Yes sir you’re reading correctly, 2002 it was introduced. In my field 
experience though, a whole lot of places it’s not getting done.

 

Regards,

Jason

 





On May 10, 2018, at 8:16 AM, Brad Casterline <[email protected] 
<mailto:[email protected]> > wrote:

 

>From NFPA 25-2014:

"13.2.5.2 In systems where the sole water supply is through a
backflow preventer and/or pressure-reducing valves, the main
drain test of at least one system downstream of the device shall
be conducted on a quarterly basis."

I've tried to make sure I am not taking this out of context or missing
something.
If this is being done there must be a WHOLE LOT of main drain testing going
on!!!

Any ITM Gurus got their ears on??