I can’t see a valve at the end of each line being practical.  Then you’d need a 
lift to drain them when you wanted to use it and these are >25K square foot 
systems, so many valves.

Scott

Office: (763) 425-1001 x 2
Cell: (612) 759-5556

From: Sprinklerforum [mailto:sprinklerforum-boun...@lists.firesprinkler.org] On 
Behalf Of Jeff Normand
Sent: Friday, March 30, 2018 5:07 PM
To: sprinklerforum@lists.firesprinkler.org
Subject: Re: PVC drain line

I say it's fine if you have drain valves at the end of each line and transition 
to pvc after the valve. But that may be expensive.

So I say pvc is ok after the drain valve.

But is that practical?

On Fri, Mar 30, 2018 at 4:59 PM, Scott Futrell 
<sco...@ffcdi.com<mailto:sco...@ffcdi.com>> wrote:

A Friday afternoon conundrum for the group.



I have a client with corrosion issues in several wet, twenty year old, ESFR, 
warehouse systems.  These are center-fed systems.  Yes, center-fed. So all of 
the branchlines are dead ends.  Corrosion scale and sludge is pushed into the 
ends of the lines.  Flushing will be done.  End of the day though the client 
wants to add a tie-in drain line connecting all the ends of all the lines to 
drain/flush in the future.  It has been suggested that schedule 40 PVC might be 
used for these tie-in drains.



My response so far:



Practically, plastic should be okay.



But, it would not be recognized in NFPA 13.  Also, because it could fail in a 
fire, and we would expect high challenge fires in warehouses filled with 
combustibles like pallets and plastics, if it failed before the sprinklers 
operated, or before they were winning the battle you would have a potential 
system failure.  Chances are probably remote, but they would exist with the 
right (wrong) conditions.



I would expect that a knowledgeable inspector would question the installation 
at least.



I wouldn’t specify it, but schedule 40 PVC might be an option for what you are 
trying to accomplish cost-effectively.



What say ye all?



Scott Futrell

Office: (763) 425-1001 x 2

Cell: (612) 759-5556

_______________________________________________
Sprinklerforum mailing list
Sprinklerforum@lists.firesprinkler.org<mailto:Sprinklerforum@lists.firesprinkler.org>
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org

_______________________________________________
Sprinklerforum mailing list
Sprinklerforum@lists.firesprinkler.org
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org

Reply via email to