Ok guys keep it civil and on topic please… I think we have beaten this horse 
enough…

Thank you,
Tom Noble
American Fire Sprinkler Assn.
Technical Programs Specialists
214-349-5965 x125
http://www.firesprinkler.org
On Jul 16, 2018, 7:04 PM -0500, Steve Leyton <[email protected]>, 
wrote:
> If George was still alive I wouldn't have had a chance to jump in.
>
>
>
> Steve Leyton
>
> (Sent from my phone; please excuse typos and voice text corruptions.)
>
>
>
> -------- Original message --------
> From: "Mark.Phelps" <[email protected]>
> Date: 7/16/18 4:59 PM (GMT-08:00)
> To: [email protected]
> Subject: RE: [EXTERNAL] RE: PRV after pump discharge control valve
>
> Second that!!
>
> Mark at Aero
> 602 820-7894
>
> -----Original Message-----
> From: Sprinklerforum [mailto:[email protected]] 
> On Behalf Of Tom Duross
> Sent: Monday, July 16, 2018 4:57 PM
> To: [email protected]
> Subject: [EXTERNAL] RE: PRV after pump discharge control valve
>
> These are the times I miss George.  He never thought he was the smartest guy 
> in the room, he just was.  And never condescending, always available off 
> site, just an honest pot smokin deadhead who's seen more than most.
>
> -----Original Message-----
> From: Sprinklerforum [mailto:[email protected]] 
> On Behalf Of Steve Leyton
> Sent: Monday, July 16, 2018 7:46 PM
> To: [email protected]
> Subject: RE: PRV after pump discharge control valve
>
> Okay, you've got my attention.  What formulas do you think I need to use, 
> besides the countless ones I already do?   Do you think your (highly 
> theoretical) impeller formula is of some substantive use to me?  How would it 
> add value to my firm's services?  What metrics would it help me derive to 
> improve our product or life safety in general?   Just because it's a 
> technical forum and you throw down a bunch of alpha-numeric equations (that 
> may or may not be accurate), it doesn't add up automatically to a good 
> practice or even information of value; much of the time, it seems like you 
> need attention and you simply post these formulas because you like having 
> people comment on them. You've said as much yourself on this forum.
>
> For my sake, I absolutely don't need to see my opinions or own words in 
> print.   When I contribute, I think most people would agree that I'm on 
> point, stay on topic and generally add to the conversation.  I don't have a 
> problem with people not agreeing with me and I don't need credit for getting 
> stuff right and I'm really good about learning from my mistakes, which starts 
> with admitting when I'm wrong.  I think I'm discriminating with my posts, 
> which I don't think that you are and this isn't the first time that you've 
> postulated regarding stuff that makes no sense.  Like your comment that 
> sprinklers likely wouldn't have saved most or all of the lives lost in the 
> Ghost Ship fire.
>
> All I'm saying is to be more thoughtful and stop posting for the sake of 
> posting.   What happens is that a thread like this one goes off on a tangent 
> and people disengage.  I'll bet I'm not the only one that doesn't want to 
> have to guess whether the next email is going to be worth opening or not.    
> The original question was very simple and about whether or not there was a 
> restriction about putting a PRV downstream of a pump discharge control valve. 
>   Please tell me how the formula  v=2*pi*r*f  gets me to a solution on this 
> issue.  And while you're at it maybe throw out another formula for the spool 
> piece you say we'll need ...  supposedly, I need to start using more formulas.
>
> SML
>
>
> -----Original Message-----
> From: Sprinklerforum [mailto:[email protected]] 
> On Behalf Of [email protected]
> Sent: Monday, July 16, 2018 4:26 PM
> To: [email protected]
> Subject: Re: PRV after pump discharge control valve
>
> One of these days you are going to have to start using some formulas and 
> numbers youself Steve, because like you said, this is a technical forum, not 
> a who can blow their own horn the loudest forum.
