We need a manufacturer’s rep on line. But if you get out their book they only 
cast a few pump casings. They engineer a wide variety of impellers to go with a 
casing and usually several different power plants. 

I’d been told in the past that final machining of the impeller was after order. 
Maybe the has changed as suppression-type sprinkler systems have become more 
common.

Maybe there are a very few super fitters out there who rebuild a pump, have an 
electricians card, and millwright skills. Maybe. When the engine or motor has 
problems, or the pump needs to be opened up its usually written up and a 
specialist comes in and works on it.

Manufacturer’s pre-test and certification. Hmm. Don’t know. Not redone when you 
replace original impeller with a like impeller.

But if you open it up that far you’ve already triggered a new acceptance test. 

Best.

Bruce Verhei 


> On Jul 16, 2018, at 13:41, Matt Grise <[email protected]> wrote:
> 
> Just out of curiosity -how much boost are you starting with? What is the 
> projected need in the future? 
> 
> Matt 
> 
> -----Original Message-----
> From: Sprinklerforum <[email protected]> On 
> Behalf Of Tom Duross
> Sent: Monday, July 16, 2018 3:33 PM
> To: [email protected]
> Subject: RE: PRV after pump discharge control valve
> 
> You start bending the listings when playing with different impellers in the 
> field.  In the old days these were listed assemblies and if you swap out an 
> impeller, there does the listing.  Some still hold that to be true.  You 
> might try a model series that meets both designs but with different pump 
> ends.  Keep the base and driver.  A new pump end will have a new serial and 
> new listing.  Most pumps, electric split case anyway are usually pit tested 
> as a pump end only before leaving the plant using one of their adjustable 
> drivers.  When you have an inline, the impeller and case are bolted to the 
> motor, and diesels historically have most times been tested as a complete 
> pump too.  Not sure of the demands but this might be a question for you pump 
> rep that maybe they can answer.
> TD
> 
> 
> Thank you Kyle, it means a great deal to me for you to say.
> I was curious about the application too, and saw a 1250 gpm, 2600 rpm with a 
> range of 69 psi based solely on impeller diameter.
> Both impellers would need to be purchased and certified up front, and every 
> one having signed off on the idea.
> I even imagined a note on the enlarged pump room plan, "mount future impeller 
> and name plate in locked cabinet next to spare sprinkler cabinet".
> 
> Brad
> 
> 
> _______________________________________________
> Sprinklerforum mailing list
> [email protected]
> http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org
> 
> _______________________________________________
> Sprinklerforum mailing list
> [email protected]
> http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org

_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org

Reply via email to