2015 IBC

[F] 905.3 Required installations.
Standpipe systems shall be installed where required by Sections 905.3.1 through 
905.3.8.Standpipe
systems are allowed to be combined with automatic sprinkler systems.

Exception: Standpipe systems are not required in Group R-3 occupancies.

[F] 905.3.1 Height.

Class III standpipe systems shall be installed throughout buildings where the 
floor level of the highest
story is located more than 30 feet (9144 mm) above the lowest level of fire 
department vehicle access,
or where the floor level of the lowest story is located more than 30 feet (9144 
mm) below the highest
level of fire department vehicle access.

Exceptions:
1. Class I standpipes are allowed in buildings equipped throughout with an
automatic sprinkler system in accordance with Section 903.3.1.1 or 903.3.1.2.
2. Class I manual standpipes are allowed in open parking garages where the 
highest
floor is located not more than 150 feet (45 720 mm) above the lowest level of 
fire
department vehicle access.
3. Class I manual dry standpipes are allowed in open parking garages that are
subject to freezing temperatures, provided that the hose connections are located
as required for Class II standpipes in accordance with Section 905.5.
4. Class I standpipes are allowed in basements equipped throughout with an
automatic sprinkler system.
5. In determining the lowest level of fire department vehicle access, it shall 
not be
required to consider either of the following:
5.1. Recessed loading docks for four vehicles or less.
5.2. Conditions where topography makes access from the fire department
vehicle to the building impractical or impossible

John Drucker, CET
Fire and Electrical Subcode Official
Building Inspector
Building Department
Borough of Red Bank, NJ 
Cell/Text 732-904-6823




From: Sprinklerforum [[email protected]] on behalf 
of Taylor Schumacher [[email protected]]
Sent: Thursday, August 09, 2018 8:39 AM
To: [email protected]
Subject: RE: Building Heights Requiring Standpipes


We had already walked through the IBC and all the pictures but he wants more 
solid info. I’ve reached out to the State Fire Marshal and they had agreed to 
write up an explanation. 
  
Like Steve explained, the access to the building and stairwells is at grade 
plane, which is first floor in this case, and is where the fire fighting 
appurtenances are located. 
  
Thanks, 
  
Taylor Schumacher 
  
From: Sprinklerforum [mailto:[email protected]] On 
Behalf Of Steele, Andrew
Sent: Wednesday, August 08, 2018 5:45 PM
To: [email protected]
Subject: RE: Building Heights Requiring Standpipes 
Good example diagrams are in the ICC Fire /Bldg Code Commentary books. 
  
On Aug 8, 2018 18:01, Jim Davidson <[email protected]> wrote: 
Go to the Building Code for the definition of height above lowest level of FD 
Access, if ICC’s IBC then call for a code interpretation and if needed ask for 
a written response. 
The ICC has been through this problem a few times. Some jurisdictions 
specifically define the height above the lowest level of FD access.   
Have a fire safe day!   
Jim Davidson 
From: Sprinklerforum <[email protected]> On Behalf 
Of Taylor Schumacher
Sent: Wednesday, August 8, 2018 5:55 PM
To: [email protected]
Subject: Building Heights Requiring Standpipes 
I have an AHJ that is adamant that a 3-story 13R project I have requires Class 
I standpipes because the underground parking level will exceed the 30’ height 
requirement. I have always viewed these heights as from the parking lot closest 
to main entry or where the FDC is located rather than the fire truck driving 
into the garage. Have I been looking at this wrong? 
Taylor Schumacher 
  
  