One thought to keep an eye on: Many pressure reducing valves have a maximum 
pressure output of 165. If you design your original system to require more than 
that from the pump discharge, you may not get it once you put in the PRV (even 
though your pump discharge is much higher).

matt

-----Original Message-----
From: Sprinklerforum <[email protected]> On Behalf 
Of Matt Grise
Sent: Monday, July 16, 2018 3:41 PM
To: [email protected]
Subject: RE: PRV after pump discharge control valve

Just out of curiosity -how much boost are you starting with? What is the 
projected need in the future? 

Matt 

-----Original Message-----
From: Sprinklerforum <[email protected]> On Behalf 
Of Tom Duross
Sent: Monday, July 16, 2018 3:33 PM
To: [email protected]
Subject: RE: PRV after pump discharge control valve

You start bending the listings when playing with different impellers in the 
field.  In the old days these were listed assemblies and if you swap out an 
impeller, there does the listing.  Some still hold that to be true.  You might 
try a model series that meets both designs but with different pump ends.  Keep 
the base and driver.  A new pump end will have a new serial and new listing.  
Most pumps, electric split case anyway are usually pit tested as a pump end 
only before leaving the plant using one of their adjustable drivers.  When you 
have an inline, the impeller and case are bolted to the motor, and diesels 
historically have most times been tested as a complete pump too.  Not sure of 
the demands but this might be a question for you pump rep that maybe they can 
answer.
TD


Thank you Kyle, it means a great deal to me for you to say.
I was curious about the application too, and saw a 1250 gpm, 2600 rpm with a 
range of 69 psi based solely on impeller diameter.
Both impellers would need to be purchased and certified up front, and every one 
having signed off on the idea.
I even imagined a note on the enlarged pump room plan, "mount future impeller 
and name plate in locked cabinet next to spare sprinkler cabinet".

Brad


_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org

_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org

_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org

Reply via email to