And NFIRS. I have little faith in results. When we decided to address false 
alarms we spent a lot of time, effort on NFIRS.  It still took two years just 
to get codes 73 & 74 (false alarms with different types of cause) regularly 
entered correctly. 

NFIRS. Ok for house fires. Commercial? No, we weren’t get good info in. 

Best.

Bruce Verhei 

> On Jun 17, 2018, at 21:45, Bruce Verhei <[email protected]> wrote:
> 
> We’ll leave 13-R vertical fire spread up from unprotected deck then lanai’s 
> to one side. 
> 
> In a career in a jurisdiction with so much high piled storage that the FF’s 
> called one area tilt up town we had one fire that opened 33 heads. 
> Manufacturer of SIF panels. Ceiling temps? Some black marks, but no real 
> attack on the CDX. The is no pre-wetting when 8’x4’x4’ blocks of styrofoam 
> are burning. Fire burns around underside, then heads to ceiling, a couple 
> heads open. Repeat. FF’s working in very low visibility conditions, but not 
> hot conditions, deploy several (3-4?) 2 1/2”’s and eventually 1 3/4”’s, run 
> through several bottles each, and extinguish fire. Another place made 
> polyurethane buns from liquid. A dozen heads? A place that bought zinc and 
> electricity, melted the zinc and made those inserts that the screw goes into 
> when you assemble KD furniture. Machines remind one of injection mold 
> operation, except for the open tops of liquid zinc. Air, water, and hydraulic 
> lines to machines. Earthquake sloshes zinc out of tanks. Zinc or fire in drip 
> pans causes lines to fails. Fireball operates 12-15 heads. Fire controlled. 
> 
> All fires well less than design area.
> 
> These are the only fires we had that operated more than half a dozen heads. 
> 
> Doors not locked from the outside. Sprinkler valves open. Gauges all seem 
> right. FACP panel status green. Confidence tests current. Sprinkler design 
> criteria is adequate for fuel matrix. 
> 
> If you don’t get these you haven’t done the basics of a fire inspection. 
> 
> Scott, the problems you describe I would assume are not confined by the 
> property line. It’s probably common all over the town.
> 
> Best.
> 
> Bruce Verhei 
> 
>> On Jun 17, 2018, at 19:16, Scott Futrell <[email protected]> wrote:
>> 
>> Ron,
>>  
>> We’ll need to talk about these so called statistics that come from 
>> incomplete and inaccurate NFIRS reports almost exclusively.  I’ve researched 
>> the statistics, spoken with NFPA, and I can tell you the statistics are only 
>> as accurate as the firefighters writing them at the time of the fire. 
>> Investigations go on for months longer and NFIRS reports are rarely updated. 
>> Currently NFPA states that 97% of fires are controlled by 5 sprinklers or 
>> less, so that is up from what it used to be.
>>  
>> I can assure you that many of the fires I investigate, that have sprinklers 
>> that were ineffective are not accurately or not included in those 
>> statistics. $35M fire in Illinois recorded as less than $10M and didn’t make 
>> the NFPA large loss fires.  Sprinklered. Sprinklered part of the building 
>> burned to the ground…none of that made NFPA investigation or statistics.
>>  
>> I have pictures, reports, NFIRS reports and more to back this up and my 
>> files grow weekly.
>>  
>> I recently had an interesting debate with a NICET designer from Denver. I 
>> told her the flow test was wrong (it is of course), the pump test was 
>> incorrect and old (it is of course) and she hadn’t as-built the BFP on the 
>> plans correctly that her company replaced.  She told me “she didn’t have 
>> time to drive the two hours to Denver to verify the as-built conditions” and 
>> that was the flow test the city gave them (incorrect side of the building, 
>> old, and off larger main than the pump suction). The supposed safety margin 
>> she was providing was non-existent.  I realize this story isn’t reflective 
>> of requirements for a safety margin, but it is reflective of an improperly 
>> designed system that will be just fine until we have a fire and then we find 
>> out it wasn’t.
>>  
>> I have many design related stories and my plan review rate remains at >70% 
>> revise and resubmit with the majority of the problems water supply and 
>> hydraulic calculation related.
>>  
>> I have a NFIRS report in my hands that states that the sprinklers 
>> operated/ineffective and that three operated.  There were more than three 
>> that operated, but more importantly the two branch lines directly over the 
>> area of origin were capped without a water supply to those sprinklers!!!
>>  
>> Take care my friend.
