Brad, you just hit the tip of the iceberg.. you are correct about the need to do Quarterly main drain testing, this is about 99.9 percent of the systems we install.
>From NFPA 25-2014: Also see 13.3.3.1 Each control valve shall be operated annually through its full range and returned to its normal position. Then 13.3.3.4 A main drain test shall be conducted any time the control valve is closed and reopened at system riser. I understand that the alarms must be tested every six months per NFPA 72 with the valves being tested for tamper, if this is not coordinated with the owner then that's a lot of main drain testing. How often do you really think this is being done? Compliance with testing and maintenance requirements just for the annual inspections is a head ache for most jurisdictions. Anthony -----Original Message----- From: Brad Casterline <[email protected]> Sent: Thursday, May 10, 2018 6:17 AM To: [email protected] Subject: Main Drain Test Question NFPA 25 >From NFPA 25-2014: "13.2.5.2 In systems where the sole water supply is through a backflow preventer and/or pressure-reducing valves, the main drain test of at least one system downstream of the device shall be conducted on a quarterly basis." I've tried to make sure I am not taking this out of context or missing something. If this is being done there must be a WHOLE LOT of main drain testing going on!!! Any ITM Gurus got their ears on?? Thanks, Brad