I've seen this. Never had too much trouble getting a ceiling added when I give 
them the add alternate for installing sprinklers at the roof.

Checking wall heights is usually one of the first things I do when opening a 
fresh set of plans. Half a dozen different color highlighters and a cup of 
coffee...

⁣John Irwin 
DynaFire Inc. 
Tampa Fire Sprinkler Division 
727-282-9243 

This email was sent from a mobile device. Please forgive brevity, typographical 
errors, and grammatical gaffes.​

On Apr 13, 2018, 6:42 PM, at 6:42 PM, Ed Kramer <e...@bamfordfire.com> wrote:
>This is something we're seeing occasionally and I'm wondering if others
>are
>seeing it also.
>
>
>
>A typical office area within a noncombustible building.  All rooms
>within
>the greater area have lowered finished ceilings, are mostly light
>hazard,
>and the space above is noncombustible and (almost) concealed.  A small
>mechanical room (or 2 or 3) is located among the various offices.  This
>mech
>room is less than 130 sf, so the floor area can be protected with 1
>sprinkler.  However, the A/E has decided this room doesn't need a
>ceiling
>and the perimeter walls can stop 6" above the ceiling height of the
>adjacent
>rooms.  This makes the space above the surrounding offices
>noncombustible
>but not truly concealed.  See below.
>
>
>
>
>
>
>
>NFPA 13 (2013) tells me I have to sprinkler the entire noncombustible
>space
>above the offices.  8.15.23.3 doesn't apply since it's open on all 4
>sides.
>We're working with GC to convince them to add a ceiling or to extend
>the
>walls up to the roof deck.  It's just way too easy to overlook this
>kind of
>seemingly minor detail when bidding, and difficult to get a change
>order (or
>walls/ceilings added) after the contract's signed.
>
>
>
>So, just wondering if anybody else is seeing this issue.
>
>
>
>Ed Kramer
>
>Bamford Fire
>
>
>
>
>
>------------------------------------------------------------------------
>
>_______________________________________________
>Sprinklerforum mailing list
>Sprinklerforum@lists.firesprinkler.org
>http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org
_______________________________________________
Sprinklerforum mailing list
Sprinklerforum@lists.firesprinkler.org
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org

Reply via email to