Remember, the Appendix is not part of the standard, unless the appendices are 
specifically brought in by the Code.   
  

  
That section is purposely vague because the term “limited combustible” is open 
to interpretation since each situation is different. That needs to be an 
agreement between the Engineer of Record and the local AHJ as to what applies 
in each situation.
  

  
You could also argue that the wood studs are indeed structural since the 
Sheetrock won’t stand up on its own. Something can be structural without being 
considered load bearing.   
  
  
  
 Todd G Williams, PE  
Fire Protection Design/Consulting
  
Stonington, CT
  
860-535-2080 (ofc)
  
860-553-3553 (fax)
  
860-608-4559 (cell)
  
  
  
  

  
  
>   
> On Jun 15, 2018 at 9:34 AM,  <SET Micah Davis (mailto:[email protected])>  
> wrote:
>   
>   
>     
>   
>
>
>
>   
>
>  I have a project that has a concealed space with exposed wood wall framing.  
>   I added concealed space sprinklers per 8.15.1.2.1.    The engineer is 
> telling me to remove them stating that, since the walls are not load bearing, 
> they are not structural walls.    He then references Appendix A for 
> 8.15.1.2.1 that states the requirements to protect the space does not apply 
> for "nonstructural" wood.    Has anyone seen this before?    What is the 
> opinion of the Forum?    
>
>     
>
>   
>
>
>     
>
>  I will, of course, defer to the engineer, but I am recommending that the 
> contractor I'm working with get a letter from the engineer clearly stating 
> that they are requesting the sprinkler not be installed.
>
>     
>
>   
>
>   
>   
>
>
>
>   
>
>
>
>
>   
>   
>   
>   
>   
>   
>   
>   Micah Davis, SET
>   NICET #124745
>  Water Based Systems Layout, Level IV   
>  Dynamic Fire Designs
>   
>   
>   
>     
>   
>   
>   
> Mail: [email protected]
>  Mobile: 931-242-1299
>   www.dynamicfiredesigns.com (http://dynamicfiredesigns.com)
>       
>   
>   
>
> Dynamic Fire Designs • 13063 County Line Rd., Box #87 • Spring Hill • FL • 
> 34609
>   
>  This message is confidential. It may also be privileged or otherwise 
> protected by work product immunity or other legal rules. If you have received 
> it by mistake, please let us know by e-mail reply and delete it from your 
> system; you may not copy this message or disclose its contents to anyone. The 
> integrity and security of this message cannot be guaranteed on the Internet.
>
>   
>   
>   
>   
>   
>   
>
>   
>   
>   
>  _______________________________________________ Sprinklerforum mailing list 
> [email protected] 
> http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org
>   
  
  
     