>
> Brad
> @
> Quoting Steve Leyton <[email protected]>:
>
> > Have you ever noticed that a single pump series can be applied across
> > what seem like an incredibly wide spectrum of flows and
> > pressures?   That’s because they can be paired with a variety of
> > drivers of different HP ratings and multitude of impellers.  AND THEN
> > LISTED AS ASSEMBLIES.  The idea that we have a plug-and-play impeller
> > variety pack or that we’ll buy one for now and one for when junior
> > grows out of this year’s school clothes (and put it in cabinet in the
> > pump room with a sign that says, “Install Me at Some
> > Point”) is not reality based.  As this is a technical forum and since
> > we’re using up bytes and storage space on AFSA’s server, I just think
> > it’s a good idea to keep to reality-based stuff, like widely accepted
> > good and best practices,  listed products,
> > prescriptive codes, and whatnot.   It’s one thing to promote a
> > theory or design concept that’s truly outside-the-box, but this is
> > not in that context.   I reiterate the question, who’s going to do
> > the work?  Why are we talking about such an extreme measure when
> > there’s already a simple solution on the table?
> >
> > Failures in sprinkler systems occur when a link in the chain of events
> > fails.  And it’s usually a simplistic link.  Rebuilding a listed fire
> > pump – or even talking about it those terms - is pretty
> > radical surgery when all the patient needs is a splint.   Keep in
> > mind Anthony, pumps fail WAY more frequently than pressure reducing
> > valves, especially if they’re not meticulously maintained.
> >
> > SL
> >
> > From: Sprinklerforum
> > [mailto:[email protected]] On Behalf Of
> > Fire Design
> > Sent: Monday, July 16, 2018 3:36 PM
> > To: [email protected]
> > Subject: Re: PRV after pump discharge control valve
> >
> > Brad said to check w/ the pump manufacturer so I don't know what the
> > all the keyboard punching is about. I thought it was a nice outside
> > the box approach. The manufacturer offers different size impellers for
> > a reason. Feasible or not I don't know - call the pump guys to find
> > out.
> >
> > Anthony
> >
> >
> >
> > [https://urldefense.proofpoint.com/v2/url?u=https-3A__ipmcdn.avast.com
> > _images_icons_icon-2Denvelope-2Dtick-2Dround-2Dorange-2Danimated-2Dno-
> > 2Drepeat-2Dv1.gif&d=DwIGaQ&c=wn3mZQLIuInh2ClcJ0_DIA&r=dLwiR71i_XhSFqam
> > 3ZLeaFLiQJ3cDTUB0ReB4-yDDcg&m=StU-ogetV9AXKRB6TaylmZ5fiCqNRfLNu86UXJtD
> > 7Zc&s=Je0SuHRYlFZ4DI3sJq2SpShiSxHJFY17vZF2z9JOmMA&e=]<https://urldefen
> > se.proofpoint.com/v2/url?u=https-3A__www.avast.com_sig-2Demail-3Futm-5
> > Fmedium-3Demail-26utm-5Fsource-3Dlink-26utm-5Fcampaign-3Dsig-2Demail-2
> > 6utm-5Fcontent-3Dwebmail-26utm-5Fterm-3Dicon&d=DwIGaQ&c=wn3mZQLIuInh2C
> > lcJ0_DIA&r=dLwiR71i_XhSFqam3ZLeaFLiQJ3cDTUB0ReB4-yDDcg&m=StU-ogetV9AXK
> > RB6TaylmZ5fiCqNRfLNu86UXJtD7Zc&s=SSmbqHZBdQr9w25Y3u7NzdDnEY2ivLjsD-BKI
> > Kq8Vy8&e=>
> >
> > Virus-free.
