8.15.14 doesn't apply to this application.  That section is for grated 
"ceilings" installed below sprinklers.

Trellis construction being open is similar to a pergola where there is no 
ceiling/roof.

Being open, you can't trap heat or smoke as long as they don't plan to let 
plants grow on the trellis work to create a "green roof/ceiling".

Is this for public seating?  If it is, there may be local requirements for 
overhead materials if they are combustible.



Craig Prahl | Jacobs | Group Lead - Fire Protection | 864.676.5252 | 
[email protected] | www.jacobs.com<http://www.jacobs.com/>

From: Sprinklerforum [mailto:[email protected]] On 
Behalf Of Kyle.Montgomery
Sent: Monday, June 25, 2018 11:02 AM
To: [email protected]
Subject: RE: [EXTERNAL] RE: % open

Then I don't think the section sited below is the correct application. I'm 
honestly not sure where that is quantified. We usually are successful making 
the argument that it won't trap heat, but I can't think of where that's 
actually spelled out in the code.  I'm interested in the responses to this one.

Would it not otherwise meet the criteria for omitting sprinklers under an 
exterior projection?

-Kyle M

From: Sprinklerforum [mailto:[email protected]] On 
Behalf Of MFP Design, LLC
Sent: Monday, June 25, 2018 7:52 AM
To: 
[email protected]<mailto:[email protected]>
Subject: [EXTERNAL] RE: % open

Yes.  That is exactly it.

[MFP_logo_F]
Travis Mack, SET
MFP Design, LLC
3356 E Vallejo Ct
Gilbert, AZ 85298
480-505-9271
fax: 866-430-6107
email:[email protected]<mailto:email:[email protected]>

http://www.mfpdesign.com<https://urldefense.proofpoint.com/v2/url?u=https-3A__na01.safelinks.protection.outlook.com_-3Furl-3Dhttp-253A-252F-252Fwww.mfpdesign.com-252F-26data-3D02-257C01-257C-257C1121d49f9e6b4cf248f108d4df580e77-257C14e5497c16da42e69ffa77d19bafe511-257C0-257C0-257C636379016677342180-26sdata-3DHJ8OA4xyeHAoxXNz5mu-252FYfycgtd5nsFrrpvzulZiNkQ-253D-26reserved-3D0&d=DwMFAg&c=wn3mZQLIuInh2ClcJ0_DIA&r=Z_2A85VL7AQzoqudh6uOyS3bn8etxB7nLN8OBJwQd9A&m=--4Q7Dz9BATd8WUxsQYTT9-zwN6lA-WWPx1vQGUNOSs&s=wAYQUJqAnaCqfrR5MlqvBUPsIFuAxuv94pP0PHJuAKI&e=>
https://www.facebook.com/pages/MFP-Design-LLC/92218417692<https://urldefense.proofpoint.com/v2/url?u=https-3A__na01.safelinks.protection.outlook.com_-3Furl-3Dhttps-253A-252F-252Fwww.facebook.com-252Fpages-252FMFP-2DDesign-2DLLC-252F92218417692-26data-3D02-257C01-257C-257C1121d49f9e6b4cf248f108d4df580e77-257C14e5497c16da42e69ffa77d19bafe511-257C0-257C0-257C636379016677342180-26sdata-3DH-252BwdcgK8DLGBcNoqJEvUrzsXngySwkX56Vgf9gM9EGk-253D-26reserved-3D0&d=DwMFAg&c=wn3mZQLIuInh2ClcJ0_DIA&r=Z_2A85VL7AQzoqudh6uOyS3bn8etxB7nLN8OBJwQd9A&m=--4Q7Dz9BATd8WUxsQYTT9-zwN6lA-WWPx1vQGUNOSs&s=uC-yrDZQYbzRw_0mpbCvvFdYDJvJKkYJD36M5tJ9XZE&e=>
Send large files to us via: 
https://www.hightail.com/u/MFPDesign<https://urldefense.proofpoint.com/v2/url?u=https-3A__na01.safelinks.protection.outlook.com_-3Furl-3Dhttps-253A-252F-252Fwww.hightail.com-252Fu-252FMFPDesign-26data-3D02-257C01-257C-257C1121d49f9e6b4cf248f108d4df580e77-257C14e5497c16da42e69ffa77d19bafe511-257C0-257C0-257C636379016677342180-26sdata-3DeGdMZGu2wXhUupGwgGTrqF3b54OP5-252BAZvlHhABSexWY-253D-26reserved-3D0&d=DwMFAg&c=wn3mZQLIuInh2ClcJ0_DIA&r=Z_2A85VL7AQzoqudh6uOyS3bn8etxB7nLN8OBJwQd9A&m=--4Q7Dz9BATd8WUxsQYTT9-zwN6lA-WWPx1vQGUNOSs&s=VANcNpjh21wGFjVtIZXIcXG1IhFERc30VWUn2SWIF8s&e=>
LinkedIn: 
https://www.linkedin.com/in/travismack<https://urldefense.proofpoint.com/v2/url?u=https-3A__na01.safelinks.protection.outlook.com_-3Furl-3Dhttps-253A-252F-252Fwww.linkedin.com-252Fin-252Ftravismack-26data-3D02-257C01-257C-257C1121d49f9e6b4cf248f108d4df580e77-257C14e5497c16da42e69ffa77d19bafe511-257C0-257C0-257C636379016677342180-26sdata-3DtT5E7LsZjSmyreKi4gDCa70EWN-252BZodi-252FhbeCbHNRijI-253D-26reserved-3D0&d=DwMFAg&c=wn3mZQLIuInh2ClcJ0_DIA&r=Z_2A85VL7AQzoqudh6uOyS3bn8etxB7nLN8OBJwQd9A&m=--4Q7Dz9BATd8WUxsQYTT9-zwN6lA-WWPx1vQGUNOSs&s=AknKYnYQfWiaEOx4mPnCJS8nwuz8Wgcrkzmw7V0Oew0&e=>

