Travis, you're right on the CC spec app heads, for some crazy reason I was
thinking 36" was the min not the max!

8.15.1.2.5 makes sense, but I look at 8.15.1.2.6 and it makes me think
there's a reason they didn't include 'composite wood joist' in 1.2.5.
Look at 1.2.8 and 1.2.13 where they use both terms.

Basically I don't feel like 'wood joist' is a catchall term for section
8.15.1

But yeah, I would love to be proven wrong on this!


Benjamin Young

On Wed, Mar 28, 2018 at 12:19 PM, MFP Design, LLC <[email protected]>
wrote:

> *I think 8.15.1.2.5 is going to be your best bet.  The issue is that in
> many other places of the standard, composite wood joist are specifically
> handled differently than wood joist and are not considered “similar solid
> member construction.”*
>
>
>
> *As far as the specially listed sprinklers, I think you would have to use
> them with 8.15.1.6.  This says less than 36”, which I take as from zero to
> 36” in depth.  The specially listed sprinklers have a requirement of 6”
> minimum clear space.  This gets you back to there is no sprinkler that is
> available to protect this space.  *
>
>
>
> *I would lean back to 8.15.1.2.5 and keep sprinklers out of the space.
> But, you will need to increase the design area to 3000 sq ft for adjacent
> spaces.*
>
>
>
>
>
>
>
> [image: MFP_logo_F]
>
> Travis Mack, SET
>
> MFP Design, LLC
>
> 3356 E Vallejo Ct
>
> Gilbert, AZ 85298
>
> 480-505-9271 <(480)%20505-9271>
>
> fax: 866-430-6107 <(866)%20430-6107>
>
> email:[email protected]
>
>
>
> http://www.mfpdesign.com
> <https://na01.safelinks.protection.outlook.com/?url=http%3A%2F%2Fwww.mfpdesign.com%2F&data=02%7C01%7C%7C1121d49f9e6b4cf248f108d4df580e77%7C14e5497c16da42e69ffa77d19bafe511%7C0%7C0%7C636379016677342180&sdata=HJ8OA4xyeHAoxXNz5mu%2FYfycgtd5nsFrrpvzulZiNkQ%3D&reserved=0>
>
> https://www.facebook.com/pages/MFP-Design-LLC/92218417692
> <https://na01.safelinks.protection.outlook.com/?url=https%3A%2F%2Fwww.facebook.com%2Fpages%2FMFP-Design-LLC%2F92218417692&data=02%7C01%7C%7C1121d49f9e6b4cf248f108d4df580e77%7C14e5497c16da42e69ffa77d19bafe511%7C0%7C0%7C636379016677342180&sdata=H%2BwdcgK8DLGBcNoqJEvUrzsXngySwkX56Vgf9gM9EGk%3D&reserved=0>
>
> Send large files to us via: https://www.hightail.com/u/MFPDesign
> <https://na01.safelinks.protection.outlook.com/?url=https%3A%2F%2Fwww.hightail.com%2Fu%2FMFPDesign&data=02%7C01%7C%7C1121d49f9e6b4cf248f108d4df580e77%7C14e5497c16da42e69ffa77d19bafe511%7C0%7C0%7C636379016677342180&sdata=eGdMZGu2wXhUupGwgGTrqF3b54OP5%2BAZvlHhABSexWY%3D&reserved=0>
>
> LinkedIn: https://www.linkedin.com/in/travismack
> <https://na01.safelinks.protection.outlook.com/?url=https%3A%2F%2Fwww.linkedin.com%2Fin%2Ftravismack&data=02%7C01%7C%7C1121d49f9e6b4cf248f108d4df580e77%7C14e5497c16da42e69ffa77d19bafe511%7C0%7C0%7C636379016677342180&sdata=tT5E7LsZjSmyreKi4gDCa70EWN%2BZodi%2FhbeCbHNRijI%3D&reserved=0>
>
>
>
> *“**The bitterness of poor quality remains long after the sweetness of
> low price is forgotten.**”*
>
>
>
> *From:* Sprinklerforum <[email protected]> *On
> Behalf Of *Mike Hairfield
> *Sent:* Wednesday, March 28, 2018 9:13 AM
> *To:* [email protected]
> *Subject:* Re: concealed space less than 6" deep
>
>
>
> I was at a AFSA NFPA 13 2013 ed seminar that was given by the AFA Virginia
> Chapter
>
> that the Great Bob Caputo was the instructor and this came up.
>
>
>
> If I remember correctly he stated that sprinklers are not required, but
> maybe it was
>
> during one of the times that doze off.
>
>
>
> Mike
>
>
> ------------------------------
>
> *From:* Sprinklerforum <[email protected]>
> on behalf of Ben Young <[email protected]>
> *Sent:* Wednesday, March 28, 2018 12:06 PM
> *To:* [email protected]
> *Subject:* concealed space less than 6" deep
>
>
>
> I feel like this has come up here before, but nothing came back when I did
> searches through the archives.
>
> I've got a concealed space that needs sprinklers, but I don't know how I'm
> going to put them in.
>
> (Light hazard office space under 2013 ED of 13)
>
>
>
> Wood TJI construction with an ACT suspended ceiling below it.
>
> From top of joist to face of ceiling is only 16.5" deep
>
> TJIs are 12" deep
>
> How the heck do I protect this space with only a 4.5" gap that will be
> even smaller with the grid?
>
> Owner refuses to fill space with insulation inside trusses (for the time
> being)
>
> CC spec app heads not required since the space is so small anyway, but I
> think that also means I can't use CPVC, which would make hanging the pipe
> parallel to the trusses a lot easier.
>
> Its obstructed construction, so I should be able to put pendent heads
> below the bottom edge of the TJIs, but it will be no more than 2-3 inches
> above the ceiling.
>
> I don't even know if that will work so worst case is I need heads inside
> every truss space, right?
>
> The salesperson is telling me to use some weird combination of 8.15.1.2.3
> (which I believe only applied to double trusses ) and 8.15.1.2.5 (which
> only applies to solid member construction and then you have 8.15.1.2.6
> directly below it calling out TJIs)
>
> This definitely feels like a catch-22.
>
> Thanks,
>
>
> Benjamin Young
>
> _______________________________________________
> Sprinklerforum mailing list
> [email protected]
> http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.
> org
>
>