> > https://urldefense.proofpoint.com/v2/url?u=http-3A__www.avast.com&d=Dw
> > IGaQ&c=wn3mZQLIuInh2ClcJ0_DIA&r=dLwiR71i_XhSFqam3ZLeaFLiQJ3cDTUB0ReB4-
> > yDDcg&m=StU-ogetV9AXKRB6TaylmZ5fiCqNRfLNu86UXJtD7Zc&s=-ROGj8aZL-tRQJrY
> > 8qN9QnzK9m4hZaZfbPE672ldrqk&e=<https://urldefense.proofpoint.com/v2/ur
> > l?u=https-3A__www.avast.com_sig-2Demail-3Futm-5Fmedium-3Demail-26utm-5
> > Fsource-3Dlink-26utm-5Fcampaign-3Dsig-2Demail-26utm-5Fcontent-3Dwebmai
> > l-26utm-5Fterm-3Dlink&d=DwIGaQ&c=wn3mZQLIuInh2ClcJ0_DIA&r=dLwiR71i_XhS
> > Fqam3ZLeaFLiQJ3cDTUB0ReB4-yDDcg&m=StU-ogetV9AXKRB6TaylmZ5fiCqNRfLNu86U
> > XJtD7Zc&s=VkiEIz1O2xOyh5_FMCpBH5wCvrtAAodKxXICdMm3_RY&e=>
> >
> >
> > On Mon, Jul 16, 2018 at 1:54 PM, Steve Leyton
> > <[email protected]<mailto:[email protected]>> wrote:
> > You gotta let go of this Brad.  You're now having a visual fantasy
> > about what can only be described as a reach at best or more
> > critically, a bad practice.  Please go back to thermal layers or
> > something ... this is ridiculous.  Have you given the future impeller
> > an actual name for the plate, or would that be a blank that's just put
> > in the cabinet so it can be appropriately named by whoever swaps it
> > out?
> >
> > I have gotten calls from people (including attorneys) who have found
> > and to varying extents vetted me using web searches.   I recently
> > got hired to present a seminar series for the FD of one of the largest
> > cities in the USA because they found me on the web; they told me that
> > my name association with AFSA and NFPA conventions caught their eye
> > and they also saw excerpts of posts I've made to the forum regarding
> > standpipes.  You should Google "Brad Casterline
> > Sprinklerforum" ... it's long list of hits.   The stuff we say on
> > this forum isn't confined to the subscribers on the list-server.
> >
> > So if/when somebody finds this stream-of-consciousness and decides to
> > use the now-and-future impeller basis of design, and then they
> > get sued ...   you can send your formulas to their defense team I
> > suppose.   I'm intentionally being histrionic and sarcastic but it's
> > to make a point:  We need to promote best practices here.  This is an
> > exchange of ideas, yes.  But we cannot allow the conversation to turn
> > to the purely speculative or the convenient or two an unsafe
> > level of compromise.   This association, this forum and we as
> > industry activists are the means to setting the standard of care
> > higher.   We strive do it right, ESPECIALLY when nobody's watching.
> >
> > I think it's time to put the impeller-in-a-cabinet idea into a
> > permanent sleep.
> >
> >
> > SML
> >
> >
> >
> >
> >
> > -----Original Message-----
> > From: Sprinklerforum
> > [mailto:[email protected]<mailto:sprinkle
> > [email protected]>] On Behalf Of
> > [email protected]<mailto:[email protected]>
> > Sent: Monday, July 16, 2018 1:19 PM
> > To:
> > [email protected]<mailto:[email protected]
> > esprinkler.org>
> > Subject: Re: PRV after pump discharge control valve Thank you Kyle, it
> > means a great deal to me for you to say.
> > I was curious about the application too, and saw a 1250 gpm, 2600 rpm
> > with a range of 69 psi based solely on impeller diameter.
> > Both impellers would need to be purchased and certified up front, and
> > every one having signed off on the idea.
> > I even imagined a note on the enlarged pump room plan, "mount future
> > impeller and name plate in locked cabinet next to spare sprinkler
> > cabinet".
> >
> > Brad
> > Quoting "Kyle.Montgomery"
> > <[email protected]<mailto:[email protected]>>:
> >
> >> I found the formula interesting.
> >>
> >> Also, I didn't think that Brad was suggesting the fitter would modify
> >> the impeller (were you?). I assumed he was just showing that it was
> >> another possibility to explore (to be performed by pump rep).
> >> You wouldn't modify the existing impeller, but replace it with a new
> >> one.
> >>
> >> I do know it is possible (and not entirely uncommon) to have the pump
> >> manufacturer "trim" the impeller to make small modifications to the
> >> pump curve, to dial in the pressure. Not sure if it would work for
> >> the kind of pressure differences the O.P. is looking at.
> >>
> >> If it is feasible, I think that (generally speaking) it might be
> >> considered a preferable approach to the PRV. Less parts and pieces,
> >> etc. However, the nice thing about a PRV is you can really dial in
> >> the pressure and you get that wide, flat pressure curve. But there
> >> are drawbacks as well.