>>  
>> Scott
>>  
>> Office: (763) 425-1001 x2
>> Cell: (612) 759-5556
>>  
>> From: Sprinklerforum [mailto:[email protected]] 
>> On Behalf Of Ron Greenman
>> Sent: Saturday, June 16, 2018 11:25 AM
>> To: [email protected]
>> Subject: Re: Safety Margin
>>  
>> Where is the data that supports the need? I don't have the exact numbers in 
>> my head this morning, nor am I willing to look them up but the statistics 
>> are that somewhere above 90% of all fires are controlled by a single or two 
>> sprinklers operating, and above 95% are controlled by three (anybody jump in 
>> with the exact numbers), and since we design to nine or usually more 
>> typically I'd say a safety factor is already built-in. I think if you look 
>> at systems that have been overwhelmed you'll mostly find that maintenance 
>> was not carried out properly, or TIs were not addressed, or fires got into 
>> unsprinklered or under sprinklered attics, or any number of things that were 
>> existing code deficient. I also think you'd find that many fires were 
>> controlled by systems that were existing code deficient. My mind could be 
>> changed if I were shown a significant amount of loss due to inadequate water 
>> in the original design in buildings where there were no other factors as 
>> stated above, but I'm not seeing a need. Additionally, in my neck of the 
>> woods, all the metropolitan jurisdictions are already imposing a 10# or 10% 
>> factor already. Most are holding to that number like it's gold and even if 
>> the hose stream allowance takes you over the supply line by 1/2# you're 
>> surely going to have to re-design. This is unreasonable already, and I 
>> realize the FDs already often act like over-indulgent parents, so I'm 
>> especially worried that if this 10#s is codified it will be an add-on to the 
>> already existent 10#s. I see tanks and pumps in everyone's future because of 
>> mistrust of municipal water systems. Rant over. Ron out.
>>  
>>  
>> Ron Greenman
>> 
>> [email protected]
>> 
>> 253.576.9700
>>  
>> The Universe is monstrously indifferent to the presence of man. -Werner 
>> Herzog, screenwriter, film director, author, actor and opera director (1942-)
>>  
>>  
>> On Sat, Jun 16, 2018 at 7:50 AM Scott Futrell <[email protected]> wrote:
>> As a plan specifier, plan reviewer and an investigator I see designs right 
>> to the supply and then as-built conditions far worse (read more demanding) 
>> than the design submitted with the calcs.  This is not a regional 
>> observation.
>>  
>> Additionally, I am aware of communities that lower elevated tank levels 20’ 
>> in winter to lower heating costs.  Contractors in those areas do NOT adjust 
>> flow tests for this seasonal variation.
>>  
>> No safety margin what-so-ever in NFPA 13 is unreasonable for a design 
>> standard.
>>  
>> Arguments on the floor including ‘requiring all systems to have back-up 
>> power’ were ridiculous.
>>  
>> Scott
>>  
>> Office: (763) 425-1001 x2
>> Cell: (612) 759-5556
>>  
>> From: Sprinklerforum [mailto:[email protected]] 
>> On Behalf Of Steve Leyton
>> Sent: Friday, June 15, 2018 2:16 PM
>> To: [email protected]
>> Subject: RE: Safety Margin
>>  
>> That was the conversation on the floor of the code hearing.  The concerns 
>> underscored by the CAM were not about whether safety factor is a good 
>> practice, it was that a fixed minimum value as high as 10 PSI could trigger 
>> all sorts of cost-impact consequences, particularly in areas where pressures 
>> are middling to poor – in Rhode Island, 10 PSI could be 25-30% of the 
>> available pressure.
>>  
>> In the West, due primarily to the politics of drought, water districts are 
>> using models in lieu of physical flow tests.  Prudent and conservative 
>> programming makes it possible for them to issue safeguarded values from 
>> which it’s not necessary to reduce the available pressure.  For ex., City of 
>> San Diego uses a three-level safety factor in their (highly accurate) 
>> models:  starting with legacy drought water levels in the reservoirs, then 
>> factor the highest seasonal demand, then the highest peak day demand of that 
>> season.   The values we’re getting are usually significantly lower than what 
>> can be measured on the hydrant, and this practice isn’t without controversy 
>> because  there are obvious complications that can and do occur, particularly 
>> with existing systems based on 20-year old (and older) pressures that were 
>> physically measured (with crappy equipment) when first designed and built.
