This was actually my mindset. And perhaps misplaced concern. Do I have to match 
surrounding sprinklers to accommodate a door?  Maybe I’m overthinking it?

Get Outlook for iOS<https://aka.ms/o0ukef>
________________________________
From: Sprinklerforum <[email protected]> on behalf 
of Kyle.Montgomery <[email protected]>
Sent: Wednesday, June 20, 2018 9:04:10 AM
To: [email protected]
Subject: RE: [EXTERNAL] Re: Staggering ESFR

Maybe not the same scenario as the OP, but related: What about 8.12.2.2.3 (2)? 
It says:

“Adjacent branch lines shall maintain the same pattern”

Might not apply here since it only applies if you are deviating from the 
maximum spacing to eliminate an obstruction, but what is the intent/purpose 
behind it?

-Kyle M

From: Sprinklerforum [mailto:[email protected]] On 
Behalf Of Roland Huggins
Sent: Wednesday, June 20, 2018 7:43 AM
To: [email protected]
Subject: [EXTERNAL] Re: Staggering ESFR

It’s been done forever with spray sprinklers and we’ve recommended it many 
times as an effort to reach the 8 ft separation.  Unfortunately, the only 
guidance we have is in 8.5.2 Protection Areas per Sprinkler.  The problem is 
that L dimension is defined as the PERPENDICULAR distance to the SPRINKLER on 
the adjacent branch line.  I tried to correct this and the TC didn’t like 
saying the perpendicular distance to the adjacent branch line. I don't remember 
the exact excuse but they are slow about accepting change to their text.  Since 
not all systems are laid out in perfect symmetry (AND NOT REQUIRED TO BE), this 
philosophy is not intended to negate staggering the layout.

Roland


Roland Huggins, PE - Senior VP Engineering
American Fire Sprinkler Assn.
Dallas, TX
http://www.firesprinkler.org<https://urldefense.proofpoint.com/v2/url?u=http-3A__www.firesprinkler.org_&d=DwMFaQ&c=wn3mZQLIuInh2ClcJ0_DIA&r=Z_2A85VL7AQzoqudh6uOyS3bn8etxB7nLN8OBJwQd9A&m=edPohNfxwkOR4DZbtVRmquhtSBj4Q9wlZiK43YT-n9A&s=WJq7PU8DHJ6QwLJinbdzhCsAZMCgEZ2g7Qh5fNEc8w8&e=>

Fire Sprinklers Saves Lives




On Jun 19, 2018, at 3:26 PM, JD Gamble 
<[email protected]<mailto:[email protected]>> wrote:

I need to move a row of ESFR to make room for a door that the ARCH is adamant 
about keeping.  Can I stagger the spacing (space them at 8’-0” in lieu of the 
current 10’-0”) on the one line effected as long as I don’t exceed the maximum 
or minimum spacing of the sprinklers?  Do I have to match that spacing / layout 
with the other lines?

Just double checking myself.

TIA

Life Safety Solutions of Sheridan

JD Gamble
[email protected]<mailto:[email protected]>
(307) 763-3361

_______________________________________________
Sprinklerforum mailing list
[email protected]<mailto:[email protected]>
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org<https://urldefense.proofpoint.com/v2/url?u=http-3A__lists.firesprinkler.org_listinfo.cgi_sprinklerforum-2Dfiresprinkler.org&d=DwMFaQ&c=wn3mZQLIuInh2ClcJ0_DIA&r=Z_2A85VL7AQzoqudh6uOyS3bn8etxB7nLN8OBJwQd9A&m=edPohNfxwkOR4DZbtVRmquhtSBj4Q9wlZiK43YT-n9A&s=cp7h4nsyhZjHiDiBNCkI8qXnzj4R0VvLpD58VkpmNc4&e=>

_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org

Reply via email to