"The bitterness of poor quality remains long after the sweetness of low price 
is forgotten."

From: Sprinklerforum 
<[email protected]<mailto:[email protected]>>
 On Behalf Of Kyle.Montgomery
Sent: Monday, June 25, 2018 7:52 AM
To: 
[email protected]<mailto:[email protected]>
Subject: RE: % open

Travis,

Are you talking about an exterior trellis? Something that would not have 
sprinklers above, just open to the sky above?

-Kyle M

From: Sprinklerforum [mailto:[email protected]] On 
Behalf Of John Paulsen
Sent: Monday, June 25, 2018 7:48 AM
To: 
[email protected]<mailto:[email protected]>
Subject: [EXTERNAL] RE: % open

8.15.14.1 (2013)

John Paulsen - SET
Crown Fire System Design
6282 Seeds Rd.
Grove City, OH 43123
P - 614-782-2438
F - 614-782-2374
C - 614-348-8206



From: Sprinklerforum [mailto:[email protected]] On 
Behalf Of MFP Design, LLC
Sent: Monday, June 25, 2018 10:44 AM
To: 
[email protected]<mailto:[email protected]>
Subject: % open

I have a project where the architect is asking what is the % opening required 
in a trellis type structure so that sprinklers are not required.  70% open is 
coming to mind, but I can't find a section referencing anything like that.  Can 
anyone help point me in the right direction?

[MFP_logo_F]
Travis Mack, SET
MFP Design, LLC
3356 E Vallejo Ct
Gilbert, AZ 85298
480-505-9271
fax: 866-430-6107
email:[email protected]<mailto:email:[email protected]>

