I think 8.15.1.2.5 is going to be your best bet.  The issue is that in many
other places of the standard, composite wood joist are specifically handled
differently than wood joist and are not considered "similar solid member
construction."

 

As far as the specially listed sprinklers, I think you would have to use
them with 8.15.1.6.  This says less than 36", which I take as from zero to
36" in depth.  The specially listed sprinklers have a requirement of 6"
minimum clear space.  This gets you back to there is no sprinkler that is
available to protect this space.  

 

I would lean back to 8.15.1.2.5 and keep sprinklers out of the space.  But,
you will need to increase the design area to 3000 sq ft for adjacent spaces.

 

 

 



Travis Mack, SET

MFP Design, LLC

3356 E Vallejo Ct

Gilbert, AZ 85298

480-505-9271

fax: 866-430-6107

 <mailto:email:tm...@mfpdesign.com> email:tm...@mfpdesign.com

 

 
<https://na01.safelinks.protection.outlook.com/?url=http%3A%2F%2Fwww.mfpdesi
gn.com%2F&data=02%7C01%7C%7C1121d49f9e6b4cf248f108d4df580e77%7C14e5497c16da4
2e69ffa77d19bafe511%7C0%7C0%7C636379016677342180&sdata=HJ8OA4xyeHAoxXNz5mu%2
FYfycgtd5nsFrrpvzulZiNkQ%3D&reserved=0> http://www.mfpdesign.com

 
<https://na01.safelinks.protection.outlook.com/?url=https%3A%2F%2Fwww.facebo
ok.com%2Fpages%2FMFP-Design-LLC%2F92218417692&data=02%7C01%7C%7C1121d49f9e6b
4cf248f108d4df580e77%7C14e5497c16da42e69ffa77d19bafe511%7C0%7C0%7C6363790166
77342180&sdata=H%2BwdcgK8DLGBcNoqJEvUrzsXngySwkX56Vgf9gM9EGk%3D&reserved=0>
https://www.facebook.com/pages/MFP-Design-LLC/92218417692

Send large files to us via:
<https://na01.safelinks.protection.outlook.com/?url=https%3A%2F%2Fwww.highta
il.com%2Fu%2FMFPDesign&data=02%7C01%7C%7C1121d49f9e6b4cf248f108d4df580e77%7C
14e5497c16da42e69ffa77d19bafe511%7C0%7C0%7C636379016677342180&sdata=eGdMZGu2
wXhUupGwgGTrqF3b54OP5%2BAZvlHhABSexWY%3D&reserved=0>
https://www.hightail.com/u/MFPDesign 

LinkedIn:
<https://na01.safelinks.protection.outlook.com/?url=https%3A%2F%2Fwww.linked
in.com%2Fin%2Ftravismack&data=02%7C01%7C%7C1121d49f9e6b4cf248f108d4df580e77%
7C14e5497c16da42e69ffa77d19bafe511%7C0%7C0%7C636379016677342180&sdata=tT5E7L
sZjSmyreKi4gDCa70EWN%2BZodi%2FhbeCbHNRijI%3D&reserved=0>
https://www.linkedin.com/in/travismack

 

"The bitterness of poor quality remains long after the sweetness of low
price is forgotten."

 

From: Sprinklerforum <sprinklerforum-boun...@lists.firesprinkler.org> On
Behalf Of Mike Hairfield
Sent: Wednesday, March 28, 2018 9:13 AM
To: sprinklerforum@lists.firesprinkler.org
Subject: Re: concealed space less than 6" deep

 

I was at a AFSA NFPA 13 2013 ed seminar that was given by the AFA Virginia
Chapter

that the Great Bob Caputo was the instructor and this came up.

 

If I remember correctly he stated that sprinklers are not required, but
maybe it was

during one of the times that doze off.

 

Mike

 

  _____  

From: Sprinklerforum <sprinklerforum-boun...@lists.firesprinkler.org
<mailto:sprinklerforum-boun...@lists.firesprinkler.org> > on behalf of Ben
Young <derblitzkrie...@gmail.com <mailto:derblitzkrie...@gmail.com> >
Sent: Wednesday, March 28, 2018 12:06 PM
To: sprinklerforum@lists.firesprinkler.org
<mailto:sprinklerforum@lists.firesprinkler.org> 
Subject: concealed space less than 6" deep 

 

I feel like this has come up here before, but nothing came back when I did
searches through the archives.

I've got a concealed space that needs sprinklers, but I don't know how I'm
going to put them in.

(Light hazard office space under 2013 ED of 13)

 

Wood TJI construction with an ACT suspended ceiling below it.

>From top of joist to face of ceiling is only 16.5" deep

TJIs are 12" deep

How the heck do I protect this space with only a 4.5" gap that will be even
smaller with the grid?

Owner refuses to fill space with insulation inside trusses (for the time
being)

CC spec app heads not required since the space is so small anyway, but I
think that also means I can't use CPVC, which would make hanging the pipe
parallel to the trusses a lot easier.

Its obstructed construction, so I should be able to put pendent heads below
the bottom edge of the TJIs, but it will be no more than 2-3 inches above
the ceiling.

I don't even know if that will work so worst case is I need heads inside
every truss space, right?

The salesperson is telling me to use some weird combination of 8.15.1.2.3
(which I believe only applied to double trusses ) and 8.15.1.2.5 (which only
applies to solid member construction and then you have 8.15.1.2.6 directly
below it calling out TJIs)



This definitely feels like a catch-22.

Thanks,


Benjamin Young