Once downstream of a labeled valve, fine. Upstream, and including valve, no. A 
gang drain, for example uses materials complying with normal NFPA 13 materials. 
I’m assuming valve at each branch line in order to get adequate flow.


Best.

Bruce Verhei 



> On Mar 30, 2018, at 14:59, Scott Futrell <sco...@ffcdi.com> wrote:
> 
> A Friday afternoon conundrum for the group.
>  
> I have a client with corrosion issues in several wet, twenty year old, ESFR, 
> warehouse systems.  These are center-fed systems.  Yes, center-fed. So all of 
> the branchlines are dead ends.  Corrosion scale and sludge is pushed into the 
> ends of the lines.  Flushing will be done.  End of the day though the client 
> wants to add a tie-in drain line connecting all the ends of all the lines to 
> drain/flush in the future.  It has been suggested that schedule 40 PVC might 
> be used for these tie-in drains.
>  
> My response so far:
>  
> Practically, plastic should be okay.
>  
> But, it would not be recognized in NFPA 13.  Also, because it could fail in a 
> fire, and we would expect high challenge fires in warehouses filled with 
> combustibles like pallets and plastics, if it failed before the sprinklers 
> operated, or before they were winning the battle you would have a potential 
> system failure.  Chances are probably remote, but they would exist with the 
> right (wrong) conditions.
>  
> I would expect that a knowledgeable inspector would question the installation 
> at least.
>  
> I wouldn’t specify it, but schedule 40 PVC might be an option for what you 
> are trying to accomplish cost-effectively.
>  
> What say ye all?
>  
> Scott Futrell
> Office: (763) 425-1001 x 2
> Cell: (612) 759-5556
> _______________________________________________
> Sprinklerforum mailing list
> Sprinklerforum@lists.firesprinkler.org
> http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org
_______________________________________________
Sprinklerforum mailing list
Sprinklerforum@lists.firesprinkler.org
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org

Reply via email to