>>  
>> But if modeling becomes the new normal, prudent water district engineering 
>> departments and fire departments they serve can coordinate manipulating data 
>> to include reasonable safety factors.  The range of variation in pressures, 
>> accuracy of flow test equipment, the use of modeling in many areas … there 
>> are too many variables to set a fixed minimum safety factor based on PSI, 
>> IMHO.
>>  
>> SML
>>  
>> From: Sprinklerforum [mailto:[email protected]] 
>> On Behalf Of Parsley Consulting
>> Sent: Friday, June 15, 2018 12:00 PM
>> To: [email protected]
>> Subject: Re: Safety Margin
>>  
>> Richard,
>> 
>> If my memory is accurate of the issues raised in the discussion that 
>> ambiguity was a part of the differing viewpoints.
>> 
>> Some argued that 10 psi was not workable in their locale as their pressures 
>> were so limited that an imposition of 10 psi was simply to drastic and would 
>> result in much larger pipe sizes as a result.
>> 
>> Others argued that 10 psi was not enough, and in their area 10 psi didn't 
>> equal 10%, and there was some reluctance to base their designs on a pressure 
>> greater than 90% of the available.
>> 
>> It was quite a discussion. 
>> Ken Wagoner, SET
>> Parsley Consulting
>> 350 West 9th Avenue, Suite 206
>> Escondido, California 92025
>> Phone 760-745-6181
>> Visit the website
>> On 06/15/2018 10:23 AM, Richard Carr wrote:
>> Even though it is not in NFPA most AHJ’s require some sort of safety margin, 
>> 10%, 10 psi which we have had to provide for a long time so most designers 
>> know to leave safety margin in the calc’s. it would be nice if they all used 
>> the same amount.
>>  
>> Richard M. Carr, SET
>> Project Manager/Design
>> Diboco Fire Sprinklers, Inc.
>> 325 Jackson Loop Road
>> Flat Rock, NC  28731
>>  
>> [email protected]
>> 828-696-3400
>> 828-696-2288 Fax
>> 828-708-9118 Mobile
>>  
>> 
>>  
>> 
>>  
>>  
>> From: Sprinklerforum <[email protected]> On 
>> Behalf Of Parsley Consulting
>> Sent: Friday, June 15, 2018 1:22 PM
>> To: [email protected]
>> Subject: Safety Margin
>>  
>> Scott,
>> 
>> Based on the material which was presented to the -24 and -291 committee 
>> meetings I believed the proposed safety margin and the means to calculate 
>> that margin there was some merit in the proposal. 
>> 
>> For reasons I don't quite remember the PI was voted down at the 2nd draft 
>> meeting.  I listened to some of the discussion, and there were some good 
>> points made.  I'm not terribly surprised it failed at the convention level.  
>> Perhaps the attendees were following the lead of the technical committees, 
>> and declining to overrule their decision.
>> 
>> sincerely,
>> Ken Wagoner, SET
>> Parsley Consulting
>> 350 West 9th Avenue, Suite 206
>> Escondido, California 92025
>> Phone 760-745-6181
>> Visit the website
>> On 06/15/2018 8:09 AM, Scott Futrell wrote:
>> Only that the 'safety margin' inclusion in the 2019 edition of NFPA 13 
>> failed, so it won't be included or required.
>>  
>> I consider this unfortunate, but I'd guess that not everyone on the forum 
>> would agree.
>>  
>> Scott
>>  
>> Office: (763) 425-1001 x2
>> Cell: (612) 759-5556
>>  
>> -----Original Message-----
>> From: Sprinklerforum [mailto:[email protected]] 
>> On Behalf Of [email protected]
>> Sent: Thursday, June 14, 2018 5:46 PM
>> To: [email protected]
>> Subject: NFPA Vegas Convention
>>  
>> I didn't make it again this year.
>> "Caputo" is the only speaker name I recognized.
>> Anybody have any earthshaking epiphanies?
>>  
>>  
>> _______________________________________________
>> Sprinklerforum mailing list
>> [email protected]
>> http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org
>> _______________________________________________
>> Sprinklerforum mailing list
>> [email protected]
>> http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org
>>  
>>  
>>  
>> 
>> _______________________________________________
>> Sprinklerforum mailing list
>> [email protected]
>> http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org
>>  
>> _______________________________________________
>> Sprinklerforum mailing list
>> [email protected]
>> http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org
>> _______________________________________________
>> Sprinklerforum mailing list
>> [email protected]
>> http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org