I say it's fine if you have drain valves at the end of each line and
transition to pvc after the valve. But that may be expensive.

So I say pvc is ok after the drain valve.

But is that practical?

On Fri, Mar 30, 2018 at 4:59 PM, Scott Futrell <[email protected]> wrote:

> A Friday afternoon conundrum for the group.
>
>
>
> I have a client with corrosion issues in several wet, twenty year old,
> ESFR, warehouse systems.  These are center-fed systems.  Yes, center-fed.
> So all of the branchlines are dead ends.  Corrosion scale and sludge is
> pushed into the ends of the lines.  Flushing will be done.  End of the day
> though the client wants to add a tie-in drain line connecting all the ends
> of all the lines to drain/flush in the future.  It has been suggested that
> schedule 40 PVC might be used for these tie-in drains.
>
>
>
> My response so far:
>
>
>
> *Practically, plastic should be okay.*
>
>
>
> *But, it would not be recognized in NFPA 13.  Also, because it could fail
> in a fire, and we would expect high challenge fires in warehouses filled
> with combustibles like pallets and plastics, if it failed before the
> sprinklers operated, or before they were winning the battle you would have
> a potential system failure.  Chances are probably remote, but they would
> exist with the right (wrong) conditions.*
>
>
>
> *I would expect that a knowledgeable inspector would question the
> installation at least.*
>
>
>
> *I wouldn’t specify it, but schedule 40 PVC might be an option for what
> you are trying to accomplish cost-effectively.*
>
>
>
> What say ye all?
>
>
>
> Scott Futrell
>
> Office: (763) 425-1001 x 2
>
> Cell: (612) 759-5556
>
> _______________________________________________
> Sprinklerforum mailing list
> [email protected]
> http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.
> org
>
>
_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org

Reply via email to