That's probably it right there Steve-- pipe schedules were blind to water supply.

Thanks,
Brad

Quoting Steve Leyton <[email protected]>:

I don't think we can predict that Brad, but pipe sizes were much bigger in those days, weren't they? If I had to guess, I think the safety factor would be "more" if the available pressure was higher and "less" if it was fair-to-poor.

Regards,
Steve Leyton

-----Original Message-----
From: Sprinklerforum [mailto:[email protected]] On Behalf Of [email protected]
Sent: Monday, June 18, 2018 3:59 PM
To: [email protected]
Subject: Re: Safety Margin

My last two cents (i guess i started it and Roland is nudging toward an end):
A calculated system is simply a reconfigured pipe scheduled system,
i.e., make the second piece 1-1/4 and get rid of the 8".
Before calcs,5 heads on 1-1/2" was 'right on the curve'.
If that was changed to 4, how much safety margin is that?

Brad

Quoting Ben Young <[email protected]>:

Most of our work in done in Delaware where the 10 PSI safety margin has
been in place since before I started. I guess I take it for granted
anymore, and we have what I would consider not-great water. You're not
likely to get anything above 50 PSI static anywhere in the state. Maybe 60
if you're lucky.
Flows are in the 1000s. But I seriously don't even notice it anymore. I try
and shoot for 15-17 PSI to give our fitters some cushion for minor field
variations, but sometimes you can't do that and you have to live with 11 or
even 10.1. That 10 PSI isn't for field changes either, its specifically for
water supply degradation and fluctuation.

Its interesting to hear about the water level being lower in the winter
too, winter flow tests here are always 3-4 PSI higher and have better flow
vs the summer.  I have been seeing a lot of single hydrant flow tests
lately which is troubling.

I mean at the end of the day, 13 will get modified or overwritten by the
building code adopted or some other ordinance or legislative change, so why
is this any different?  States and towns have been deleting adding and
modifying sections of code forever, so if your local jurisdiction doesn't
like the 10 PSI, just change it when its adopted.


Benjamin Young

On Mon, Jun 18, 2018 at 1:20 PM, Daniel Arnold <[email protected]>
wrote:

But Horror stories have been the basis for ‘safety margins’ in our codes
and standards since their inception... including NFPA 13.

 There have been amazing strides made  in understanding and quantifying
the dynamics of sprinkler performance, limitations, etc. over the past 30
years and incorporating that knowledge into NFPA 13. A defined safety
factor in hydraulic calculations is but one logical step in the continuing
maturation of 13  and will eventually be in the standard. The more useful
discussion is how it should be quantified and Incorporated.   I agree with
Scott and share his experiences....NFIRS stats are not helpful in
justifying technical stagnation.

I absolutely understand and agree with the position that a safety factor
is already baked in the standard but what is it?  Saying it’s “enough”
without being able to eventually define it doesn’t help further progress.

... 2 cents from a lurker (usually 😉)

Daniel Arnold, PE, FSFPE
Seneca Fire Engineering, LLC
Atlanta, Georgia

Daniel L. Arnold, PE, FSFPE
Sent from my iPhone

On Jun 18, 2018, at 11:34 AM, Mark Sornsin [FAR] <[email protected]>
wrote:

All of the horror stories in the world do not change the fact that
requiring a specific safety margin for calculations is difficult to justify
in an internationally recognized standard.  I could see Annex language
offering pros for a margin and maybe giving examples of when one might be
considered.



In my view it’s the responsibility of the person engineering the system to
make this call. In this industry 99% of the time that is the designer
working for the low-bid contractor. The designer who may or may not be
NICET certified, depending on the rules of the jurisdiction in which they
are working. The point is the person with the most knowledge of the local
conditions should be making this call.  In an ideal world, when you have
someone specifying the design parameters for a bid project, it would be the
specifying engineer. I also realize that this is fantasy 98% of the time,
which is a stain on the engineering profession, but that’s a different
rant. We can’t expect to codify a requirement like this in a standard that
needs to apply throughout the world. It would require specific numbers and
these will vary on local conditions. Instead it is the engineer/designers
responsibility to become familiar with local conditions and adjust
accordingly.  The example of reduced water levels in municipal water towers
is a great one. Not all cities engage in this practice, but where they do
the designer needs to know what the minimum static pressures can be.  Or
the local reviewing authority needs to adopt specific requirements to match
their local conditions.



But the real problem comes when a contractor is bidding on a job with no
real engineering guidance and no local amendments to account for special
local conditions. The low-bid contractor or will be the one who assumes
their water test is valid despite having taken it at the highest possible
pressure of the day/season. And a specific safety margin requirement in
NFPA 13 cannot guarantee proper correction for this error.



<image1fad98.JPG> <http://www.SummitCoUS.com> Mark Sornsin
Sr. Fire Protection Engineer
Direct: 701-499-1391
Cell: 701-526-8585

*From:* Sprinklerforum [mailto:[email protected].
org <[email protected]>] *On Behalf Of *Scott
Futrell
*Sent:* Saturday, June 16, 2018 9:51 AM
*To:* [email protected]
*Subject:* RE: Safety Margin



As a plan specifier, plan reviewer and an investigator I see designs right
to the supply and then as-built conditions far worse (read more demanding)
than the design submitted with the calcs.  This is not a regional
observation.



Additionally, I am aware of communities that lower elevated tank levels
20’ in winter to lower heating costs.  Contractors in those areas do NOT
adjust flow tests for this seasonal variation.



