I have to agree with Ben here. If 8.15.1.2.5 was intended to include composite 
wood joists, then there is no reason to have the more restrictive 8.15.1.2.6, 
which applies specifically to composite wood joists.

-Kyle M

From: Sprinklerforum [mailto:[email protected]] On 
Behalf Of Ben Young
Sent: Wednesday, March 28, 2018 9:35 AM
To: [email protected]
Subject: [EXTERNAL] Re: concealed space less than 6" deep

Travis, you're right on the CC spec app heads, for some crazy reason I was 
thinking 36" was the min not the max!
8.15.1.2.5 makes sense, but I look at 8.15.1.2.6 and it makes me think there's 
a reason they didn't include 'composite wood joist' in 1.2.5.
Look at 1.2.8 and 1.2.13 where they use both terms.
Basically I don't feel like 'wood joist' is a catchall term for section 8.15.1
But yeah, I would love to be proven wrong on this!


Benjamin Young

On Wed, Mar 28, 2018 at 12:19 PM, MFP Design, LLC 
<[email protected]<mailto:[email protected]>> wrote:
I think 8.15.1.2.5 is going to be your best bet.  The issue is that in many 
other places of the standard, composite wood joist are specifically handled 
differently than wood joist and are not considered “similar solid member 
construction.”

As far as the specially listed sprinklers, I think you would have to use them 
with 8.15.1.6.  This says less than 36”, which I take as from zero to 36” in 
depth.  The specially listed sprinklers have a requirement of 6” minimum clear 
space.  This gets you back to there is no sprinkler that is available to 
protect this space.

I would lean back to 8.15.1.2.5 and keep sprinklers out of the space.  But, you 
will need to increase the design area to 3000 sq ft for adjacent spaces.



[MFP_logo_F]
Travis Mack, SET
MFP Design, LLC
3356 E Vallejo Ct
Gilbert, AZ 85298
480-505-9271<tel:(480)%20505-9271>
fax: 866-430-6107<tel:(866)%20430-6107>
email:[email protected]<mailto:email:[email protected]>

http://www.mfpdesign.com<https://urldefense.proofpoint.com/v2/url?u=https-3A__na01.safelinks.protection.outlook.com_-3Furl-3Dhttp-253A-252F-252Fwww.mfpdesign.com-252F-26data-3D02-257C01-257C-257C1121d49f9e6b4cf248f108d4df580e77-257C14e5497c16da42e69ffa77d19bafe511-257C0-257C0-257C636379016677342180-26sdata-3DHJ8OA4xyeHAoxXNz5mu-252FYfycgtd5nsFrrpvzulZiNkQ-253D-26reserved-3D0&d=DwMFaQ&c=wn3mZQLIuInh2ClcJ0_DIA&r=Z_2A85VL7AQzoqudh6uOyS3bn8etxB7nLN8OBJwQd9A&m=GrULeWpdM7cpEkXHtsdVqtVtmQdWfkM3zplzAhtyLwY&s=I58ROUQUvra_J2RL_MK4g8SJGz2cGCUV68H4nrePJkY&e=>
https://www.facebook.com/pages/MFP-Design-LLC/92218417692<https://urldefense.proofpoint.com/v2/url?u=https-3A__na01.safelinks.protection.outlook.com_-3Furl-3Dhttps-253A-252F-252Fwww.facebook.com-252Fpages-252FMFP-2DDesign-2DLLC-252F92218417692-26data-3D02-257C01-257C-257C1121d49f9e6b4cf248f108d4df580e77-257C14e5497c16da42e69ffa77d19bafe511-257C0-257C0-257C636379016677342180-26sdata-3DH-252BwdcgK8DLGBcNoqJEvUrzsXngySwkX56Vgf9gM9EGk-253D-26reserved-3D0&d=DwMFaQ&c=wn3mZQLIuInh2ClcJ0_DIA&r=Z_2A85VL7AQzoqudh6uOyS3bn8etxB7nLN8OBJwQd9A&m=GrULeWpdM7cpEkXHtsdVqtVtmQdWfkM3zplzAhtyLwY&s=hHv2c-a1y5MMMat0i_bJdSt8oHEVMX_tSF1WEoSG76I&e=>
Send large files to us via: 
https://www.hightail.com/u/MFPDesign<https://urldefense.proofpoint.com/v2/url?u=https-3A__na01.safelinks.protection.outlook.com_-3Furl-3Dhttps-253A-252F-252Fwww.hightail.com-252Fu-252FMFPDesign-26data-3D02-257C01-257C-257C1121d49f9e6b4cf248f108d4df580e77-257C14e5497c16da42e69ffa77d19bafe511-257C0-257C0-257C636379016677342180-26sdata-3DeGdMZGu2wXhUupGwgGTrqF3b54OP5-252BAZvlHhABSexWY-253D-26reserved-3D0&d=DwMFaQ&c=wn3mZQLIuInh2ClcJ0_DIA&r=Z_2A85VL7AQzoqudh6uOyS3bn8etxB7nLN8OBJwQd9A&m=GrULeWpdM7cpEkXHtsdVqtVtmQdWfkM3zplzAhtyLwY&s=VygTWx3S0fPn-zz_C3Uo97WysEuiUS1aWCevUR4p5gg&e=>
LinkedIn: 
https://www.linkedin.com/in/travismack<https://urldefense.proofpoint.com/v2/url?u=https-3A__na01.safelinks.protection.outlook.com_-3Furl-3Dhttps-253A-252F-252Fwww.linkedin.com-252Fin-252Ftravismack-26data-3D02-257C01-257C-257C1121d49f9e6b4cf248f108d4df580e77-257C14e5497c16da42e69ffa77d19bafe511-257C0-257C0-257C636379016677342180-26sdata-3DtT5E7LsZjSmyreKi4gDCa70EWN-252BZodi-252FhbeCbHNRijI-253D-26reserved-3D0&d=DwMFaQ&c=wn3mZQLIuInh2ClcJ0_DIA&r=Z_2A85VL7AQzoqudh6uOyS3bn8etxB7nLN8OBJwQd9A&m=GrULeWpdM7cpEkXHtsdVqtVtmQdWfkM3zplzAhtyLwY&s=OtLk7cYJ5T8MNPZqV6QHKJRiSLYyLs5vweuzg__1_CE&e=>

