It’s been done forever with spray sprinklers and we’ve recommended it many times as an effort to reach the 8 ft separation. Unfortunately, the only guidance we have is in 8.5.2 Protection Areas per Sprinkler. The problem is that L dimension is defined as the PERPENDICULAR distance to the SPRINKLER on the adjacent branch line. I tried to correct this and the TC didn’t like saying the perpendicular distance to the adjacent branch line. I don't remember the exact excuse but they are slow about accepting change to their text. Since not all systems are laid out in perfect symmetry (AND NOT REQUIRED TO BE), this philosophy is not intended to negate staggering the layout.
Roland Roland Huggins, PE - Senior VP Engineering American Fire Sprinkler Assn. Dallas, TX http://www.firesprinkler.org <http://www.firesprinkler.org/> Fire Sprinklers Saves Lives > On Jun 19, 2018, at 3:26 PM, JD Gamble <[email protected]> wrote: > > I need to move a row of ESFR to make room for a door that the ARCH is adamant > about keeping. Can I stagger the spacing (space them at 8’-0” in lieu of the > current 10’-0”) on the one line effected as long as I don’t exceed the > maximum or minimum spacing of the sprinklers? Do I have to match that > spacing / layout with the other lines? > > Just double checking myself. > > TIA > > Life Safety Solutions of Sheridan > > JD Gamble > [email protected] <mailto:[email protected]> > (307) 763-3361 > > _______________________________________________ > Sprinklerforum mailing list > [email protected] > <mailto:[email protected]> > http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org > <http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org>
_______________________________________________ Sprinklerforum mailing list [email protected] http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org