http://www.mfpdesign.com<https://urldefense.proofpoint.com/v2/url?u=https-3A__na01.safelinks.protection.outlook.com_-3Furl-3Dhttp-253A-252F-252Fwww.mfpdesign.com-252F-26data-3D02-257C01-257C-257C1121d49f9e6b4cf248f108d4df580e77-257C14e5497c16da42e69ffa77d19bafe511-257C0-257C0-257C636379016677342180-26sdata-3DHJ8OA4xyeHAoxXNz5mu-252FYfycgtd5nsFrrpvzulZiNkQ-253D-26reserved-3D0&d=DwMFAg&c=wn3mZQLIuInh2ClcJ0_DIA&r=Z_2A85VL7AQzoqudh6uOyS3bn8etxB7nLN8OBJwQd9A&m=XXSFsdp3C6lw_EoQ52zofB317Ch5AodVrALwfCjiGik&s=UDadvmExbxR_qUp3fko6fjEGJjwHxPSOhhQhvMgFwPg&e=>
https://www.facebook.com/pages/MFP-Design-LLC/92218417692<https://urldefense.proofpoint.com/v2/url?u=https-3A__na01.safelinks.protection.outlook.com_-3Furl-3Dhttps-253A-252F-252Fwww.facebook.com-252Fpages-252FMFP-2DDesign-2DLLC-252F92218417692-26data-3D02-257C01-257C-257C1121d49f9e6b4cf248f108d4df580e77-257C14e5497c16da42e69ffa77d19bafe511-257C0-257C0-257C636379016677342180-26sdata-3DH-252BwdcgK8DLGBcNoqJEvUrzsXngySwkX56Vgf9gM9EGk-253D-26reserved-3D0&d=DwMFAg&c=wn3mZQLIuInh2ClcJ0_DIA&r=Z_2A85VL7AQzoqudh6uOyS3bn8etxB7nLN8OBJwQd9A&m=XXSFsdp3C6lw_EoQ52zofB317Ch5AodVrALwfCjiGik&s=2cL17WmNxprzrKunHO7EaTVV46hC_zGM3rCXzOuh3F4&e=>
Send large files to us via: 
https://www.hightail.com/u/MFPDesign<https://urldefense.proofpoint.com/v2/url?u=https-3A__na01.safelinks.protection.outlook.com_-3Furl-3Dhttps-253A-252F-252Fwww.hightail.com-252Fu-252FMFPDesign-26data-3D02-257C01-257C-257C1121d49f9e6b4cf248f108d4df580e77-257C14e5497c16da42e69ffa77d19bafe511-257C0-257C0-257C636379016677342180-26sdata-3DeGdMZGu2wXhUupGwgGTrqF3b54OP5-252BAZvlHhABSexWY-253D-26reserved-3D0&d=DwMFAg&c=wn3mZQLIuInh2ClcJ0_DIA&r=Z_2A85VL7AQzoqudh6uOyS3bn8etxB7nLN8OBJwQd9A&m=XXSFsdp3C6lw_EoQ52zofB317Ch5AodVrALwfCjiGik&s=rOaLbk6urRmGXdsyO0D1xyUGO52mWjpY1s8ohxYg3-8&e=>
LinkedIn: 
https://www.linkedin.com/in/travismack<https://urldefense.proofpoint.com/v2/url?u=https-3A__na01.safelinks.protection.outlook.com_-3Furl-3Dhttps-253A-252F-252Fwww.linkedin.com-252Fin-252Ftravismack-26data-3D02-257C01-257C-257C1121d49f9e6b4cf248f108d4df580e77-257C14e5497c16da42e69ffa77d19bafe511-257C0-257C0-257C636379016677342180-26sdata-3DtT5E7LsZjSmyreKi4gDCa70EWN-252BZodi-252FhbeCbHNRijI-253D-26reserved-3D0&d=DwMFAg&c=wn3mZQLIuInh2ClcJ0_DIA&r=Z_2A85VL7AQzoqudh6uOyS3bn8etxB7nLN8OBJwQd9A&m=XXSFsdp3C6lw_EoQ52zofB317Ch5AodVrALwfCjiGik&s=QKz1KKXvAldylNJ_R_aJTTdt9r_5dF87zFky8P5VaSk&e=>

"The bitterness of poor quality remains long after the sweetness of low price 
is forgotten."


________________________________________________________________________________________

NOTICE - This communication may contain confidential and privileged information 
that is for the sole use of the intended recipient. Any viewing, copying or 
distribution of, or reliance on this message by unintended recipients is 
strictly prohibited. If you have received this message in error, please notify 
us immediately by replying to the message and deleting it from your computer.
_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org

Reply via email to