Thank you very much Anthony.

 

Brad

 

From: Sprinklerforum [mailto:[email protected]]
On Behalf Of [email protected]
Sent: Thursday, May 10, 2018 9:57 AM
To: 'Brad Casterline' <[email protected]>;
[email protected]
Subject: RE: Main Drain Test Question NFPA 25

 

Brad, you just hit the tip of the iceberg.. you are correct about the need
to do Quarterly main drain testing, this is about 99.9 percent of the
systems we install.

>From NFPA 25-2014: 

Also see 13.3.3.1 Each control valve shall be operated annually through its
full range and returned to its normal position.

Then 13.3.3.4 A main drain test shall be conducted any time the control
valve is closed and reopened at system riser.

I understand that the alarms must be tested every six months per NFPA 72
with the valves being tested for tamper, if this is not coordinated with the
owner then that's a lot of main drain testing.

 

How often do you really think this is being done? Compliance with testing
and maintenance requirements just for the annual inspections is a head ache
for most jurisdictions.

 

Anthony

 

-----Original Message-----
From: Brad Casterline <[email protected]
<mailto:[email protected]> > 
Sent: Thursday, May 10, 2018 6:17 AM
To: [email protected]
<mailto:[email protected]> 
Subject: Main Drain Test Question NFPA 25

 

>From NFPA 25-2014:

 

"13.2.5.2 In systems where the sole water supply is through a backflow
preventer and/or pressure-reducing valves, the main drain test of at least
one system downstream of the device shall be conducted on a quarterly
basis."

 

I've tried to make sure I am not taking this out of context or missing
something.

If this is being done there must be a WHOLE LOT of main drain testing going
on!!!

 

Any ITM Gurus got their ears on??

 

Thanks,

 

Brad

 

 

 

 

 

 

 