“The bitterness of poor quality remains long after the sweetness of low price 
is forgotten.”

From: Sprinklerforum 
<[email protected]<mailto:[email protected]>>
 On Behalf Of Mike Hairfield
Sent: Wednesday, March 28, 2018 9:13 AM
To: 
[email protected]<mailto:[email protected]>
Subject: Re: concealed space less than 6" deep


I was at a AFSA NFPA 13 2013 ed seminar that was given by the AFA Virginia 
Chapter

that the Great Bob Caputo was the instructor and this came up.



If I remember correctly he stated that sprinklers are not required, but maybe 
it was

during one of the times that doze off.



Mike

________________________________
From: Sprinklerforum 
<[email protected]<mailto:[email protected]>>
 on behalf of Ben Young 
<[email protected]<mailto:[email protected]>>
Sent: Wednesday, March 28, 2018 12:06 PM
To: 
[email protected]<mailto:[email protected]>
Subject: concealed space less than 6" deep

I feel like this has come up here before, but nothing came back when I did 
searches through the archives.
I've got a concealed space that needs sprinklers, but I don't know how I'm 
going to put them in.
(Light hazard office space under 2013 ED of 13)

Wood TJI construction with an ACT suspended ceiling below it.
From top of joist to face of ceiling is only 16.5" deep
TJIs are 12" deep
How the heck do I protect this space with only a 4.5" gap that will be even 
smaller with the grid?
Owner refuses to fill space with insulation inside trusses (for the time being)
CC spec app heads not required since the space is so small anyway, but I think 
that also means I can't use CPVC, which would make hanging the pipe parallel to 
the trusses a lot easier.
Its obstructed construction, so I should be able to put pendent heads below the 
bottom edge of the TJIs, but it will be no more than 2-3 inches above the 
ceiling.
I don't even know if that will work so worst case is I need heads inside every 
truss space, right?
The salesperson is telling me to use some weird combination of 8.15.1.2.3 
(which I believe only applied to double trusses ) and 8.15.1.2.5 (which only 
applies to solid member construction and then you have 8.15.1.2.6 directly 
below it calling out TJIs)
This definitely feels like a catch-22.
Thanks,

Benjamin Young

_______________________________________________
Sprinklerforum mailing list
[email protected]<mailto:[email protected]>
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org<https://urldefense.proofpoint.com/v2/url?u=http-3A__lists.firesprinkler.org_listinfo.cgi_sprinklerforum-2Dfiresprinkler.org&d=DwMFaQ&c=wn3mZQLIuInh2ClcJ0_DIA&r=Z_2A85VL7AQzoqudh6uOyS3bn8etxB7nLN8OBJwQd9A&m=GrULeWpdM7cpEkXHtsdVqtVtmQdWfkM3zplzAhtyLwY&s=GhQO8jVHeo5qxQVa4DEy7SVYxXvUsk1Ie9TywiYiUBI&e=>

_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org

Reply via email to