that addresses 
anti-freeze only.  I suppose if you wanted to add the "test after twenty years" 
to the "what information SHOULD the contractor provide" part, you could.


12.1* General. The installer shall provide to the owner/occupant instructions 
on inspecting, testing, and maintaining the system.

12.2* Inspections and Tests.  The sprinkler system shall be inspected and 
tested periodically to make sure the system is in good working condition.

12.3 Maintenance.

12.3.1 The sprinkler system shall be properly maintained in accordance with 
this standard and the manufacturers’ instructions.

12.3.2 Any sprinkler that is operated, damaged, corroded, covered with foreign 
materials, or showing signs of leakage shall be replaced with a new listed 
sprinkler having the same performance characteristics as the original equipment.

12.3.2.1* Where replacing residential sprinklers manufactured prior to 2003 
that are no longer available from the manufacturer and are installed using a 
design density less than 0.05 gpm/ft2 (204 mm/min), a residential sprinkler 
with an equivalent K-factor (± 5 percent) shall be permitted to be used 
provided the currently listed coverage area for the replacement sprinkler is 
not exceeded.

12.3.3 Painting Sprinklers.

12.3.3.1 Sprinklers shall not be painted unless applied by the manufacturer.

12.3.3.2* Any sprinklers that have been painted outside of the factory shall be 
replaced with a new listed sprinkler.

12.3.4* Wet Pipe Systems.  A wet pipe system shall be maintained above 40°F 
(4°C), including areas properly insulated to maintain 40°F (4°C).

A.12.1 These instructions should include the following:

(1) Information regarding the necessary system inspection, testing, and 
maintenance as described in this standard

(2) The manufacturers’ installation, care, and maintenance instructions for the 
installed sprinkler system components

(3) Name, address, and phone number of the installing contractor of the fire 
sprinkler system

(4) Name, address, and phone number of a fire sprinkler system service company 
if different than the installing contractor


The occupants of a home with a sprinkler system should

understand that maintaining a sprinkler system is mostly about

common sense. Keeping the control valve open, not hanging

items from the sprinklers, and making sure that the sprinklers

do not get painted or obstructed are the most important items.

It is also important to know the function of the main control

valve and where the control valve is located.


A.12.2 The building owner or manager should understand the sprinkler system 
operation and conduct periodic inspections and tests to make sure that the 
system is in good working condition. A recommended inspection and testing 
program includes the following:

(1) Monthly inspection of all valves to ensure that they are open

(2) Monthly inspection of tanks, if present, to confirm they are full

(3) Monthly testing of pumps, if present, to make sure they operate properly 
and do not trip circuit breakers when starting

(4) Testing of all waterflow devices, when provided, every 6 months including 
monitoring service (note that notification of the monitoring service is 
essential to make sure that the fire department is not called due to testing)

(5) Ongoing visual inspection of all sprinklers to make sure they are not 
obstructed, damaged, corroded, covered with foreign materials, field painted, 
or showing signs of leakage, and that decorations are not attached to them

(6) Annually, fully open the test connection downstream of any 
pressure-reducing or pressure-regulating valve, and make sure that the pressure 
gauge reads a reasonable value

(7) Inspect systems by individuals knowledgeable and trained in such systems 
when there is a change in ownership


A.12.3.2.1 It is recognized that the flow and pressure available to the 
replacement sprinkler might be less than its current flow and pressure 
requirement.


A.12.3.3.2 Whenever painting or home improvements are made in the dwelling 
unit, special attention should be paid to ensure that sprinklers are not 
painted or obstructed either at the time of installation or during subsequent 
redecoration. This is as important for the cover plates of concealed sprinklers 
as it is to the sprinklers themselves. Special paint is used for cover plates 
and can only be applied by the manufacturer. Applying paint to cover plates 
outside of the factory can cause the sprinkler to malfunction and possibly not 
operate during a fire. When painting is occurring in the vicinity of 
sprinklers, the sprinklers should be protected by covering them with a bag, 
which should be removed immediately after painting is finished. For 
concealed-type sprinklers, the cover plates should be removed (most are 
designed to be unscrewed) and then the

sprinklers should be protected underneath from paint and overspray with a bag. 
After the painting is finished, the bags should be removed from the sprinklers 
and the cover plates should be replaced.


A.12.3.4 See Figure A.9.1.1(a) through Figure A.9.1.1(d) for possible methods 
used by the installer to insulate sprinkler piping in unheated areas. It is 
important that this insulation not be disturbed or removed.
Disturbing or removing this insulation could result in sprinkler pipes being 
frozen during winter months that would not only block water flow to the 
sprinklers but could cause broken pipes and fittings.






Ron Greenman

rongreen...@gmail.com

253.576.9700

The Universe is monstrously indifferent to the presence of man. -Werner Herzog, 
screenwriter, film director, author, actor and opera director (1942-)

On Sat, Feb 24, 2018 at 6:43 AM, Scott Futrell <sco...@ffcdi.com> wrote:

> I talked to the FD.  They will do a yearly inspection, test the 
> waterflow switch, no charge and look at sprinklers for corrosion and 
> obstruction.  No other testing recommendations to the owners. I 
> specifically ask about twenty year testing.
>
> So, if NFPA 25 isn't in play, how does a homeowner know they have a 
> twenty year sprinkler test required? Agree with Ron G.
>
> Scott
>
> Office: (763) 425-1001 x2
> Cell: (612) 759-5556
>
> -----Original Message-----
> From: Sprinklerforum [mailto:sprinklerforum-bounces@lists.firesprinkler.
> org] On Behalf Of Bruce Verhei
> Sent: Friday, February 23, 2018 10:34 PM
> To: sprinklerforum@lists.firesprinkler.org
> Subject: Re: Residential sprinkler question
>
> From Scottsdale FP’s website:
>
> http://www.scottsdaleaz.gov/fire/residential-sprinkler
>
> Sounds as if you may schedule a visit from the fire department.
>
> Best.
>
> Bruce Verhei
>
> > On Feb 23, 2018, at 17:51, John Irwin <john.ir...@dynafire.com> wrote:
> >> I understand the inspection is not required, but the sprinkler 
> >> doesn't
> know it's in a house and not a highrise. If asked I would reccomend 
> they get tested as they would in an NFPA 13 occupancy.
> >
> > ⁣John Irwin
> >
> > On Feb 23, 2018, 8:41 PM, at 8:41 PM, Ron Greenman <
> rongreen...@gmail.com> wrote:
> >> John. It’s different because the requirement is in 25 and 13d 
> >> systems are exempt from 25. It would need to be a jurisdiction 
> >> amendment to
> >> 25 or a stand alone requirement.
> >>
> >> On Fri, Feb 23, 2018 at 4:29 PM John Irwin 
> >> <john.ir...@dynafire.com>
> >> wrote:
> >>
> >>> Why would it be any different than a Residential sprinkler 
> >>> installed
> >> in a
> >>> dwelling unit in an NFPA 13 system?
> >>>
> >>> ⁣John Irwin
> _______________________________________________
> Sprinklerforum mailing list
> Sprinklerforum@lists.firesprinkler.org
> http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.
> org
>
-------------- next part --------------
An HTML attachment was scrubbed...
URL: 
<http://lists.firesprinkler.org/private.cgi/sprinklerforum-firesprinkler.org/attachments/20180226/56c3a85b/attachment.html>
_______________________________________________
Sprinklerforum mailing list
Sprinklerforum@lists.firesprinkler.org
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org

_______________________________________________
Sprinklerforum mailing list
Sprinklerforum@lists.firesprinkler.org
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org

Reply via email to