The section (16.2) in that chapter only applies to "Small Residential Board
& Care Facilities."



Ron Greenman

[email protected]

253.576.9700

The Universe is monstrously indifferent to the presence of man. -Werner
Herzog, screenwriter, film director, author, actor and opera
director (1942-)

On Mon, Feb 26, 2018 at 9:58 AM, Tom Duross <[email protected]> wrote:

> Also see Chapter 16 of 25.
>
> -----Original Message-----
> From: Sprinklerforum [mailto:[email protected].
> org] On Behalf Of Ron Greenman
> Sent: Monday, February 26, 2018 12:56 PM
> To: [email protected]
> Subject: Re: Residential sprinkler question
>
> Below is the language in 13D/2016 regarding maintenance. It is
> substantially, if not exactly the same as 2013. I left out section 12.3.5
> as that addresses anti-freeze only.  I suppose if you wanted to add the
> "test after twenty years" to the "what information SHOULD the contractor
> provide" part, you could.
>
>
> 12.1* General. The installer shall provide to the owner/occupant
> instructions on inspecting, testing, and maintaining the system.
>
> 12.2* Inspections and Tests.  The sprinkler system shall be inspected and
> tested periodically to make sure the system is in good working condition.
>
> 12.3 Maintenance.
>
> 12.3.1 The sprinkler system shall be properly maintained in accordance
> with this standard and the manufacturers’ instructions.
>
> 12.3.2 Any sprinkler that is operated, damaged, corroded, covered with
> foreign materials, or showing signs of leakage shall be replaced with a new
> listed sprinkler having the same performance characteristics as the
> original equipment.
>
> 12.3.2.1* Where replacing residential sprinklers manufactured prior to
> 2003 that are no longer available from the manufacturer and are installed
> using a design density less than 0.05 gpm/ft2 (204 mm/min), a residential
> sprinkler with an equivalent K-factor (± 5 percent) shall be permitted to
> be used provided the currently listed coverage area for the replacement
> sprinkler is not exceeded.
>
> 12.3.3 Painting Sprinklers.
>
> 12.3.3.1 Sprinklers shall not be painted unless applied by the
> manufacturer.
>
> 12.3.3.2* Any sprinklers that have been painted outside of the factory
> shall be replaced with a new listed sprinkler.
>
> 12.3.4* Wet Pipe Systems.  A wet pipe system shall be maintained above
> 40°F (4°C), including areas properly insulated to maintain 40°F (4°C).
>
> A.12.1 These instructions should include the following:
>
> (1) Information regarding the necessary system inspection, testing, and
> maintenance as described in this standard
>
> (2) The manufacturers’ installation, care, and maintenance instructions
> for the installed sprinkler system components
>
> (3) Name, address, and phone number of the installing contractor of the
> fire sprinkler system
>
> (4) Name, address, and phone number of a fire sprinkler system service
> company if different than the installing contractor
>
>
> The occupants of a home with a sprinkler system should
>
> understand that maintaining a sprinkler system is mostly about
>
> common sense. Keeping the control valve open, not hanging
>
> items from the sprinklers, and making sure that the sprinklers
>
> do not get painted or obstructed are the most important items.
>
> It is also important to know the function of the main control
>
> valve and where the control valve is located.
>
>
> A.12.2 The building owner or manager should understand the sprinkler
> system operation and conduct periodic inspections and tests to make sure
> that the system is in good working condition. A recommended inspection and
> testing program includes the following:
>
> (1) Monthly inspection of all valves to ensure that they are open
>
> (2) Monthly inspection of tanks, if present, to confirm they are full
>
> (3) Monthly testing of pumps, if present, to make sure they operate
> properly and do not trip circuit breakers when starting
>
> (4) Testing of all waterflow devices, when provided, every 6 months
> including monitoring service (note that notification of the monitoring
> service is essential to make sure that the fire department is not called
> due to testing)
>
> (5) Ongoing visual inspection of all sprinklers to make sure they are not
> obstructed, damaged, corroded, covered with foreign materials, field
> painted, or showing signs of leakage, and that decorations are not attached
> to them
>
> (6) Annually, fully open the test connection downstream of any
> pressure-reducing or pressure-regulating valve, and make sure that the
> pressure gauge reads a reasonable value
>
> (7) Inspect systems by individuals knowledgeable and trained in such
> systems when there is a change in ownership
>
>
> A.12.3.2.1 It is recognized that the flow and pressure available to the
