Tie in drains don't need it at every line.  But, it is my understanding, as
others have said on here - up to the drain valve must be listed.  After the
valve can be just about anything within reason.  We were suggesting a valve
at the end of every line as the ONLY way you could run PVC for the drain
lines.  It is highly impractical from a cost perspective.

 

Check in A3.2.1 in the 2016 NFPA 13 handbook if you have it.

 



Travis Mack, SET

MFP Design, LLC

3356 E Vallejo Ct

Gilbert, AZ 85298

480-505-9271

fax: 866-430-6107

 <mailto:email:tm...@mfpdesign.com> email:tm...@mfpdesign.com

 

 
<https://na01.safelinks.protection.outlook.com/?url=http%3A%2F%2Fwww.mfpdesi
gn.com%2F&data=02%7C01%7C%7C1121d49f9e6b4cf248f108d4df580e77%7C14e5497c16da4
2e69ffa77d19bafe511%7C0%7C0%7C636379016677342180&sdata=HJ8OA4xyeHAoxXNz5mu%2
FYfycgtd5nsFrrpvzulZiNkQ%3D&reserved=0> http://www.mfpdesign.com

 
<https://na01.safelinks.protection.outlook.com/?url=https%3A%2F%2Fwww.facebo
ok.com%2Fpages%2FMFP-Design-LLC%2F92218417692&data=02%7C01%7C%7C1121d49f9e6b
4cf248f108d4df580e77%7C14e5497c16da42e69ffa77d19bafe511%7C0%7C0%7C6363790166
77342180&sdata=H%2BwdcgK8DLGBcNoqJEvUrzsXngySwkX56Vgf9gM9EGk%3D&reserved=0>
https://www.facebook.com/pages/MFP-Design-LLC/92218417692

Send large files to us via:
<https://na01.safelinks.protection.outlook.com/?url=https%3A%2F%2Fwww.highta
il.com%2Fu%2FMFPDesign&data=02%7C01%7C%7C1121d49f9e6b4cf248f108d4df580e77%7C
14e5497c16da42e69ffa77d19bafe511%7C0%7C0%7C636379016677342180&sdata=eGdMZGu2
wXhUupGwgGTrqF3b54OP5%2BAZvlHhABSexWY%3D&reserved=0>
https://www.hightail.com/u/MFPDesign 

LinkedIn:
<https://na01.safelinks.protection.outlook.com/?url=https%3A%2F%2Fwww.linked
in.com%2Fin%2Ftravismack&data=02%7C01%7C%7C1121d49f9e6b4cf248f108d4df580e77%
7C14e5497c16da42e69ffa77d19bafe511%7C0%7C0%7C636379016677342180&sdata=tT5E7L
sZjSmyreKi4gDCa70EWN%2BZodi%2FhbeCbHNRijI%3D&reserved=0>
https://www.linkedin.com/in/travismack

 

"The bitterness of poor quality remains long after the sweetness of low
price is forgotten."

 

From: Sprinklerforum <sprinklerforum-boun...@lists.firesprinkler.org> On
Behalf Of Scott Futrell
Sent: Friday, March 30, 2018 3:22 PM
To: sprinklerforum@lists.firesprinkler.org
Subject: RE: PVC drain line

 

Well.

 

Am I having a Friday afternoon brain fart?

 

Where does 13 say I can't have a drain line out of other materials, and
tie-in drains don't need valves at the end of every line, right?

 

Scott

 

Office: (763) 425-1001 x 2

Cell: (612) 759-5556

 

From: Sprinklerforum [
<mailto:sprinklerforum-boun...@lists.firesprinkler.org>
mailto:sprinklerforum-boun...@lists.firesprinkler.org] On Behalf Of Matthew
J Willis
Sent: Friday, March 30, 2018 5:13 PM
To: Forum < <mailto:sprinklerforum@lists.firesprinkler.org>
sprinklerforum@lists.firesprinkler.org>
Subject: RE: PVC drain line

 

So,

The answer would be no. Right?

Plastic is fine for drain, not listed. But all piping before the valve is.

 

R/

Matt

 