> >>
> >> Kyle Montgomery
> >>
> >> Aero Automatic Sprinkler Co.
> >> 21605 N. Central Ave.
> >> Phoenix, AZ 85024
> >> Direct: 623.580.7820
> >> Cell: 602.763.4736
> >> [email protected]<mailto:[email protected]>
> >
> >
> >
> >
> > _______________________________________________
> > Sprinklerforum mailing list
> > [email protected]<mailto:[email protected]
> > esprinkler.org>
> > https://urldefense.proofpoint.com/v2/url?u=http-3A__lists.firesprinkle
> > r.org_listinfo.cgi_sprinklerforum-2Dfiresprinkler.org&d=DwIGaQ&c=wn3mZ
> > QLIuInh2ClcJ0_DIA&r=dLwiR71i_XhSFqam3ZLeaFLiQJ3cDTUB0ReB4-yDDcg&m=StU-
> > ogetV9AXKRB6TaylmZ5fiCqNRfLNu86UXJtD7Zc&s=W5YPSKJz3RjsOo8n7UIeRj42dieD
> > Qm6AeQiwzTYcVWs&e= _______________________________________________
> > Sprinklerforum mailing list
> > [email protected]<mailto:[email protected]
> > esprinkler.org>
> > https://urldefense.proofpoint.com/v2/url?u=http-3A__lists.firesprinkle
> > r.org_listinfo.cgi_sprinklerforum-2Dfiresprinkler.org&d=DwIGaQ&c=wn3mZ
> > QLIuInh2ClcJ0_DIA&r=dLwiR71i_XhSFqam3ZLeaFLiQJ3cDTUB0ReB4-yDDcg&m=StU-
> > ogetV9AXKRB6TaylmZ5fiCqNRfLNu86UXJtD7Zc&s=W5YPSKJz3RjsOo8n7UIeRj42dieD
> > Qm6AeQiwzTYcVWs&e=
>
>
>
> _______________________________________________
> Sprinklerforum mailing list
> [email protected]
> https://urldefense.proofpoint.com/v2/url?u=http-3A__lists.firesprinkler.org_listinfo.cgi_sprinklerforum-2Dfiresprinkler.org&d=DwIGaQ&c=wn3mZQLIuInh2ClcJ0_DIA&r=dLwiR71i_XhSFqam3ZLeaFLiQJ3cDTUB0ReB4-yDDcg&m=StU-ogetV9AXKRB6TaylmZ5fiCqNRfLNu86UXJtD7Zc&s=W5YPSKJz3RjsOo8n7UIeRj42dieDQm6AeQiwzTYcVWs&e=
> _______________________________________________
> Sprinklerforum mailing list
> [email protected]
> https://urldefense.proofpoint.com/v2/url?u=http-3A__lists.firesprinkler.org_listinfo.cgi_sprinklerforum-2Dfiresprinkler.org&d=DwIGaQ&c=wn3mZQLIuInh2ClcJ0_DIA&r=dLwiR71i_XhSFqam3ZLeaFLiQJ3cDTUB0ReB4-yDDcg&m=StU-ogetV9AXKRB6TaylmZ5fiCqNRfLNu86UXJtD7Zc&s=W5YPSKJz3RjsOo8n7UIeRj42dieDQm6AeQiwzTYcVWs&e=
>
> _______________________________________________
> Sprinklerforum mailing list
> [email protected]
> https://urldefense.proofpoint.com/v2/url?u=http-3A__lists.firesprinkler.org_listinfo.cgi_sprinklerforum-2Dfiresprinkler.org&d=DwIGaQ&c=wn3mZQLIuInh2ClcJ0_DIA&r=dLwiR71i_XhSFqam3ZLeaFLiQJ3cDTUB0ReB4-yDDcg&m=StU-ogetV9AXKRB6TaylmZ5fiCqNRfLNu86UXJtD7Zc&s=W5YPSKJz3RjsOo8n7UIeRj42dieDQm6AeQiwzTYcVWs&e=
> _______________________________________________
> Sprinklerforum mailing list
> [email protected]
> http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org
> _______________________________________________
> Sprinklerforum mailing list
> [email protected]
> http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org
_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org

Reply via email to