No safety margin what-so-ever in NFPA 13 is unreasonable for a design
standard.



Arguments on the floor including ‘requiring all systems to have back-up
power’ were ridiculous.



Scott



Office: (763) 425-1001 x2

Cell: (612) 759-5556



*From:* Sprinklerforum [mailto:[email protected].
org <[email protected]>] *On Behalf Of *Steve
Leyton
*Sent:* Friday, June 15, 2018 2:16 PM
*To:* [email protected]
*Subject:* RE: Safety Margin



That was the conversation on the floor of the code hearing.  The concerns
underscored by the CAM were not about whether safety factor is a good
practice, it was that a fixed minimum value as high as 10 PSI could trigger
all sorts of cost-impact consequences, particularly in areas where
pressures are middling to poor – in Rhode Island, 10 PSI could be 25-30% of
the available pressure.



In the West, due primarily to the politics of drought, water districts are
using models in lieu of physical flow tests.  Prudent and conservative
programming makes it possible for them to issue safeguarded values from
which it’s not necessary to reduce the available pressure.  For ex., City
of San Diego uses a three-level safety factor in their (highly accurate)
models:  starting with legacy drought water levels in the reservoirs, then
factor the highest seasonal demand, then the highest peak day demand of
that season.   The values we’re getting are usually significantly lower
than what can be measured on the hydrant, and this practice isn’t without
controversy because there are obvious complications that can and do occur,
particularly with existing systems based on 20-year old (and older)
pressures that were physically measured (with crappy equipment) when first
designed and built.



But if modeling becomes the new normal, prudent water district engineering
departments and fire departments they serve can coordinate manipulating
data to include reasonable safety factors.  The range of variation in
pressures, accuracy of flow test equipment, the use of modeling in many
areas … there are too many variables to set a fixed minimum safety factor
based on PSI, IMHO.



SML



*From:* Sprinklerforum [mailto:[email protected].
org <[email protected]>] *On Behalf Of *Parsley
Consulting
*Sent:* Friday, June 15, 2018 12:00 PM
*To:* [email protected]
*Subject:* Re: Safety Margin



Richard,

If my memory is accurate of the issues raised in the discussion that
ambiguity was a part of the differing viewpoints.

Some argued that 10 psi was not workable in their locale as their
pressures were so limited that an imposition of 10 psi was simply to
drastic and would result in much larger pipe sizes as a result.

Others argued that 10 psi was not enough, and in their area 10 psi didn't
equal 10%, and there was some reluctance to base their designs on a
pressure greater than 90% of the available.

It was quite a discussion.


*Ken Wagoner, SET *


*Parsley Consulting 350 West 9th Avenue, Suite 206 Escondido, California
92025 *
*Phone 760-745-6181 Visit the website <http://www.parsleyconsulting.com/> *

On 06/15/2018 10:23 AM, Richard Carr wrote:

Even though it is not in NFPA most AHJ’s require some sort of safety
margin, 10%, 10 psi which we have had to provide for a long time so most
designers know to leave safety margin in the calc’s. it would be nice if
they all used the same amount.



Richard M. Carr, SET

Project Manager/Design

Diboco Fire Sprinklers, Inc.

325 Jackson Loop Road

Flat Rock, NC  28731



[email protected]

828-696-3400

828-696-2288 Fax

828-708-9118 Mobile



<image001.jpg>



<image002.png>





*From:* Sprinklerforum <[email protected]>
<[email protected]> *On Behalf Of *Parsley
Consulting
*Sent:* Friday, June 15, 2018 1:22 PM
*To:* [email protected]
*Subject:* Safety Margin



Scott,

Based on the material which was presented to the -24 and -291 committee
meetings I believed the proposed safety margin and the means to calculate
that margin there was some merit in the proposal.

For reasons I don't quite remember the PI was voted down at the 2nd draft
meeting.  I listened to some of the discussion, and there were some good
points made.  I'm not terribly surprised it failed at the convention
level.  Perhaps the attendees were following the lead of the technical
committees, and declining to overrule their decision.

sincerely,


*Ken Wagoner, SET **Parsley Consulting*


* 350 West 9th Avenue, Suite 206 Escondido, California 92025 *
*Phone 760-745-6181 Visit the website <http://www.parsleyconsulting.com/> *

On 06/15/2018 8:09 AM, Scott Futrell wrote:

Only that the 'safety margin' inclusion in the 2019 edition of NFPA
13 failed, so it won't be included or required.



I consider this unfortunate, but I'd guess that not everyone on the
forum would agree.



Scott



Office: (763) 425-1001 x2

Cell: (612) 759-5556



-----Original Message-----

From: Sprinklerforum
[mailto:[email protected]
<[email protected]>] On Behalf Of
[email protected]

Sent: Thursday, June 14, 2018 5:46 PM

To: [email protected]

Subject: NFPA Vegas Convention



I didn't make it again this year.

"Caputo" is the only speaker name I recognized.

Anybody have any earthshaking epiphanies?





_______________________________________________

Sprinklerforum mailing list

[email protected]

http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org

_______________________________________________

Sprinklerforum mailing list

[email protected]

http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org







_______________________________________________

Sprinklerforum mailing list

[email protected]

http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org




______________________________________________________________________
This email has been scanned by the Symantec Email Security.cloud service.
For more information please visit http://www.symanteccloud.com
______________________________________________________________________

_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.
org

_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.
org





_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org
_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org



_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org

Reply via email to