> replacement sprinkler might be less than its current flow and pressure
> requirement.
>
>
> A.12.3.3.2 Whenever painting or home improvements are made in the dwelling
> unit, special attention should be paid to ensure that sprinklers are not
> painted or obstructed either at the time of installation or during
> subsequent redecoration. This is as important for the cover plates of
> concealed sprinklers as it is to the sprinklers themselves. Special paint
> is used for cover plates and can only be applied by the manufacturer.
> Applying paint to cover plates outside of the factory can cause the
> sprinkler to malfunction and possibly not operate during a fire. When
> painting is occurring in the vicinity of sprinklers, the sprinklers should
> be protected by covering them with a bag, which should be removed
> immediately after painting is finished. For concealed-type sprinklers, the
> cover plates should be removed (most are designed to be unscrewed) and then
> the
>
> sprinklers should be protected underneath from paint and overspray with a
> bag. After the painting is finished, the bags should be removed from the
> sprinklers and the cover plates should be replaced.
>
>
> A.12.3.4 See Figure A.9.1.1(a) through Figure A.9.1.1(d) for possible
> methods used by the installer to insulate sprinkler piping in unheated
> areas. It is important that this insulation not be disturbed or removed.
> Disturbing or removing this insulation could result in sprinkler pipes
> being frozen during winter months that would not only block water flow to
> the sprinklers but could cause broken pipes and fittings.
>
>
>
>
>
>
> Ron Greenman
>
> [email protected]
>
> 253.576.9700
>
> The Universe is monstrously indifferent to the presence of man. -Werner
> Herzog, screenwriter, film director, author, actor and opera director
> (1942-)
>
> On Sat, Feb 24, 2018 at 6:43 AM, Scott Futrell <[email protected]> wrote:
>
> > I talked to the FD.  They will do a yearly inspection, test the
> > waterflow switch, no charge and look at sprinklers for corrosion and
> > obstruction.  No other testing recommendations to the owners. I
> > specifically ask about twenty year testing.
> >
> > So, if NFPA 25 isn't in play, how does a homeowner know they have a
> > twenty year sprinkler test required? Agree with Ron G.
> >
> > Scott
> >
> > Office: (763) 425-1001 x2
> > Cell: (612) 759-5556
> >
> > -----Original Message-----
> > From: Sprinklerforum [mailto:[email protected].
> > org] On Behalf Of Bruce Verhei
> > Sent: Friday, February 23, 2018 10:34 PM
> > To: [email protected]
> > Subject: Re: Residential sprinkler question
> >
> > From Scottsdale FP’s website:
> >
> > http://www.scottsdaleaz.gov/fire/residential-sprinkler
> >
> > Sounds as if you may schedule a visit from the fire department.
> >
> > Best.
> >
> > Bruce Verhei
> >
> > > On Feb 23, 2018, at 17:51, John Irwin <[email protected]> wrote:
> > >> I understand the inspection is not required, but the sprinkler
> > >> doesn't
> > know it's in a house and not a highrise. If asked I would reccomend
> > they get tested as they would in an NFPA 13 occupancy.
> > >
> > > ⁣John Irwin
> > >
> > > On Feb 23, 2018, 8:41 PM, at 8:41 PM, Ron Greenman <
> > [email protected]> wrote:
> > >> John. It’s different because the requirement is in 25 and 13d
> > >> systems are exempt from 25. It would need to be a jurisdiction
> > >> amendment to
> > >> 25 or a stand alone requirement.
> > >>
> > >> On Fri, Feb 23, 2018 at 4:29 PM John Irwin
> > >> <[email protected]>
> > >> wrote:
> > >>
> > >>> Why would it be any different than a Residential sprinkler
> > >>> installed
> > >> in a
> > >>> dwelling unit in an NFPA 13 system?
> > >>>
> > >>> ⁣John Irwin
> > _______________________________________________
> > Sprinklerforum mailing list
> > [email protected]
> > http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler
> .
> > org
> >
> -------------- next part --------------
> An HTML attachment was scrubbed...
> URL: <http://lists.firesprinkler.org/private.cgi/
> sprinklerforum-firesprinkler.org/attachments/20180226/
> 56c3a85b/attachment.html>
> _______________________________________________
> Sprinklerforum mailing list
> [email protected]
> http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.
> org
>
> _______________________________________________
> Sprinklerforum mailing list
> [email protected]
> http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.
> org
>
-------------- next part --------------
An HTML attachment was scrubbed...
URL: 
<http://lists.firesprinkler.org/private.cgi/sprinklerforum-firesprinkler.org/attachments/20180226/4cb3c4a3/attachment.html>
_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org

Reply via email to