Yes sir you’re reading correctly, 2002 it was introduced. In my field 
experience though, a whole lot of places it’s not getting done.

Regards,
Jason



> On May 10, 2018, at 8:16 AM, Brad Casterline <[email protected]> wrote:
> 
> From NFPA 25-2014:
> 
> "13.2.5.2 In systems where the sole water supply is through a
> backflow preventer and/or pressure-reducing valves, the main
> drain test of at least one system downstream of the device shall
> be conducted on a quarterly basis."
> 
> I've tried to make sure I am not taking this out of context or missing
> something.
> If this is being done there must be a WHOLE LOT of main drain testing going
> on!!!
> 
> Any ITM Gurus got their ears on??
> 
> Thanks,
> 
> Brad
> 
> 
> 
> 
> 
> 